Re: Victron solar controller high charge voltage

Quote:
Originally Posted by mikedefieslife View Post
Well that's not what's happening. In the morning when it is 10c outside, the controller is putting out around 13.6v or similar probably due to the low sun. It is the middle of winter here. 15v doesn't seem to show up in the min/max display on the app until late afternoon. By then the temperature is closer to 18c.

Oh well anyway, I need to keep them below 15v anyhow so does that mean going against the temp comp ratings issued by Trojan?
in the morning it's still in bulk charge, it's not going to hit peak voltage untill the batteries are more full.

why are you running 400w of panel through a 20a controller??
smac999 is offline   Reply With Quote
Old 21-12-2018, 21:09   #17
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by smac999 View Post

why are you running 400w of panel through a 20a controller??
I agree, a bit over panelled. You should have a 100/30 controller.
mitiempo is offline   Reply With Quote
Old 21-12-2018, 23:52   #18
Registered User

Join Date: Aug 2016
Location: ABC's
Boat: Prout Snowgoose 35
Posts: 1,756
Re: Victron solar controller high charge voltage

20a is about right. These are old panels. It is very common in the industry to ever-so-slightly over-spec the array to take into account placement/angle, clouds, winter, and efficiency losses. It's even mentioned as a consideration on the Victron website.
mikedefieslife is offline   Reply With Quote
Old 21-12-2018, 23:52   #19
Moderator
 
Jim Cate's Avatar

Join Date: May 2008
Location: cruising SW Pacific
Boat: Jon Sayer 1-off 46 ft fract rig sloop strip plank in W Red Cedar
Posts: 21,187
Re: Victron solar controller high charge voltage

Quote:
why are you running 400w of panel through a 20a controller??
Not so much why, but more "how"? I too now have 400 watts of panels and I felt it necessary to buy the 100/30... it just barely meets the power spec itself.

Jim
__________________
Jim and Ann s/v Insatiable II, lying Port Cygnet Tasmania once again.
Jim Cate is online now   Reply With Quote
Old 22-12-2018, 00:02   #20
Registered User

Join Date: Aug 2016
Location: ABC's
Boat: Prout Snowgoose 35
Posts: 1,756
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by Jim Cate View Post
Not so much why, but more "how"? I too now have 400 watts of panels and I felt it necessary to buy the 100/30... it just barely meets the power spec itself.

Jim
Panels are mounted on a curved surface, so they rarely deliver more than 15a

I should add that I aware that the current configuration potentially exceeds the max input current for the controller, but as it's the height of winter, it's not a problem.

The panel in spring is to replace the 100w panels with 2x200w panels each with their own controller.
mikedefieslife is offline   Reply With Quote
Old 22-12-2018, 01:49   #21
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: Victron solar controller high charge voltage

Is reconditioning enabled on the Victron controller as automatic battery maintenance? You should disable it for AGM /GEL.
__________________
Lagoon 400S2 refit for cruising: LiFeYPO4, solar and electric galley...
CatNewBee is offline   Reply With Quote
Old 22-12-2018, 05:22   #22
Registered User
 
thomm225's Avatar

Join Date: Aug 2011
Location: Lower Chesapeake Bay Area
Boat: Bristol 27
Posts: 10,540
Re: Victron solar controller high charge voltage

The Victron Connect etc many times will read a bit off. it's still only .2 volts or so which is nothing to worry about.

I believe mine reads a bit low on the connect but about right with my meter (uncalibrated)

I have my Victron disconnected right now and my PWM controller connected to one 20 W panel to maintain my batteries charge while the boat is in the yard
thomm225 is online now   Reply With Quote
Old 22-12-2018, 05:47   #23
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by thomm225 View Post
The Victron Connect etc many times will read a bit off. it's still only .2 volts or so which is nothing to worry about.
Thomm, you keep stating this. Why don’t you try deliberately altering the battery absorption voltage by 0.2v. For example, from 14.6 to 14.4V. I think you may be surprised by the corresponding change in the current accepted by the battery.
noelex 77 is offline   Reply With Quote
Old 22-12-2018, 06:00   #24
Registered User
 
thomm225's Avatar

Join Date: Aug 2011
Location: Lower Chesapeake Bay Area
Boat: Bristol 27
Posts: 10,540
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by noelex 77 View Post
Thomm, you keep stating this. Why don’t you try deliberately altering the battery absorption voltage by 0.2v. For example, from 14.6 to 14.4V. I think you may be surprised by the corresponding change in the current accepted by the battery.
Sounds like a good test.

I'll try it when I reconnect the Victron in a couple months.

Today I'm painting my boot top and the section of the stern where my new (four stroke) outboard bracket will be remounted. I painted the bottom where the stands had been yesterday.

I'll also be doing a bit of touchup on the topside hull. Temp is already 50 degrees and it's only 0900
thomm225 is online now   Reply With Quote
Old 22-12-2018, 10:42   #25
Registered User

Join Date: Apr 2017
Posts: 133
Images: 1
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by noelex 77 View Post
…Why don’t you try deliberately altering the battery absorption voltage by 0.2v. For example, from 14.6 to 14.4V. I think you may be surprised by the corresponding change in the current accepted by the battery.
Noelex, wouldn't lowering the voltage reduce the current accepted? Or is that just in situation of line loss?
Yellowjacket is offline   Reply With Quote
Old 22-12-2018, 10:49   #26
Registered User

Join Date: Apr 2017
Posts: 133
Images: 1
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by mikedefieslife View Post
The battery sense module is stuck to side of one of the batteries in the middle of the bank. Then the wires attached to the positive and negative of the connected pairs i.e in the middle one the cables that make the parallel.

Think I'll just dial the setting back a bit for now, as there really isn't a lot that can be done.
When talking to Victron about the 712, they were adamant that the negative be the sole connection at the battery post to get accurate readings. I don't know if this applies also to Sense device.
Yellowjacket is offline   Reply With Quote
Old 22-12-2018, 11:09   #27
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Victron solar controller high charge voltage

An AH counter used to monitor a battery must be wired so **all** currents to and from the bank pass through its shunt. That does not need to mean right at the post.

Voltage closer to the post the better, but no exclusivity requirement.

Temperature best on the case body, maybe thermo coupling paste. Ideal sensor would be internal.
john61ct is offline   Reply With Quote
Old 23-12-2018, 03:35   #28
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Victron solar controller high charge voltage

Quote:
Originally Posted by Erik Dolson View Post
Noelex, wouldn't lowering the voltage reduce the current accepted?
Yes, that is correct. The important time is in the absorption phase. If you reduce the absorption voltage the charge rate will go down. The battery will charge slower.

This is not a great problem if you are going to spend a long time plugged into shore power, but with the limited charging times available from solar or a generator supply, the reduced charge rate can give less usable power and/or a lower state of charge, which reduces battery life expectancy.

It is always dangerous to generalise, but if the voltage at the battery is measured, with a properly calibrated meter it is quite common for the charging voltages to be below the manufacturer’s recommendations.

There are a couple of caveats. As the charge voltage is increased, battery efficiency drops. So if you alter the absorption voltage and increase the charging current, not quite all of this extra current is being translated into usable capacity. The second factor is once the battery is full it will still accept some charge at higher voltages, but this is not translated to any more usable capacity. Another way of looking at this factor, is battery efficiency drops to zero as the battery becomes fully charged. This does fool some people who set very long absorption times believing all the current entering the battery is being converted into usable capacity.
noelex 77 is offline   Reply With Quote
Old 23-12-2018, 06:27   #29
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Victron solar controller high charge voltage

A lead battery does need to regularly get to mfg defined 100% Full state in order to maximize longevity.

Besides setting Absorb V at the high end, that needs to be held long enough to get there, even if 95% of the charge current is not being accepted for the last few hours of the charge cycle.

Of course other concurrent loads can change thing, need to keep any trivial "load dumps" from preventing that "long tail" process.

Of course going past the endAmps stopping point for too many hours too frequently can reduce AGM longevity, FLA just need to keep watered.

But that is very rare, and usually impossible with most solar setups, given the sun usually sets.

Going to Float **way too early* is very common, maybe 90+% of charge sources left at their defaults.

But cross-referencing whatever Absorb Hold Time and Absorb Return adjustments the source allows against an ammeter regularly, those two goals are not that hard to balance, as you get more familiar with usage patterns vs changing conditions, can become instinctive.

Of course the ideal is shunt-based charge regulation that transitions to Float based directly off trailing amps acceptance hitting the endAmps spec.

As a bank ages and wears, this gets harder, takes longer, and at a certain SoH% does eventually become impossible to reach the spec'd endAmps.

Nothing to do with overcharging, and may in fact indicate it's time to schedule replacing that bank.

An alternative spec to use is Deka's:

> Absorption End Point = Current change over 1 hour period of less than 0.1A

Note the*current***change** point there, no actual absolute value given for endAmps

Thus it will work even with an old worn-out no-name Wally's batt that has trouble hitting .05C

But when that batt is fresh and new, and you can't find the specific protocol from the maker, then .005C is a good default to start with, especially for FLA.

For a sub-par*AGM, maybe use .02C if you're worried about overcharging.

As a side note, if you can't easily find detailed specs like endAmps from a batt maker, it's a sure sign IMO that you should avoid*purchasing*that brand.

The point is to have an objective benchmark to hit consistently "most cycles" if possible,

rather than assuming your charge source's "going to float" is an indicator of the bank being Full.
john61ct is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Victron BlueSolar charge controller mikedefieslife Electrical: Batteries, Generators & Solar 84 14-03-2021 04:46
[SOLD] For Sale - Victron BlueSolar 100/50 solar charge controller with Bluetooth dongle Bleemus General Classifieds (no boats) 4 21-04-2018 20:27
Victron BlueSolar Charge Controller MPPT 75/115 "Load" Terminal Question PetePetePete Electrical: Batteries, Generators & Solar 5 30-04-2017 03:44
Solar Charge Controller and Solar Flares newhaul Electrical: Batteries, Generators & Solar 24 06-10-2015 07:39
Solar Charge Controller Voltage and Current Matching DefinitelyMe Electrical: Batteries, Generators & Solar 4 12-06-2013 08:40

Advertise Here