Re: Main breaker popping at 10A

Quote:
Originally Posted by Cadence View Post
I doubt you meter isn't up to the task. Replace the breaker. If you had a bad connection to make a 30A break trip at around 10A you would have already burnt to the waterline.
That's quite reassuring..... I think.

It is a point well taken though and very helpful advice. To continue the troubleshooting, I do have a voltage meter built into the system and it never drops. In addition, I've encountered this problem at 5 different marinas recently so the issue isn't the voltage supply.

I do have a spare shore power cord I could swap out, as one poster mentioned they burn up when heaters are used. I'm not sure how or why that happens, but I have observed blackening at the shore side end of cables before.

I'll definitely replace the breaker as it sounds like a likely culprit.
Korvessa is offline   Reply With Quote
Old 20-02-2018, 11:23   #17
Registered User

Join Date: Feb 2018
Posts: 1
Re: Main breaker popping at 10A

Get yourself an AMP Meeter. Only way to truly know what is going on.
send me the results and I can tell you where the problem is. They are super easy to use.
ojwoody is offline   Reply With Quote
Old 20-02-2018, 12:55   #18
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Main breaker popping at 10A

Check the voltage to the breaker. If it doesn't drop under load your shore power cord isn't the problem. If it does look at it. Your meter not being good enough is not a problem. Buying a Fluke or an clamp on ammeter is totally unnecessary. I'm still betting on a bad breaker. The only other thing I can see is you have a current draw you aren't considering, a reefer or something?
Cadence is offline   Reply With Quote
Old 20-02-2018, 13:13   #19
Registered User
 
Korvessa's Avatar

Join Date: Apr 2016
Location: Anacortes WA, USA
Boat: Nauticat 40 (1985)
Posts: 38
Re: Main breaker popping at 10A

Quote:
Originally Posted by ojwoody View Post
Get yourself an AMP Meeter. Only way to truly know what is going on.
send me the results and I can tell you where the problem is. They are super easy to use.
Seems like a piece of kit I need. I've ordered one and it should arrive tomorrow.

Stay tuned!

Korvessa
Korvessa is offline   Reply With Quote
Old 20-02-2018, 15:21   #20
Registered User
 
hzcruiser's Avatar

Join Date: Aug 2008
Location: Sydney, Australia
Boat: Roberts 45
Posts: 1,037
Re: Main breaker popping at 10A

Quote:
Originally Posted by Korvessa View Post
Seems like a piece of kit I need. I've ordered one and it should arrive tomorrow.

Stay tuned!

Korvessa
Which one did you get?
__________________
Fair winds,
heinz

https://www.timantra.net
hzcruiser is offline   Reply With Quote
Old 20-02-2018, 15:40   #21
Registered User
 
Korvessa's Avatar

Join Date: Apr 2016
Location: Anacortes WA, USA
Boat: Nauticat 40 (1985)
Posts: 38
Re: Main breaker popping at 10A

Quote:
Originally Posted by hzcruiser View Post
Which one did you get?
While I know Fluke is the best, it's a lot of coin. If my cheap unit doesn't do the job, it'll at least be a backup if I have to buy a better one.

Here's what I chose. It was highly rated on Amazon.
Korvessa is offline   Reply With Quote
Old 20-02-2018, 18:09   #22
Registered User
 
hzcruiser's Avatar

Join Date: Aug 2008
Location: Sydney, Australia
Boat: Roberts 45
Posts: 1,037
Re: Main breaker popping at 10A

Quote:
Originally Posted by Korvessa View Post
While I know Fluke is the best, it's a lot of coin. If my cheap unit doesn't do the job, it'll at least be a backup if I have to buy a better one.

Here's what I chose. It was highly rated on Amazon.
That looks decent enough for your specific purpose. However, there are two "pitfalls for young players" with them.

First, check out the first cu review:

I purchased this clamp meter primarily to measure current/amps on 120 volt appliances, heaters, etc. To do this with ANY clamp meter, you MUST separate the hot and neutral conductors or they will cancel each other out and give a zero amp reading.


To cover that, I fabricated my own little adapter that has the three leads separated so I can measure AC current with the clamp.

Secondly: In the future, you might be interested in measuring DC currents to/from your batteries as well, and this is something a lot of the clamp meters (even from Fluke) including yours-to-be, can't do, unless it's explicitly stated.
__________________
Fair winds,
heinz

https://www.timantra.net
hzcruiser is offline   Reply With Quote
Old 20-02-2018, 19:50   #23
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Main breaker popping at 10A

yes I did mention to get one that will do both ac and dc. so you can trouble shoot battery issues as well. oh well.
smac999 is offline   Reply With Quote
Old 21-02-2018, 03:47   #24
Registered User

Join Date: May 2016
Posts: 84
Re: Main breaker popping at 10A

I worked in a related field.
Breakers do not employ a "controlled explosion". They will trip at the specified value, in the specified time for many trips.
Some breakers are rated for use as a switch and can be turned on an off daily. Most are NOT rated for use as a switch.
However, breakers often go bad.
Moisture is bad for the metal parts, slight heat is bad for the insulating parts. High heat is bad for the steel parts.

A 30 amp breaker that tripped at the 13 amps your heater was running at is now bad. Before you even open the panel, have a new breaker on hand.
Replace the breaker.
It will cost far more than the breaker is worth to properly test it.
Replace the breaker. Even if you find the heat you felt was from wiring, the breaker has been ruined by heat. Replace the breaker.

After you replace the breaker, diagnose other problems if the trip persists.

Breakers hold at their rating, and trip above the rating, the higher the current, the faster they trip.
Redpcx is offline   Reply With Quote
Old 21-02-2018, 10:40   #25
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Main breaker popping at 10A

Quote:
Originally Posted by Korvessa View Post
...I've encountered this problem at 5 different marinas recently...
"Get yourself an AMP Meeter"

Quote:
Originally Posted by Korvessa View Post
Seems like a piece of kit I need. I've ordered one and it should arrive tomorrow...
You should have just replaced the bad breaker already.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 21-02-2018, 10:51   #26
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Main breaker popping at 10A

Quote:
Originally Posted by Terra Nova View Post
"Get yourself an AMP Meeter"



You should have just replaced the bad breaker already.
Buy a breaker for a few bucks? Hell no, buy a Fluke and Amprobe you don't know how to use. Makes sense to me.
Cadence is offline   Reply With Quote
Old 21-02-2018, 11:41   #27
Registered User
 
Boatyarddog's Avatar

Join Date: Nov 2014
Location: Olympia, Washington
Boat: 1979 Mariner Ketch 32-Hull 202
Posts: 2,124
Images: 2
Re: Main breaker popping at 10A

Quote:
Originally Posted by Cadence View Post
Buy a breaker for a few bucks? Hell no, buy a Fluke and Amprobe you don't know how to use. Makes sense to me.
Having spares around is always a good idea, for any cruiser/boater.
Easy diagnosis just swap it out, simplest is best.will save lots of time Head Scratching.
Then get more complicated, if your not comfortable doing that, ask yer neighbors maybe someone will help, boaters love to help.
Cheers,
SV Cloud Duster
Boatyarddog is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Volvo Penta 10A Cooling Problem Richard-R Engines and Propulsion Systems 4 07-07-2016 12:30
10a Dual Battery Solar Controller? EagleBay Electrical: Batteries, Generators & Solar 2 19-02-2014 01:07
Starter exciter input drawing >10A, normal? jbrownson Electrical: Batteries, Generators & Solar 32 20-05-2013 13:49
My 20 Amp Breaker Keeps Popping and Shutting Down Genset Turtlep Electrical: Batteries, Generators & Solar 4 26-07-2012 13:23

Advertise Here


All times are GMT -7. The time now is 01:28.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.