So explain to me again why fuses are required [emoji848]
markcouz is offline   Reply With Quote
Old 31-10-2023, 11:06   #32
Registered User

Join Date: May 2020
Location: SoCal
Boat: 35' Alden Design Cutter
Posts: 413
Re: Everything to bus bars?

Quote:
Originally Posted by Jammer View Post


Although you dismiss the possibility of a short in the cables from the battery to the inverter, such shorts can and do occur. Among the many possible causes are metal cable clamps that cut into the cable, contact between the + cable and moving parts of the engine (or propshaft0 or exhaust components, and heat damage to the insulation near the connection to the inverter caused by high resistance in the terminals or bolts.
While I haven't experienced this on a boat, I have diagnosed a car fire for an insurance claim that was caused by an ashtray light + being grounded during a radio install.
The installer replaced the 10amp fuse with a 30amp fuse. According to the owner, the dash lights worked fine for about 4 hours... before the fire.

Anyway, the original fuse worked as it was supposed to, and you're right, accidental groundings do happen.
Iron E is offline   Reply With Quote
Old 04-02-2024, 12:31   #33
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,119
Re: Everything to bus bars?

Quote:
Originally Posted by Jammer View Post
The MRBF fuses you plan to install on the battery terminals may not have a sufficient interrupting rating for your situation. Typically they are rated for 10,000 amps. It is likely that your batteries will be capable of delivering more than that, when new and fully charged. You may find that the ABYC requires a minimum 2" spacing between the battery and the fuse and does not permit installations on the battery terminals themselves.
Please provide the ABYC Section in E-11 that specifies a 2" minimum and prohibits MRBF fuses on the terminals themselves. I can't find it.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 05-02-2024, 02:31   #34
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,472
Images: 241
Re: Everything to bus bars?

According to Blue Sea Systems http://assets.bluesea.com/files/reso...YCexcerpts.pdf

“The ABYC requirement is for a battery bank fuse is to be within 7 wire inches of the battery bank. The European ISO/RCD (which is law) requires the fuse be within 200mm. 200mm equates to about 7.9”.


Quote:
Originally Posted by ABYC
ABYC 11.10.1.1.1. OVERCURRENT PROTECTION DEVICE LOCATION:
Undergrounded conductors shall be provided with overcurrent protection within a distance of seven inches (175 mm) of the point at which the conductor is connected to the source of power measured along the conductor.”
Mounting placement dimensions for a fuse or circuit breaker (7"/40"/72" ABYC rule): 7 inch maximum if the conductor is not housed in a sheath or enclosure in addition to the wire insulation, 40 inch maximum if the conductor is housed in a sheath or enclosure in addition to the wire insulation, 72 inch maximum if the conductor is connected directly to the battery and housed in a sheath or enclosure in addition to the wire insulation.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cable sizing for battery switch, bus bars etc jonase Electrical: Batteries, Generators & Solar 15 22-01-2019 01:00
For Sale: Dual Bus Bars hikersailor Classifieds Archive 0 11-06-2016 16:22
Best ( or preferred ) location for Bus Bars both +ive & -ive CruiserPete Electrical: Batteries, Generators & Solar 3 28-02-2016 23:58
Small Junction Boxes/ Bus Bars? Dockhead Electrical: Batteries, Generators & Solar 4 19-05-2013 04:53
Mounting Terminal Strips, Bus Bars, etc. to Hull davisr Electrical: Batteries, Generators & Solar 28 06-06-2012 18:22

Advertise Here


All times are GMT -7. The time now is 14:49.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.