The OC lockout is good protection against filling the
exhaust with seawater, next attempt turn off the seawater intake until it fires up. If you’re certain that the
fuel supply up to the
injector pump is NOT the problem and the Glowplugs are all working, read on. I’m pretty sure your Kohler has the same engine as the small
Northern lights 673 (and up) so probably the same stop solenoid but the Kohler
wiring is different with the electronic
control panel.
First check the senders for
corrosion and function, there could be a fault in the shutdown circuit that’s cancelling the startup, then check the screw in “run” solenoid on the back of the
injector pump housing and partially hidden by the fuel
lift pump. The solenoid is “active to run” and allows the rack to move to no fuel when it’s disconnected .
However , if the solenoid is the same as the rest of the Kohler range (Woodward brand with 2 mounting screws) there is a potential risk of the “pull in” coil burning out due to too many start attempts and the engine won’t start until the solenoid is replaced.
Good genset but the electronic panel and Woodward solenoid are the downside.