AC plug requirements for Charger

Just picked up a new Victron 30A 3 outlet charger for the boat. Previously the boat did not have a charger however there is an empty breaker on the AC panel for an install. The charger has a plug that is rather not cut off so I was thinking of installing a GFI receptacle and wiring that to the breaker on the panel. My question is, shopping for a receptacle (Blue sea etc) they are rated for 20A. How does that work when it’s less than the charger amps?
Cdn_bacon is offline   Reply With Quote
Old 16-04-2024, 19:53   #2
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,454
Re: AC plug requirements for Charger

The charger outputs max 30A (and 14V DC).

This is NOT the input current. The AC input current will be only a few amps so any GFI respectable will be suitable.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-04-2024, 20:09   #3
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,349
Re: AC plug requirements for Charger

Quote:
Originally Posted by Cdn_bacon View Post
The charger has a plug that is rather not cut off so I was thinking of installing a GFI receptacle and wiring that to the breaker on the panel.
^
Yep, even if it had no plug hardwiring it by using the line/load on a GFCI is good.
I've done that, every AC unit in the boat is wired thru a GFCI.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 17-04-2024, 07:52   #4
Registered User

Join Date: Apr 2022
Posts: 41
Re: AC plug requirements for Charger

Quote:
Originally Posted by Bowdrie View Post
^
Yep, even if it had no plug hardwiring it by using the line/load on a GFCI is good.
I've done that, every AC unit in the boat is wired thru a GFCI.
Thanks! Actually going to see if I can open up the charger tonight and get access to where the plug wires into the guts of the charger and run direct wiring.
Cdn_bacon is offline   Reply With Quote
Old 17-04-2024, 08:15   #5
Registered User

Join Date: Apr 2022
Posts: 41
Re: AC plug requirements for Charger

Quote:
Originally Posted by Wotname View Post
The charger outputs max 30A (and 14V DC).

This is NOT the input current. The AC input current will be only a few amps so any GFI respectable will be suitable.
So how do I know if I need a 15A or 20A GFI outlet?
Cdn_bacon is offline   Reply With Quote
Old 17-04-2024, 08:45   #6
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,349
Re: AC plug requirements for Charger

30 amps at 14VDC is only ~420 watts.
Discounting any losses that's only ~3.5 amps of 120VAC input.
Take your pick of GFCIs.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 18-04-2024, 02:52   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,494
Images: 241
Re: AC plug requirements for Charger

Quote:
Originally Posted by Bowdrie View Post
30 amps at 14VDC is only ~420 watts.
Discounting any losses that's only ~3.5 amps of 120VAC input.
Take your pick of GFCIs.
Indeed.
A 15A 120VAC GFCI Receptacle can run at least a 1440 Watt* [12A @ 120VAC] load continuously, which is sufficient to power a 100 Amp charger [@14VDC].


* FWIW: 15A GFI Receptacles are generally rated at 1800 Watts maximum
But:
The Circuit Breaker, feeding it, is probably not.


For a particular circuit breaker, even though the 80% and 100% versions have the same amp rating (use the same trip curve), in actual use they are applied differently, depending on the continuous loads
The standard 80% rated breaker can only be applied continuously [defined as 3 hours or more] at 80% of its continuous current rating.
100% rated circuit breakers can be applied at up to 100% of their current rating continuously. Breakers rated at 80% can be applied at 100% of their rating, if the loading will last for less than 3 hours.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 18-04-2024, 03:23   #8
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,494
Images: 241
Re: AC plug requirements for Charger

A Continuous current rating is the designated amperes [RMS AC or DC] that a device will carry continuously, for 3+ hours, in free air, without tripping, or exceeding temperature limits.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
charger, men, plug


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Want To Buy: Dri-Plug connector- old autopilot/tiller pilot plug sanibel sailor General Classifieds (no boats) 4 01-05-2020 06:34
Changes on the Plug-in Download page & new plug-in packages nohal OpenCPN 8 04-07-2014 07:15
Separate Charger and Inverter or Charger-Inverter ? SvenG Electrical: Batteries, Generators & Solar 14 15-10-2010 17:14
Opinions on this charger: BASSMASTER ProMariner Marine Battery Charger exranger Electrical: Batteries, Generators & Solar 6 30-11-2008 07:25
AC charger smarter than the 3 stage "smart" charger? CSY Man Electrical: Batteries, Generators & Solar 64 30-09-2006 12:49

Advertise Here


All times are GMT -7. The time now is 19:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.