Yet another solar wiring question

I am about to add four solar panels to the fly-bridge roof of my Leopard 47PC to go “off the grid”. I am a solar “newbie” and would appreciate any comments before I mess this up.

The four panels are Apolloflex 145W and the manufacturers spec sheet indicates a “short circuit current” of 8.69A and open circuit voltage of 22.57V (rated current and voltage 8.08A and 19.01V respectively). The battery bank will be 4 in parallel of 210 Ah AGMs, set up for a 12 volt system.

I plan to wire the 4 solar panels series / parallel producing an assumed 45.14 Volts @ 17.38 Amps to be fed into a Morningstar Tristar MPPT 45A controller. The controller specs claim a maximum current of 45 Amps and 600 Watts of power at a nominal maximum input of 12V. Max open circuit voltage of 150V.

My questions are: Any problems going series / parallel on the panels? Do you think that the controller is within spec for this set-up? Finally, 4 AWG gauge wire OK for controller to battery and 14 or 15 AWG gauge wire OK to wire up the solar panels?
Ed
edmundsteele is offline   Reply With Quote
Old 24-07-2015, 11:53   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Yet another solar wiring question

I think you will hear, way upsize your wire at least to the controller and to go with parallel as opposed to any series.
Lets see
a64pilot is offline   Reply With Quote
Old 24-07-2015, 12:33   #3
Registered User

Join Date: Apr 2015
Location: Copenhagen, Denmark
Boat: 1968 29' Quorning Tri
Posts: 20
Re: Yet another solar wiring question

I think your setup sounds reasonable given the numbers and series/parallel you've decided on, so if it's what you're set on, no worries.

I ran some numbers, and if it were me, I'd run independent charge controllers per panel for efficiency gains with regard to shading and equipment redundancy. The only slight downside here is mounting a few more charge controllers and a slightly different wiring job. I had originally posted some Genasun GV-10's, but I noticed the rated maximum wattage for those is at 140W, which is just a bit under the 145W panels you've shown. They would probably work, but you don't want to cut it that close. I don't know of any other real reputable charge controllers within the ~12.5A range that are cheap enough to really be suitable here, but maybe others could comment on one. The GV-10's are just $109 each, but again without downsizing the panels just slightly I'd be sort of uncomfortable cutting it so close.

So I guess it's back to either your original proposed setup, or maybe 2 30amp controllers for redundancy/efficiency, with each controller hooked up to a pair of paralleled panels.

1 TriStar TS-MPPT-45 at $459.49, or 2x TriStar TS-MPPT-30's for $720 total.

My thoughts for being self-reliant is with multiple controllers if something goes wrong with 1 controller or panel, you only lose a portion of the system. I imagine that comparing the two setups you will have slightly better numbers with the multiple controller setup in shade or partial shading scenarios.
FatChance is offline   Reply With Quote
Old 24-07-2015, 14:03   #4
Registered User

Join Date: Apr 2014
Location: Puerto Rico
Boat: Cape Dory 28
Posts: 144
Re: Yet another solar wiring question

Thank you both for the feedback. The solar panel manufacturer recommended 5 m of 1.5 mm**2 and that translates as 15AWG. Seems skinny though.
Ed
edmundsteele is offline   Reply With Quote
Old 24-07-2015, 18:02   #5
Registered User
 
OceanPlanet's Avatar

Join Date: May 2009
Location: Woolwich, Maine
Boat: Mull 42-cold molded NZ 1970
Posts: 512
Send a message via Skype™ to OceanPlanet
Re: Yet another solar wiring question

Quote:
Originally Posted by FatChance View Post
I think your setup sounds reasonable given the numbers and series/parallel you've decided on, so if it's what you're set on, no worries.

I ran some numbers, and if it were me, I'd run independent charge controllers per panel for efficiency gains with regard to shading and equipment redundancy. The only slight downside here is mounting a few more charge controllers and a slightly different wiring job. I had originally posted some Genasun GV-10's, but I noticed the rated maximum wattage for those is at 140W, which is just a bit under the 145W panels you've shown. They would probably work, but you don't want to cut it that close. I don't know of any other real reputable charge controllers within the ~12.5A range that are cheap enough to really be suitable here, but maybe others could comment on one. The GV-10's are just $109 each, but again without downsizing the panels just slightly I'd be sort of uncomfortable cutting it so close.

So I guess it's back to either your original proposed setup, or maybe 2 30amp controllers for redundancy/efficiency, with each controller hooked up to a pair of paralleled panels.

1 TriStar TS-MPPT-45 at $459.49, or 2x TriStar TS-MPPT-30's for $720 total.

My thoughts for being self-reliant is with multiple controllers if something goes wrong with 1 controller or panel, you only lose a portion of the system. I imagine that comparing the two setups you will have slightly better numbers with the multiple controller setup in shade or partial shading scenarios.
There is actually a little bit of headroom in the Genasun GV10 specs...they should be fine with those panels.
__________________
Twice around was enough for me...
Now I just help others prep for ocean trips...
www.oceanplanetenergy.com
[SIGPIC][/SIGPIC]
OceanPlanet is offline   Reply With Quote
Old 24-07-2015, 23:06   #6
Registered User

Join Date: Apr 2015
Location: Copenhagen, Denmark
Boat: 1968 29' Quorning Tri
Posts: 20
Re: Yet another solar wiring question

Quote:
Originally Posted by OceanPlanet View Post
There is actually a little bit of headroom in the Genasun GV10 specs...they should be fine with those panels.
Interesting, do you have a source or numbers on that you could provide? I have been really happy with the GV-10.
FatChance is offline   Reply With Quote
Old 25-07-2015, 00:20   #7
Registered User
 
OceanPlanet's Avatar

Join Date: May 2009
Location: Woolwich, Maine
Boat: Mull 42-cold molded NZ 1970
Posts: 512
Send a message via Skype™ to OceanPlanet
Re: Yet another solar wiring question

Quote:
Originally Posted by FatChance View Post
Interesting, do you have a source or numbers on that you could provide? I have been really happy with the GV-10.
"Officially" the rating is 140W. However we have gotten approval to use the GV10 with the Solbian CP144 and SXP145 panels where they have been working fine.

In the coming weeks we (OPE) are planning some more head to head small controller testing. We already have been trying some shading configurations to learn answers to questions we've had, it has been fun. Hope to get info up online eventually.
__________________
Twice around was enough for me...
Now I just help others prep for ocean trips...
www.oceanplanetenergy.com
[SIGPIC][/SIGPIC]
OceanPlanet is offline   Reply With Quote
Old 25-07-2015, 07:19   #8
Registered User

Join Date: Jul 2013
Location: San Diego, CA
Posts: 6,619
Re: Yet another solar wiring question

Quote:
Originally Posted by edmundsteele View Post
I am about to add four solar panels to the fly-bridge roof of my Leopard 47PC to go “off the grid”. I am a solar “newbie” and would appreciate any comments before I mess this up.

The four panels are Apolloflex 145W and the manufacturers spec sheet indicates a “short circuit current” of 8.69A and open circuit voltage of 22.57V (rated current and voltage 8.08A and 19.01V respectively). The battery bank will be 4 in parallel of 210 Ah AGMs, set up for a 12 volt system.

I plan to wire the 4 solar panels series / parallel producing an assumed 45.14 Volts @ 17.38 Amps to be fed into a Morningstar Tristar MPPT 45A controller. The controller specs claim a maximum current of 45 Amps and 600 Watts of power at a nominal maximum input of 12V. Max open circuit voltage of 150V.

My questions are: Any problems going series / parallel on the panels? Do you think that the controller is within spec for this set-up? Finally, 4 AWG gauge wire OK for controller to battery and 14 or 15 AWG gauge wire OK to wire up the solar panels?
Ed

your solar panels and MPPT controller are well matched, both in terms of Voc and Impp.

I'd like to point out that if you get any shading at all on the panels, you'd be better off with all 4 panels in parallel for the least amount of losses. If you have them in series/parallel, the one panel that gets shaded will affect the other panel in series with it. In a worse case scenario, 2 panels get shaded, and the other 2 panels are affected for a loss in power from all 4 panels.

In all 4 parallel, only the shaded panels are affected, and there really isn't much advantage to series connections other than providing higher voltage and allowing one size smaller cabling. I always recommend the largest cabling practical for the lowest losses possible, just for good measure.

Another possible way to go is 2 Eco-worthy 20 amp controllers. If you're set on 2 series sets of panels, then go with a pair of panels into each of these 20 amp controllers at only $102 (ea.) delivered.

Or, if you want max. harvest and one controller per panel, get 4 of the Eco-worthy controllers and connect one panel to each. This would give a max. possible current of 75-78 amps if you chose to add 4 more panels. Total cost for 4 controllers is only $408.

Now as for cable size: 15 ga is much too thin. If I were running 4 panels into 4 controllers, I'd use 8awg. If running 4 panels into 2 controllers, I'd use 6 awg. If running 4 panels into one controller, then I'd use MC4 combiners to combine pairs of panels into 6awg, then join the 2 6awg sets into a 4 awg run to the controller.

If the controller is going to be close to the batteries, then I'd use 4 awg between controller and batteries, if longer, then 2 awg would be recommended. These numbers are off the top of my head, use an amperage chart for proper sizing, and don't be afraid to go one size larger for less loss. Also, make sure all connections are waterproof to minimize corrosion, you'll lose a lot of power from poor connections!
socaldmax is offline   Reply With Quote
Old 25-07-2015, 08:42   #9
Registered User

Join Date: Jan 2009
Location: where ever my anchor is
Boat: 28' Bristol Channel Cutter - Angelsea
Posts: 277
Images: 3
Re: Yet another solar wiring question

Saw this post and since it was similar I thought I would add to it.

Ok, I have two separate solar systems on board (two controllers). One forward with a 100w panel and one aft with 2-100w panels. I am using Renogy panels and their MPPT 20A controllers, one for each location.

Now here's the question: They both feed into the house bank. Do the separate controllers see the increased system voltage of the other and say...hmmm looks like the system is up and I don't need to do anything? So does one of the systems shut down now? Or output substantially less since it thinks the system is up?

I have read that some people use seperate controllers for each panel. don't they get confused? Something like me?
__________________
Gary Shanti's blog
"two wrongs don't make a right, but three lefts will get you back on the freeway"
seacap is offline   Reply With Quote
Old 25-07-2015, 08:59   #10
Registered User

Join Date: Jul 2009
Location: Ontario, Canada
Boat: Niagara 31
Posts: 252
Re: Yet another solar wiring question

Quote:
Originally Posted by socaldmax View Post
your solar panels and MPPT controller are well matched, both in terms of Voc and Impp.

I'd like to point out that if you get any shading at all on the panels, you'd be better off with all 4 panels in parallel for the least amount of losses. If you have them in series/parallel, the one panel that gets shaded will affect the other panel in series with it. In a worse case scenario, 2 panels get shaded, and the other 2 panels are affected for a loss in power from all 4 panels.

In all 4 parallel, only the shaded panels are affected, and there really isn't much advantage to series connections other than providing higher voltage and allowing one size smaller cabling. I always recommend the largest cabling practical for the lowest losses possible, just for good measure.

Another possible way to go is 2 Eco-worthy 20 amp controllers. If you're set on 2 series sets of panels, then go with a pair of panels into each of these 20 amp controllers at only $102 (ea.) delivered.

Or, if you want max. harvest and one controller per panel, get 4 of the Eco-worthy controllers and connect one panel to each. This would give a max. possible current of 75-78 amps if you chose to add 4 more panels. Total cost for 4 controllers is only $408.

Now as for cable size: 15 ga is much too thin. If I were running 4 panels into 4 controllers, I'd use 8awg. If running 4 panels into 2 controllers, I'd use 6 awg. If running 4 panels into one controller, then I'd use MC4 combiners to combine pairs of panels into 6awg, then join the 2 6awg sets into a 4 awg run to the controller.

If the controller is going to be close to the batteries, then I'd use 4 awg between controller and batteries, if longer, then 2 awg would be recommended. These numbers are off the top of my head, use an amperage chart for proper sizing, and don't be afraid to go one size larger for less loss. Also, make sure all connections are waterproof to minimize corrosion, you'll lose a lot of power from poor connections!
Agree with cable size. Much better to go larger than smaller, and allow cable to vibrate. The following is from experience: I had a 00 cable, 6" long connected from the 120 amp alternator to a connector on the bulkhead. After two years, the cable covering burnt off !! Someone on this forum told me that if cable is restricted and has a high number of amps going through it it will heat up. Never learnt that in Physics class !! I made a 14" loop of 00 cable to connect the two 6" apart points. Now it vibrates a bit, but stays cool. I use an infrared thermometer to measure cable temps of inaccessible cables. Something to think about.
macbeth is offline   Reply With Quote
Old 25-07-2015, 09:42   #11
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Yet another solar wiring question

Quote:
Originally Posted by edmundsteele View Post
My questions are: Any problems going series / parallel on the panels? Do you think that the controller is within spec for this set-up? Finally, 4 AWG gauge wire OK for controller to battery and 14 or 15 AWG gauge wire OK to wire up the solar panels?
Ed
The controller specs look fine.

There is a lot of debate about whether series or parallel connections are best. Series/parallel means you keep both camps happy . Personally, while I would like to see more evidence, I think a pure parallel connection is best if there is room for the correct wire size.

In terms of wire size the distance is important and without this information it is impossible to calculate the minimium diameter.

I would encourage you to measure the actual distance with a string led through where the wire will run. A rough estimate often underestimates the true distance as the wire needs to snake around to get through the various apertures. You will need a reasonably accurate length measurement to purchase the cable anyway.
noelex 77 is offline   Reply With Quote
Old 25-07-2015, 16:53   #12
Registered User
 
Nicholson58's Avatar

Cruisers Forum Supporter

Join Date: Jan 2011
Location: Caribbean live aboard
Boat: Camper & Nicholson58 Ketch - ROXY Traverse City, Michigan No.668283
Posts: 6,369
Images: 84
Re: Yet another solar wiring question

Quote:
Originally Posted by a64pilot View Post
I think you will hear, way upsize your wire at least to the controller and to go with parallel as opposed to any series.
Lets see
TOTALLY agree


I suggest you run nothing less than #6 AWG & parallel on all four.
Nicholson58 is offline   Reply With Quote
Old 25-07-2015, 18:29   #13
Registered User

Join Date: Aug 2012
Posts: 811
Re: Yet another solar wiring question

I also favour multiple controllers for the same reasons others have suggested. I have 2 Morningstar and one older Solarex controller.
The Morningstar controllers are connected to the house bank with their own panels.


The Solarex and one other panel is dedicated to the start battery while the boat is moored unused.


When we are away cruising I use a jack plug by a quaterberth in a box on the cable between the panel for the start battery and its controller to plug that panel instead into another cable connected to a controller connected to the house bank. As the alternator is keeping the start battery charged while cruising solar is then unnecessary on the start battery. That provides additional solar capacity for the house bank.


When running more than one panel to a single controller I think it's best to take separate cables from each panel to a junction box before the the controller. Then from there one short cable to the controller. Otherwise it's almost impossible to attach multiple wires to the small controller terminals. Doing that also keeps joins inside the boat. Don't skimp on cable size.


The controllers should be as close as practical to the batteries so there is minimal cable voltage drop in the regulated voltage. The inevitable voltage drop in the longer cables from the panels doesn't matter so much as its unregulated. Also having more than one controller means separate cables from the panels to controllers which means less loss in those long cables, as well as the advantages mentioned by others.



You can have multiple methods charging one battery / bank at the same time; i.e. solar controllers, engine alternator, and a shore power mains charger. Just make sure the relevant cables are suitable size.
GrahamHO is offline   Reply With Quote
Old 26-07-2015, 00:01   #14
Registered User

Join Date: Nov 2013
Location: Nice, France
Boat: Hunter Marine 38
Posts: 1,342
Re: Yet another solar wiring question

Concerning panel output, one factor often neglected is that in fixed horizontal mount you never get more then 70% of nominal output. Unless you are cruising in the tropics of course.


Envoyé de mon iPad à l'aide de Cruisers Sailing Forum
sailormed is offline   Reply With Quote
Old 26-07-2015, 02:57   #15
Registered User

Join Date: Aug 2012
Posts: 811
Re: Yet another solar wiring question

Quote:
Originally Posted by sailormed View Post
Concerning panel output, one factor often neglected is that in fixed horizontal mount you never get more then 70% of nominal output. Unless you are cruising in the tropics of course.


Envoyé de mon iPad à l'aide de Cruisers Sailing Forum
If they are fixed panels for say street lighting they should of course point due north or south and be at the same angle above horizontal as your geographic latitude.
But boats move around and for me the best average on a boat is horizontal.
GrahamHO is offline   Reply With Quote
Reply

Tags
solar, wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Modern Yet Cheap - Bluewater Worthy Yet Fast ? kman07 Dollars & Cents 21 31-05-2019 10:10
Yet Another Question About Inflatables OLDSON Auxiliary Equipment & Dinghy 3 09-09-2011 20:23
Yet Another Battery Choice Question . HarveyN Electrical: Batteries, Generators & Solar 2 04-08-2011 05:12
Yet Another ICW Question . . . daysailj Atlantic & the Caribbean 33 27-10-2010 07:34
Yet another teak finish question MABell Construction, Maintenance & Refit 12 21-09-2007 04:38

Advertise Here


All times are GMT -7. The time now is 15:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.