Old 16-08-2022, 15:57   #1
Registered User

Join Date: Aug 2022
Posts: 3
Victron Smart Shunt conflicting instructions.

Victron provides conflicting technical information on the correct way to connect a DC Smart Shunt in dual battery system.
I plan to use the aux input to monitor the starter battery voltage.

Which side of the Victron SmartShunt should the starter battery negative terminal be connected?

I think this is correct with the starter battery connected to the smart shunt load minus.

pic attached
https://www.dropbox.com/s/86t70756l1...ctron.jpg?dl=0

However this picture from a Victron instruction video shows the starter battery negative connected to the smart shunt battery minus.

pic attached
https://www.dropbox.com/s/istly33coe...ctron.jpg?dl=0

Attached Thumbnails
Click image for larger version

Name:	victron.jpg
Views:	181
Size:	48.6 KB
ID:	262981   Click image for larger version

Name:	dc shunt victron.jpg
Views:	244
Size:	352.2 KB
ID:	262982  

mrlorin is offline   Reply With Quote
Old 16-08-2022, 16:26   #2
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

Welcome aboard CF, great first post / question!

Interesting, I hadn't noticed this discrepancy before.

Both might give the same result but that depends on how 'smart' the shunt really is.

Intuitively I think it should be connected to the smart shunt load minus.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-08-2022, 16:52   #3
Registered User
 
jt11791's Avatar

Join Date: Aug 2017
Location: Cruising the world
Boat: Hylas 54
Posts: 414
Re: Victron Smart Shunt conflicting instructions.

Makes no difference. It's just sensing voltage, no measurable current, so can be on either side of the shunt.
jt11791 is offline   Reply With Quote
Old 16-08-2022, 17:17   #4
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

The problem is the voltage across the shunt varies as the house load current varies. The voltage across the shunt could be as high as 100mV (I forget ATM what shunt voltage is used by Victron).

If the Victron smart algorithm copes and adjusts for the varying shunt voltage, then all is good otherwise connecting it to the smart shunt battery minus in the same as putting a small variable voltage source in series with a voltmeter.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-08-2022, 17:30   #5
Registered User

Join Date: Aug 2022
Posts: 3
Re: Victron Smart Shunt conflicting instructions.

I also plan to install a voltage sensitive relay to enable the alternator to charge the system battery and the solar panel to charge the start battery.

https://www.kickassproducts.com.au/B...groupid=&adid=

If the start battery is linked to the shunt battery negative any current flowing through the VSR would not be measured by the shunt.

Have I just answered my question?
mrlorin is offline   Reply With Quote
Old 16-08-2022, 19:58   #6
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 2,936
Re: Victron Smart Shunt conflicting instructions.

The starting battery negative needs to be connected to the load side of the shunt. If it is connected the the battery side with the house battery, then any current going into or out of the starting battery would be totaled with the house battery, and throw off the SOC calculation.
__________________
-Warren
wholybee is offline   Reply With Quote
Old 16-08-2022, 20:13   #7
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: Victron Smart Shunt conflicting instructions.

Eng bat needs to go on the load side. Top pic is correct
smac999 is offline   Reply With Quote
Old 16-08-2022, 21:01   #8
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by wholybee View Post
The starting battery negative needs to be connected to the load side of the shunt. If it is connected the the battery side with the house battery, then any current going into or out of the starting battery would be totaled with the house battery, and throw off the SOC calculation.
No. The starting battery current will not flow through the shunt in either case.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-08-2022, 21:04   #9
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by smac999 View Post
Eng bat needs to go on the load side. Top pic is correct
While I agree it should go to the load side, it is hard to argue that the other pic is wrong when the information is supplied by the manufacturer.

It is possible that both ways are correct.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-08-2022, 21:40   #10
Registered User
 
AKA-None's Avatar

Join Date: Oct 2013
Location: Lake City MN
Boat: C&C 27 Mk III
Posts: 2,647
Victron Smart Shunt conflicting instructions.

Which side is common between the two batteries

That’s where is will measure as 0

The shunt goes from measured battery ground out to common ground so it will measure voltage from common ground to battery plus

If it weren’t for them tying common ground to one side of the shunt then you would be able to put the shunt on the battery plus side. But if you try that the all your voltage readings would be backwards


I think I said that correctly but let me think about that a bit :-)
__________________
Special knowledge can be a terrible disadvantage if it leads you too far along a path that you cannot explain anymore.
Frank Herbert 'Dune'
AKA-None is offline   Reply With Quote
Old 17-08-2022, 01:21   #11
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 2,936
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by Wotname View Post
No. The starting battery current will not flow through the shunt in either case.
It would depend on what device. As drawn, no the starter current wouldn't flow through the shunt. But a charger connected to the Starter battery and grounded to the ground bus would if the battery were connected to the battery side of the shunt. Any other loads that might be connected to the Start battery and grounded to the negative bus would flow through the shunt.

And if connected to the battery side, then with a VSR current would flow from the alternator to the house battery without going through the shunt.
Both of those situations would cause an incorrect SOC reading. Absolutely, no question, the start battery negative needs to go on the load side.

The picture that shows the connection to the load side is directly out of the smart shunt manual, and is correct.
__________________
-Warren
wholybee is offline   Reply With Quote
Old 17-08-2022, 01:55   #12
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by Wotname View Post
While I agree it should go to the load side, it is hard to argue that the other pic is wrong when the information is supplied by the manufacturer.

It is possible that both ways are correct.
No it’s not correct. In the 2nd pic the amp meter would only show a neg draw. Even if the engine was running. It will start at 100% Soc and only go down. No mater how much you run the engine the battery monitor would never gain Soc or show pos amps. Eventully the display would always show O% even if the battery was full.
smac999 is offline   Reply With Quote
Old 17-08-2022, 05:43   #13
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by smac999 View Post
No it’s not correct. In the 2nd pic the amp meter would only show a neg draw. Even if the engine was running. It will start at 100% Soc and only go down. No mater how much you run the engine the battery monitor would never gain Soc or show pos amps. Eventully the display would always show O% even if the battery was full.
I think it is safe to assume Victron meant to show the green box as "Loads and Chargers" just like the green box in the 1st picture otherwise the main battery would never get charged.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 17-08-2022, 15:56   #14
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Victron Smart Shunt conflicting instructions.

The Victron first document is absolutely correct; the second document is a special case. In general, there is no intent to measure the 1 to 2 Ahrs that it takes to start a marine diesel. House bank B- on the high side of the shunt (marked Battery); everything else on the low side of the shunt. It is that simple.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 17-08-2022, 16:48   #15
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,433
Re: Victron Smart Shunt conflicting instructions.

Quote:
Originally Posted by CharlieJ View Post
The Victron first document is absolutely correct; the second document is a special case. In general, there is no intent to measure the 1 to 2 Ahrs that it takes to start a marine diesel. House bank B- on the high side of the shunt (marked Battery); everything else on the low side of the shunt. It is that simple.
The start current is not flowing through the shunt in the second document (nor in the first document).
What is the special case shown by the second document?

I only see drafting errors in the green panel on the second document.

The final note on the second document states the negative of both batteries must be common. The first document does not achieve this requirement.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bluetooth Smart Shunt - anything other than Victron? mvweebles Electrical: Batteries, Generators & Solar 26 03-08-2022 12:43
To shunt or not to shunt JimMann Electrical: Batteries, Generators & Solar 22 07-06-2022 07:19
Alternator output integrated into a smart Shunt mcon12000 Electrical: Batteries, Generators & Solar 6 08-02-2022 23:33
Conflicting "rules" for trimming jib? OldFrog75 Seamanship & Boat Handling 4 25-09-2013 06:17
Conflicting Info About Size of Second Anchor... DennisM Anchoring & Mooring 13 25-03-2010 17:18

Advertise Here


All times are GMT -7. The time now is 16:51.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.