I've had my 125 AH
LiFEPO4 battery paralleled with a 165 AH
AGM bank for 2 years and about 75 discharge/charge cycles. No problems.
LiFePO4 batteries should have all charge disconnected when (or before) reaching full charge, and the
battery disconnected when (or before) it reaches its discharge floor.
If you have the
lithium set up as a separate bank, how will the loads behave when the
lithium is switched off at the discharge floor? You could use
steering diodes to combine your lead-acid and lithium, but I've chosen instead to run the lithium in parallel. Here are my parameters: (LFP = LiFePO4 battery. LA = lead-acid batteries). Voltages are measured at the LA bank.
Charge:
13.8 volts, LFP switched off the bank, LFP charging ceases
14.4 volts, LA charging ceases.
13.4 (temperature compensated) LA float voltage.
Discharge:
13.2 volts, LFP is reconnected to bank in parallel.
12.7 volts, LFP is disconnected from bank.
The LFP is disconnected from the bank with a breaker switch at the end of each sail, and reconnected for charge immediately prior to next sail. There is no
danger to leaving the LFP battery partially charged (they don't sulfate) but the calendar life is reduced by storing it in a fully charged state.
That's it. Nothing untoward happens when the LFP is connected in parallel with the LA batts at 13.2 volts. The LA batteries draw practically no
current from the LFP at 13.2 volts. I've measured it - there is a "surge" of 2 amps that diminishes to zero in one minute (0.03 amp hour - if you prefer). For the first 100 AH (I don't fully charge/discharge the LFP), it does all the
work. The LA batts just float. The LA batteries take over at 12.7 volts.
Power is never interrupted to the bus.
I'm using a relay (
https://www.digikey.com/products/en?...N2C-DC12&v=236) to connect/disconnect the LFP to the bank. I'm using a APO3 (
http://www.aprsworld.com/apo3/) to disconnect the LFP at 12.7 volts, and a
Victron battery
monitor (
https://www.victronenergy.com/batter.../bmv-712-smart) to both
monitor the battery and de-energize the relay at 13.8 volts. The maximum charge/discharge
current used in my application is 30 amps (I don't try to start an
engine with the bank). The LFP is fused at 50 amps, and the breaker trips at 30 amps. If your current needs are higher, you'll have to use a different relay.
I suggest using the DPDT relay linked above, and
wiring the two sets of normally open contacts in parallel. The DPDT relay doesn't cost much more that a SPST/SPDT relay, but it'll last longer with a set of connects doubled.