When is AGM 100% full charged at Float voltage?

Say your charger is set in power supply mode to 13.8V & you just keep it at this voltage all the time. Is there some tail current % figure at Float voltage that means full? I have read that at absorption voltage full means tail current of 0.5% of capacity, so just curious.

thanks
JmanC is offline   Reply With Quote
Old 13-03-2019, 05:22   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
When is AGM 100% full charged at Float voltage?

It should I believe be roughly the same.
If 13.8 is your float voltage and the only voltage your charger outputs, you will see a charge if the bank is down, it won’t be nearly as much charge current as higher voltages of course, but it will eventually charge.

Don’t quote me, but it will I think be a lower amperage, but ought to be close.

Of course if this is your float voltage then of course you want to leave the charger on always whenever possible

I don’t think being an AGM is relevant.

The .5% pertains to Lifeline batteries, it may be a different manufacturer uses a different number, although many or most don’t specify
a64pilot is offline   Reply With Quote
Old 13-03-2019, 06:17   #3
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: When is AGM 100% full charged at Float voltage?

The manufacturer's spec'd definition of Full will be measuring trailing amps at Absorb voltage.

Once you drop to a much lower Float voltage anywhere near that point, very little current will flow.

Best to get to the 100% Full before dropping to Float,

it would be possible (but not easy) to cross-reference to get to the same SoC at Float, but doing that regularly is not recommended, could easily take days.
john61ct is offline   Reply With Quote
Old 13-03-2019, 09:35   #4
Registered User

Join Date: Mar 2012
Location: On board in Leros, Greece
Boat: Hunter Legend 420 Passage
Posts: 863
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by JmanC View Post
Is there some tail current % figure at Float voltage that means full? ....
All you do is turn the charger back on and it will go to 14.4v and the tail current should 0.5% of the Ah capacity.
sailinglegend is offline   Reply With Quote
Old 13-03-2019, 09:51   #5
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by JmanC View Post
Say your charger is set in power supply mode to 13.8V

What brand/model charger?
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 14-03-2019, 06:38   #6
Registered User

Join Date: Mar 2019
Posts: 54
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by Maine Sail View Post
What brand/model charger?
Hi, It's Sterling pro ultra charge 50A.
JmanC is offline   Reply With Quote
Old 14-03-2019, 07:16   #7
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by sailinglegend View Post
All you do is turn the charger back on and it will go to 14.4v and the tail current should 0.5% of the Ah capacity.
Yes unfortunate that such kludgey workarounds are needed.

Sterling's PCU units' algorithm is certainly much better than a dumb egg-timer, and their user-defined setpoint programming is great.

But apparently they do not allow the Absorb Hold Time to be adjusted directly for current conditions?

_____
From Maine Sail's HowTo
https://marinehowto.com/installing-a...ttery-charger/

In an *ideal recharge* a battery charger would not drop to float voltage until the battery bank had attained the 99.5% to 100% SOC point. Almost all battery chargers out there, for marine use, drop to float before the battery bank has attained 100% SOC. While this makes them “safe“, for the manufacturers lawyers, it also means that in order to get back to 100% SOC it just takes a bit longer. At a dock this is not a huge deal, if we are getting into the mid to upper 90’s before the float transition. Once the charger drops to float this dramatically extends the time it takes to get to 100% SOC. The absorption cycle is perhaps the most important stage of charging and if it is too short, due to an egg-timer, the batteries can become chronically under charged and suffer the effects of sulfation.

Even the best AGM batteries still require well over 3 hours of absorption charging, under ideal conditions, to get anywhere near 100% SOC from 50% SOC, even when being changed at rates as high as 40% of Ah capacity or 40A for a 100Ah battery.
john61ct is offline   Reply With Quote
Old 14-03-2019, 10:40   #8
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: When is AGM 100% full charged at Float voltage?

Why would you use it in power supply mode with the batteries still connected?
a64pilot is offline   Reply With Quote
Old 14-03-2019, 11:04   #9
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by JmanC View Post
Hi, It's Sterling pro ultra charge 50A.

Power supply mode is just the old "battery charger" mode and it should still do bulk, absorb & float but not do the CEC turn-off thing.. The only way to get it to do 13.8V constant would be to set both absorption & float to the same value in the custom settings.

When they came out with California Energy Compliance chargers they kept the original battery charger mode and they just call it PS mode.
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 15-03-2019, 03:48   #10
Registered User

Join Date: Mar 2019
Posts: 54
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by john61ct View Post
Yes unfortunate that such kludgey workarounds are needed.

Sterling's PCU units' algorithm is certainly much better than a dumb egg-timer, and their user-defined setpoint programming is great.

But apparently they do not allow the Absorb Hold Time to be adjusted directly for current conditions?
From what I can tell with AGM presets, the absorption timer is too short (premature float) when sized to large banks, like 50A for 300-400AH, but when sized so it's 0.2C min charge rate in bulk it actually stays in absorption too long, usually until tail current is alot below 0.5%.
JmanC is offline   Reply With Quote
Old 15-03-2019, 03:49   #11
Registered User

Join Date: Mar 2019
Posts: 54
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by Maine Sail View Post
Power supply mode is just the old "battery charger" mode and it should still do bulk, absorb & float but not do the CEC turn-off thing.. The only way to get it to do 13.8V constant would be to set both absorption & float to the same value in the custom settings.

When they came out with California Energy Compliance chargers they kept the original battery charger mode and they just call it PS mode.
Thanks for that. I had no idea it worked like that in PS mode, alot more flexible.
JmanC is offline   Reply With Quote
Old 15-03-2019, 03:54   #12
Registered User

Join Date: Mar 2019
Posts: 54
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by a64pilot View Post
Why would you use it in power supply mode with the batteries still connected?
My understanding is. In a situation where there is mains power 24/7 & I have lead acid, I would use it so the battery stays full & is less cycled & the charger supplies loads. Power supply is the same as float & 13.8V just seems like a good set & forget voltage.
JmanC is offline   Reply With Quote
Old 15-03-2019, 05:22   #13
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by Maine Sail View Post
When they came out with California Energy Compliance chargers they kept the original battery charger mode and they just call it PS mode.

Didn’t know that. I assumed power supply would have been a single voltage
a64pilot is offline   Reply With Quote
Old 15-03-2019, 09:16   #14
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: When is AGM 100% full charged at Float voltage?

Yes that is what those words usually mean, no varying stages at all.
john61ct is offline   Reply With Quote
Old 15-03-2019, 11:11   #15
Registered User

Join Date: Mar 2012
Location: On board in Leros, Greece
Boat: Hunter Legend 420 Passage
Posts: 863
Re: When is AGM 100% full charged at Float voltage?

Quote:
Originally Posted by JmanC View Post
My understanding is. In a situation where there is mains power 24/7 & I have lead acid, I would use it so the battery stays full & is less cycled & the charger supplies loads. Power supply is the same as float & 13.8V just seems like a good set & forget voltage.
I think you have misunderstood Mr Sterling's badly written instruction manual. PS mode is used when no batteries are connected.

PS mode is a permanent Float setting so if you go sailing and come back to 24/7 shorepower the charger will not go up to an Absorption voltage so it will not charge the batteries properly.
sailinglegend is offline   Reply With Quote
Reply

Tags
agm, loa


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lifeline AGM's Fully Charged Voltage? frankson Electrical: Batteries, Generators & Solar 61 12-10-2018 12:54
Battery banks loosing voltage while being charged Kiss My Aft Electrical: Batteries, Generators & Solar 5 07-07-2014 15:08
float switch far away from pump... should I use the neg side for the float switch? felipe Electrical: Batteries, Generators & Solar 13 02-02-2014 13:20
Battery voltage conversion to % charged while lightly loaded at say 5a Fuss Electrical: Batteries, Generators & Solar 38 04-06-2012 17:29

Advertise Here


All times are GMT -7. The time now is 05:11.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.