A friend had a system that was undersized for the volume of the cabinet.
She has just purchased a new system
Isotherm 2503 comprising of a bigger evaporator plate, a BD50 air cooled
compressor, in order to be more efficient at
cooling the entire box.
She arrived back in
Panama, did a wonderful
installation, and on powering up, it did not cool at all. I was in another island 200 miles away so asked her to attach a gauge to the Schraeder valve, and it read 2psi with system off. It looks like the TSA guys must have purged the system as it was carried as luggage. (This is a guess)
So she got a local "expert" to come and re-gas the system, and then she called me as it was acting weirdly. Namely ice on the return line near the compressor!
I told her that it had too much refrigerant, and she should bleed it till:
The frostline was at the end of the plate,
and
The Amperage was about 5-ish.
and
The running low side pressure was about 15 psi.
All of that done, but I got back here yesterday and went to take a look.
There are some strange things.
When it is cycled OFF the filter and capillary and HP quick connect get really cold.
The amperage is approximately 6-7 during a run cycle.
The cycle time is approx 3 minutes on and 6 off.
The whole purpose of the job was to reduce the daily Ah
consumption and its gone UP!
Please can someone comment.
What does your
Isotherm system draw at 12v in amperes?
Does your cap tube at the
compressor get cold when off?
Is this indicative of a non-condensing gas in the system?
All suggestions warmly welcome.