What is this heavy copper cable?

My Bayfield 29c has these heavy copper cables connected to the thing...not sure what it's called when it's inside the hull...that the shroud attaches to. They are on both the port and starboard sides. Would it be grounding? Maybe lightening protection? I can't get to the boat now due to Covid travel restrictions, but I'd like to get opinions so I can know if I need to do further investigation when I get back there.
Attached Thumbnails
Click image for larger version

Name:	Big Copper Cables.jpg
Views:	1264
Size:	118.1 KB
ID:	230455  
and4ew is offline   Reply With Quote
Old 15-01-2021, 13:15   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,082
Images: 241
Re: What is this heavy copper cable?

Yes, it looks like a lightning mitigation downconductor bonding/grounding wire, from the chainplates (pictured), probably to an immersed ground plate(s), because (I believe) the keel is encapsulated , on the Bayfield 29.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 15-01-2021, 13:18   #3
Registered User

Join Date: Mar 2015
Location: Sail out of Mahone Bay, Nova Scotia
Boat: Bayfield 29C Cutter
Posts: 53
Re: What is this heavy copper cable?

Hi Gord, thanks for the response. Yes, the keel is encapsulated. So would the grounding plate be in the keel, on the outside of the keel, on the hull somewhere and painted over (so I haven't seen it)?
and4ew is offline   Reply With Quote
Old 15-01-2021, 13:24   #4
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,057
Re: What is this heavy copper cable?

Those round things look like speakers to play music for the barnacles.
https://www.pyiinc.com/sonihull/
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 15-01-2021, 13:31   #5
Registered User
 
Kelkara's Avatar

Join Date: Oct 2016
Location: Vancouver Island
Boat: Hullmaster 27
Posts: 1,041
Re: What is this heavy copper cable?

Quote:
Originally Posted by and4ew View Post
Hi Gord, thanks for the response. Yes, the keel is encapsulated. So would the grounding plate be in the keel, on the outside of the keel, on the hull somewhere and painted over (so I haven't seen it)?
I have a bronze plate bolted onto the hull from the bilge just above the keel. The cable connects to one of the bolts on the inside.
Attached Thumbnails
Click image for larger version

Name:	Capture1.JPG
Views:	289
Size:	102.6 KB
ID:	230458  
Kelkara is offline   Reply With Quote
Old 16-01-2021, 10:16   #6
Registered User

Join Date: Jun 2009
Location: Annapolis, MD
Boat: Gozzard, 44CC, 50'
Posts: 549
Re: What is this heavy copper cable?

For questions about Bayfields you might also want to contact Mike Gozzard at Mike@Gozzard.com. His dad, Ted, built the Bayfields and then took the design upmarket to the Gozzard line. Mike now runs the company and is extremely knowledgeable about both lines. The cable is most likely the rigging lightning ground. JMHO
Scrimshaw4 is offline   Reply With Quote
Old 16-01-2021, 10:16   #7
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: What is this heavy copper cable?

Quote:
Originally Posted by GordMay View Post
Yes, it looks like a lightning mitigation downconductor bonding/grounding wire, from the chainplates (pictured), probably to an immersed ground plate(s), because (I believe) the keel is encapsulated , on the Bayfield 29.
A second on this. You will find an immersed ground plate.
Cadence is offline   Reply With Quote
Old 16-01-2021, 10:21   #8
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,757
Re: What is this heavy copper cable?

I recommend to investigate and follow the cables to inspect their attachment points. Also, take the terminals off the chainplates and ground plates and clean it all for good contact before connecting tight.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 16-01-2021, 10:41   #9
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Thumbs up Re: What is this heavy copper cable?

Quote:
Originally Posted by GordMay View Post
Yes, it looks like a lightning mitigation downconductor bonding/grounding wire, from the chainplates (pictured), probably to an immersed ground plate(s), because (I believe) the keel is encapsulated , on the Bayfield 29.
Hurray for Gord and the term "lightning mitigation". Closer to the truth than " lightning protection". We should have shifted to that term years back.


Frankly
Frankly is offline   Reply With Quote
Old 16-01-2021, 13:35   #10
Registered User

Join Date: Sep 2007
Location: Queensland, Australia
Boat: None at present--between vessels. Ex Piver Loadstar 12.5 metres
Posts: 1,475
Re: What is this heavy copper cable?

Looks like part of a lightning protection system to me. Do not remove it.
Mike Banks is offline   Reply With Quote
Old 16-01-2021, 15:24   #11
Registered User

Join Date: Dec 2014
Location: Lake Macquarie, NSW, Australia
Boat: Beneteau Oceanis 45
Posts: 44
Re: What is this heavy copper cable?

I would like to from anybody who has had lightning protection such as this that has been struck by lightning. Did it do any good when after all there is so energy in lightning that it makes me wonder if those tiny little cables would be enough to defuse that energy?
philcun50 is offline   Reply With Quote
Old 16-01-2021, 18:04   #12
Registered User

Join Date: Mar 2016
Location: New England. USA.
Boat: McCurdy & Rhodes Custom 46
Posts: 1,474
Re: What is this heavy copper cable?

Just as an FYI for lightning I think of “heavy cable” as a conductor at least as big around as your thumb. And as straight as possible.

It could be bonding and lightning mitigation though.

Lightning is a reminder we are puny.
dfelsent is offline   Reply With Quote
Old 16-01-2021, 18:29   #13
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,757
Re: What is this heavy copper cable?

Quote:
Originally Posted by philcun50 View Post
I would like to from anybody who has had lightning protection such as this that has been struck by lightning. Did it do any good when after all there is so energy in lightning that it makes me wonder if those tiny little cables would be enough to defuse that energy?
They don’t defuse energy. They channel it to ground instead of the strike choosing it’s own path, which often pokes holes in fiberglass hulls.

6 AWG is considered good iirc
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 16-01-2021, 19:24   #14
Registered User

Join Date: Dec 2014
Location: Lake Macquarie, NSW, Australia
Boat: Beneteau Oceanis 45
Posts: 44
Re: What is this heavy copper cable?

I just re-read my previous post, terrible. I was asking if anyone that had experienced a lightning strike who had this type of grounding could report on the effectiveness of a small wire to mitigate damage.
I have spoken with people who worked in the lightning protection industry and they told me it was useless and may have even caused damage by it attracting lightning.
philcun50 is offline   Reply With Quote
Old 16-01-2021, 19:35   #15
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,047
Re: What is this heavy copper cable?

Quote:
Originally Posted by philcun50 View Post
I just re-read my previous post, terrible. I was asking if anyone that had experienced a lightning strike who had this type of grounding could report on the effectiveness of a small wire to mitigate damage.
I have spoken with people who worked in the lightning protection industry and they told me it was useless and may have even caused damage by it attracting lightning.
No, it does not attract lightning. I've done a number of lightning strike investigations and yes they are pretty much useless as 3,000,000volts at 30,000amps and moving at 270,000mph will vaporize that conductor in an instant.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
More than one Cable in a Cable Clam? sully75 Electrical: Batteries, Generators & Solar 19 17-11-2022 04:42
How heavy is too heavy? Arrandir Anchoring & Mooring 45 09-03-2017 03:35
1 Guage Starter Cable v. AWG 6 Boat Cable Gone2long Electrical: Batteries, Generators & Solar 0 10-01-2017 05:35
For Sale: 50' Telephone/Cable TV Combo Cable off-the-grid Classifieds Archive 5 27-10-2009 12:00

Advertise Here


All times are GMT -7. The time now is 22:41.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.