Generator or A/C problem?

Yesterday I ran my old Entec/Kubota 6kw generator and when I tried to run my air conditioner, fan would run but compressor makes some starting noise but stays huming and dies. Everything else seems to run fine (water heater, batt charger, bread toaster) and the generator voltage dial reads 120v. But when I checked the ground to hot voltage on one of the receptacles it read 55volts and the hot to neutral 113volts.

The generator is very old and has a running capacitor to maintain voltage I guess? About six months ago I replaced the E/G capacitor because the dial was reading about 90volts and after replacing it, it came up to the correct voltage (120). Worked fine until yesterday.

Could it be the generator windings, a bad capacitor in the air conditioner, any ideas???
avazquez is offline   Reply With Quote
Old 01-01-2010, 08:29   #2
Registered User

Join Date: Apr 2007
Location: Humacao, Puerto Rico
Boat: Beneteau 456
Posts: 433
Images: 8
any ideas?
avazquez is offline   Reply With Quote
Old 01-01-2010, 09:08   #3
Registered User
 
svHyLyte's Avatar

Join Date: Mar 2006
Location: Tampa Bay area, USA
Boat: Beneteau First 42
Posts: 3,961
Images: 25
Last year we had a similar problem with out 4.2Kw genny. It proved to be a bad capacitor. In our case the controller box has 3 capacitors. Two that evidently stabilize the voltage and a 3rd to maintain the voltage when a heavy load is applied. For whatwever reason, the fellow that installed our system installed the controller box in a sideways rather than vertical position which led to the failure of the capacitors. It seems they are filled with oil and have tiny vent hole on the tops to allow air to escape when they get heated up. Mounted sideways, the oil was able to leak out. Only a small amount but enough to cause the capacitors to fail. The boys at Panda picked up on the problem right away--"Is your controller mounted vertically?". Fortunately remounting the controller and replacing the capacitors was not unduly costly but it was a pain in the neck, eh?

Good luck and happy New Year.

s/v HyLyte
__________________
"It is not so much for its beauty that the Sea makes a claim upon men's hearts, as for that subtle something, that quality of air, that emanation from the waves, that so wonderfully renews a weary spirit."
svHyLyte is offline   Reply With Quote
Old 01-01-2010, 09:28   #4
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,451
Images: 241
I don't know.

Is there any voltage Neutral to Ground?

What is the voltage when trying to start Air-Con?

Did you replace the control panel, back in 2007?
http://www.cruisersforum.com/forums/...ent-10682.html

Entec Corporation
PO Box 94242, Seattle, WA 98124
Tel: 206-624-2169
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 05-01-2010, 16:19   #5
Registered User

Join Date: Apr 2007
Location: Humacao, Puerto Rico
Boat: Beneteau 456
Posts: 433
Images: 8
Gord,

In 07 we did not replace the control panel. We were able to figure it out. I just came back to the marina and everything run well with shore power even the a/c. So evidently it seems like there is something wrong with the generator. Yes there were 55 volts between neutral to ground.
avazquez is offline   Reply With Quote
Old 05-01-2010, 17:48   #6
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
There should be a N-G bond at the genset. So that is at least one problem.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Diesel generator irwinsailor Electrical: Batteries, Generators & Solar 1 08-02-2016 12:33
Problem with Westerbeke 3.8KW Generator Mike Sibley Electrical: Batteries, Generators & Solar 6 14-01-2009 04:37
Wind Generator billangiep Electrical: Batteries, Generators & Solar 60 07-06-2008 12:06
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06
Generator for 25ft... kindtampa General Sailing Forum 13 20-10-2005 13:32

Advertise Here


All times are GMT -7. The time now is 02:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.