Re: Westerbeke 8.0BTDA - Voltage Drop Under Load

I did not realize that the rpm was dropping that much.
The manual governor (speed control ) normally has an adjustment to adjust speed droop If the change is consistent, then it may be a matter of a linkage adjustment. Did this condition occur gradually or a step change? A broken preload spring could cause this problem
lorenzoj is offline   Reply With Quote
Old 01-11-2020, 08:21   #17
Registered User

Join Date: Aug 2015
Boat: Hallberg-Rassy 53
Posts: 70
Re: Westerbeke 8.0BTDA - Voltage Drop Under Load

Lorenzo,

The genset has had the problem since the boat came to us.

There is certainly an adjustment to control generator RPMs. I have tinkered with that to change the no load speed of the genset. The issue is how much it drops under load.

I am in agreement that either the weights in the governor or the springs require service/replacement. I just haven't had the time to tackle this problem just yet.

In the meantime, I'll continue gathering information.

Someone with this specific genset must have experienced the same problem.....

Quote:
Originally Posted by lorenzoj View Post
I did not realize that the rpm was dropping that much.
The manual governor (speed control ) normally has an adjustment to adjust speed droop If the change is consistent, then it may be a matter of a linkage adjustment. Did this condition occur gradually or a step change? A broken preload spring could cause this problem
flippercarson is offline   Reply With Quote
Old 16-02-2021, 05:57   #18
Registered User

Join Date: Feb 2017
Location: Seattle
Boat: Defever 42 trawler
Posts: 6
Re: Westerbeke 8.0BTDA - Voltage Drop Under Load

I have the same generator and the same problem. 8 BTD. The governor set speed is easy enough to control by adjusting the solenoid pushrod length.
But, under load, it varies about 10Hz across 4.5kW: well within appropriate operating load, so that seems like a "weak" governor response.
Seems like the governor needs more authority or in control systems lingo, more gain. I don't know what it is yet, but will post when I do. Meanwhile, if you've resolved it, I'd love to hear.

A fuel filter or electrical adjustment both sound wrong to me.
mark krebs is offline   Reply With Quote
Reply

Tags
loa, westerbeke


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rapid voltage drop under small loads with new Trajan T-105 BluJu Electrical: Batteries, Generators & Solar 24 05-11-2018 13:08
Voltage Drop in AGM Under Load? neelie Electrical: Batteries, Generators & Solar 103 28-08-2014 10:47
Battery Charger Drops Voltage Under Load Heikki Marine Electronics 1 29-05-2012 05:41
Voltage drop under load, amps read 99% ?? VVD Electrical: Batteries, Generators & Solar 25 28-06-2011 15:25
Voltage Drops Under Load Reklobe Electrical: Batteries, Generators & Solar 22 09-06-2011 09:54

Advertise Here


All times are GMT -7. The time now is 22:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.