And that switch would be ON only when I start the engine? If so, that'd mean no o more path to earth from my DC negative. I thought that was necessary, or is it only when there's a bonding circuit connecting underwater metals?
Yes, I thought that was clear as I said safety from AC faults, but maybe they could come from an inverter (which I don't have) as well?
|
You keep the switch on while using the engine, or you turn it off when not using the engine for a while
For AC grounding, see my attached diagram. An isolation transformer is the best protection for people as well as for the boat. It will completely eliminate the issue. Look at every detail of the diagram, especially every grounding wire. A very important point is that the ground from shore terminates at the transformer and does NOT connect to the transformer ground wire that connects to the rest of the boat.
Also, for bonding metals: when you have underwater metals and they need cathodic protection, they usually have zincs. This is mostly for
parts made out of several different metals, like propshaft and
propeller etc.
I am not a fan of connecting everything to a central zinc. Most metals, like
bronze thru-hull fittings, don’t need anything.
Then there’s also bonding for
lightning protection. This concerns the
mast, stays and
shroud chainplates and connecting these either to underwater bonding plates or special discharge fittings just above the waterline. Searching on this forum will find threads on the subject.