I am finally getting to my rewiring project and at the heart of my charging system is an older Xantrex Pathmaker Automatic Battery Switch which is wired up exactly as per the manual. It says any other charging system can be connected to "any battery". But it seems that once the system is connected, it treats all 3 banks (house and 2 starts) as 1 system. The start batteries need little recharging while the house would certainly require much more in the morning. This does not seem correct to me. And when connected, it would seem the lower voltage house would draw down the 2 start batteries. The manual also has the alternator connected directly to the starter as well. I am about to install my new large house bank and would like to get this correct. Not looking to spend more money but stay with this Xantrex system or do something different? If different , what? Proposed wiring diagram attached,, switch is marked as a Heart Pathmaker. BTW, the main house bank is a good 15 feet forward of the switch. Port engine is about 10 from the switch and the SB engine about 15 ft from it. House bank is 645 Ahr. - all FLA. Older Heart 2000w inverter is adjacent to the house bank.
thanks in advance...Ed

Attached Files
File Type: pdf proposed wire diagram.pdf (215.3 KB, 183 views)
Sailorman Ed is offline   Reply With Quote
Old 14-07-2016, 02:00   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,773
Re: Xantrex Pathmaker Automatic battery switch

The pathfinder are auto charge relays just like the acrs and vsrs which are commonly used today. And work fine.

They should be connected to each of the 3 batteries with large enough cable to handle all the charge loads. Likly direct to battery. The interconnecting negs also have to be big.

They are not switches. You are still missing all the switches in your diagram. Each start battery, house loads , and inverter should have battery switches. But then you need to seperate switched and un switched loads. Currently you have them combined on same bus. (Solar and electronics)


Inverter is a class t fuse not anl.

The wind gen should go to the house battery. As I wouldn't trust it to get the voltage up to engage the pathmaker. The "connect to any battery". Only holds true to decent size charging devices.

Alts connecting to starter post is common factory wiring. If you have small Alts <60a I would leave it the way it is. If you have larger external reg Alts then wire direct to house bank.

The pathfinder can not draw down batteries. It will only join batteries under a charging voltage. At which point all batteries will be charging.
smac999 is offline   Reply With Quote
Old 14-07-2016, 06:50   #3
Registered User
 
Sailorman Ed's Avatar

Join Date: Jun 2010
Boat: Gemini 105Mc+
Posts: 953
Images: 15
Send a message via Skype™ to Sailorman Ed
Re: Xantrex Pathmaker Automatic battery switch

Thanks smac999,
Yes, I left off the battery switches ( and lots of other components) as I was primarily interested in the Pathmaker. I do have a battery monitor for the house and the SB start battery since it is the farthest away. All my charging sources are near the stern while the large house bank in forward. I think I will connect all charging to the house and leave the Pathmaker as is.

Quote:
The pathfinder are auto charge relays just like the acrs and vsrs which are commonly used today
I spent time on the Blue Seas web site yesterday and don't see that the newer ACR products do anything differently.

Quote:
Inverter is a class t fuse not anl.
- I will have to look into class T fuses as I was not aware of them before I came across a chart of how much of an overload different types of fuses can handle yesterday. The current setup uses ANL and probably has for years before I got the boat.

Quote:
The interconnecting negs also have to be big.
they are

Quote:
you need to seperate switched and un switched loads.
help me to understand why. What does separating them do? Are they not all at the same voltage as the house bank? Or some other reason? I was under the impression that every connection ( including switches) adds a slight resistance to the circuit ( I remember something from MaineSail even showing a smaller fuse adding resistance)

One last question. How does the size of the hole in a terminal lug matter? Most of the busses have 1/4" studs but some of the cables have lugs with 5/16 or even 3/8" holes. Is it worthwhile to cut these off and crimp on new lugs with smaller holes?

thanks again for the review and input. Ed
Sailorman Ed is offline   Reply With Quote
Old 14-07-2016, 23:24   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,773
Re: Xantrex Pathmaker Automatic battery switch

Quote:
Originally Posted by Sailorman Ed View Post
Thanks smac999,
Yes, I left off the battery switches ( and lots of other components) as I was primarily interested in the Pathmaker. I do have a battery monitor for the house and the SB start battery since it is the farthest away. All my charging sources are near the stern while the large house bank in forward. I think I will connect all charging to the house and leave the Pathmaker as is.

I spent time on the Blue Seas web site yesterday and don't see that the newer ACR products do anything differently.

- I will have to look into class T fuses as I was not aware of them before I came across a chart of how much of an overload different types of fuses can handle yesterday. The current setup uses ANL and probably has for years before I got the boat.

they are

help me to understand why. What does separating them do? Are they not all at the same voltage as the house bank? Or some other reason? I was under the impression that every connection ( including switches) adds a slight resistance to the circuit ( I remember something from MaineSail even showing a smaller fuse adding resistance)

One last question. How does the size of the hole in a terminal lug matter? Most of the busses have 1/4" studs but some of the cables have lugs with 5/16 or even 3/8" holes. Is it worthwhile to cut these off and crimp on new lugs with smaller holes?

thanks again for the review and input. Ed
the main difference with the ACR's is they only do 2 batteries so you need to buy 2 of them and wire them side by side. vs the pathfinder which does 3 banks already. that and they are new. the old pathfinder may not last forever and and some point may have to be replaced.

Class T fuses are probably a newer product. I think they blow faster and will better protect an expensive inverter from a failure. all the new inverters call for class T fuses in the manuals.


I would cut off the lugs and use the correct size. especially 3/8 to 1/4 that is a hudge diff and the nut will probably barley grab.. the 5/16 may get away with.


with regards to separating the switched and unswitches loads I mean all the charging stuff should go straight to the battery. solar, wind, battery charger, pathmaker, bilge pump etc. when you turn off the house switch these stay connected to the battery on the battery side of the switch. and everything else goes after. electronics, lights, etc.

in your drawing you have solar and electronics comming off the same bus. so there is no place to properly add the house switch into your diagram. what you really need is an "unswitched" bus from the battery, and a "switched bus" after the battery switch.
smac999 is offline   Reply With Quote
Old 14-06-2022, 13:39   #5
Registered User
 
Wainui's Avatar

Join Date: Nov 2007
Location: Southern California
Boat: Cal 48 Wainui
Posts: 289
Re: Xantrex Pathmaker Automatic battery switch

Can the Heart Pathfinder combine the start bank with the house bank to start the engine.
Or only for charging.
Wainui is offline   Reply With Quote
Old 15-06-2022, 00:28   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,773
Re: Xantrex Pathmaker Automatic battery switch

Quote:
Originally Posted by Wainui View Post
Can the Heart Pathfinder combine the start bank with the house bank to start the engine.
Or only for charging.
I think they have an on / off / auto slider switch on them. But it’s been years since I have seen them.


Yes

“Connecting with a RemoteYou can force the PathMaker to “Connect” for five minutes foremergency starting by momentarily pressing the “Manual On” switchon the remote panel. “
smac999 is offline   Reply With Quote
Reply

Tags
battery

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heart Pathmaker switch making noise Sailorman Ed Electrical: Batteries, Generators & Solar 10 24-09-2022 19:24
Automatic Charging Relay/Xantrex Battery Combiner Admiral Cat Electrical: Batteries, Generators & Solar 5 13-09-2012 08:14
Rule Automatic Bilge Pump Switch #43 endoftheroad Plumbing Systems and Fixtures 13 26-12-2010 16:20
PathMaker Battery Combiner Override markpj23 Electrical: Batteries, Generators & Solar 6 24-12-2009 11:15
heart pathmaker ub1 Electrical: Batteries, Generators & Solar 4 08-10-2006 10:56

Advertise Here


All times are GMT -7. The time now is 10:29.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.