Victron 150/45 for 550W 13A panel

The Victron calculator says I need a Victron 150/45 controller for a single 550W 13A 42W panel. As I understand it the 150 in the title refers to Volt and the 45 means A. So why do I need a 45A controller for a 13A panel? Is it correct?

https://mppt.victronenergy.com/
Nor is offline   Reply With Quote
Old 01-09-2022, 23:31   #2
Registered User

Join Date: Nov 2018
Location: San Diego
Boat: Shannon 50 Ketch
Posts: 744
Re: Victron 150/45 for 550W 13A panel

I'm wondering if you have your panel specs right - is it a single 550w panel as you say? But you wrote 550W 13A 42W - some of these numbers may be incorrect, it can't be both 550w and 42w.

I am thinking it is 550w at 42vdc, which would equal 13a, but 13a at 42v has to be "massaged" (by the controller) into 42a at 13v in order to feed it into your 12v battery bank (unless you have a 24v batt bank in which case it has to massage it to appx 21amps at 26v.).

So, if you have a 12v bank, you do need the 150/45. If you have a 24v bank, I think you could use the MPPT 100/30 (because final output will be @ 21amps at 26v).

Hope this helps.
jordanbigel is offline   Reply With Quote
Old 01-09-2022, 23:50   #3
Nor
Registered User

Join Date: Mar 2018
Posts: 118
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by jordanbigel View Post
I'm wondering if you have your panel specs right - is it a single 550w panel as you say? But you wrote 550W 13A 42W - some of these numbers may be incorrect, it can't be both 550w and 42w.

I am thinking it is 550w at 42vdc, which would equal 13a, but 13a at 42v has to be "massaged" (by the controller) into 42a at 13v in order to feed it into your 12v battery bank (unless you have a 24v batt bank in which case it has to massage it to appx 21amps at 26v.).

So, if you have a 12v bank, you do need the 150/45. If you have a 24v bank, I think you could use the MPPT 100/30 (because final output will be @ 21amps at 26v).

Hope this helps.
Thanks! Yes, that was a typo, it should be 42V not W. And thanks for the explanation showing why I need the 45A.
Nor is offline   Reply With Quote
Old 02-09-2022, 00:05   #4
Nor
Registered User

Join Date: Mar 2018
Posts: 118
Re: Victron 150/45 for 550W 13A panel

One thing I haven't thought about is if the 42A is too much current to charge my two 90A batteries. I was planning to upgrade the batteries in the future, and thought the 550W panel will give benefits of also having more power available during the daytime for charging phones, tablets, fridge etc.

But can 42A be too much for two car batteries? It seems CCA is >650, is that relevant to charging also?
Nor is offline   Reply With Quote
Old 02-09-2022, 05:54   #5
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,627
Re: Victron 150/45 for 550W 13A panel

Your batteries will only accept 42a when they need the charge, otherwise the expensive blue regulator will be doing what it is designed to do,manage the charge profile.
Sailmonkey is offline   Reply With Quote
Old 02-09-2022, 06:46   #6
Registered User

Join Date: Dec 2009
Location: Australia
Boat: BUILT!!! Roberts Mauritius 43ft
Posts: 4,153
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by Sailmonkey View Post
Your batteries will only accept 42a when they need the charge, otherwise the expensive blue regulator will be doing what it is designed to do,manage the charge profile.

Is it necessary to have a "load"? Does the controller direct current to the "load" only if the batteries are fully charged?
coopec43 is offline   Reply With Quote
Old 02-09-2022, 07:04   #7
JBP
Registered User
 
JBP's Avatar

Join Date: Sep 2016
Location: Lake Erie, PA
Boat: Jeanneau Tonic 23
Posts: 555
Re: Victron 150/45 for 550W 13A panel

You can adjust Victron controllers to limit their output current, so you could set your controller to output a max of 30A (or whatever). Note that your solar panel will only output full power under ideal conditions anyway. Most of the time you will only get 3/4 or 1/2 the maximum possible, so you aren't really losing much by restricting the maximum output. Thus you could use a 30A controller without losing much.
JBP is offline   Reply With Quote
Old 02-09-2022, 07:07   #8
JBP
Registered User
 
JBP's Avatar

Join Date: Sep 2016
Location: Lake Erie, PA
Boat: Jeanneau Tonic 23
Posts: 555
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by coopec43 View Post
Is it necessary to have a "load"? Does the controller direct current to the "load" only if the batteries are fully charged?
No, you don't need to use the "load" output on Victron controllers. The load output has some extra controls, like being able to turn it on or off at night, but it is perfectly fine to ignore the load output.
JBP is offline   Reply With Quote
Old 02-09-2022, 07:10   #9
Registered User

Join Date: Nov 2018
Location: San Diego
Boat: Shannon 50 Ketch
Posts: 744
Re: Victron 150/45 for 550W 13A panel

The "load" connections on the MPPT are optional, they allow you to wire up something which will draw power directly from the controller. The only thing I have ever heard it being used for was to power an external cooling fan (presumably for keeping the MPPT cool, I guess). I suspect other people have found other uses for this which I am unaware.
jordanbigel is offline   Reply With Quote
Old 02-09-2022, 08:51   #10
Nor
Registered User

Join Date: Mar 2018
Posts: 118
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by JBP View Post
You can adjust Victron controllers to limit their output current, so you could set your controller to output a max of 30A (or whatever). Note that your solar panel will only output full power under ideal conditions anyway. Most of the time you will only get 3/4 or 1/2 the maximum possible, so you aren't really losing much by restricting the maximum output. Thus you could use a 30A controller without losing much.
Thanks!
How should I set the limit? The batteries are car batteries and I haven't found any detailed max charge limit, only the >650 CCA.
For two 90A batteries is 30A a safe setting?
Nor is offline   Reply With Quote
Old 02-09-2022, 08:55   #11
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,972
Re: Victron 150/45 for 550W 13A panel

The Victron 100/50 would also be an acceptable alternative to the 150/45 (and it appears to be a few dollars cheaper).
rslifkin is offline   Reply With Quote
Old 02-09-2022, 09:57   #12
JBP
Registered User
 
JBP's Avatar

Join Date: Sep 2016
Location: Lake Erie, PA
Boat: Jeanneau Tonic 23
Posts: 555
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by Nor View Post
Thanks!
How should I set the limit? The batteries are car batteries and I haven't found any detailed max charge limit, only the >650 CCA.
For two 90A batteries is 30A a safe setting?
I believe the rule of thumb for car batteries is to charge them at no more than 10% of their Amp hour capacity, thus two 90 AH batteries in parallel should be charged at no more than 18A. However I expect your batteries would have to be very dead before they would accept 18A. You also have other stuff running. Perhaps limit it to 20A and see what happens. You can always adjust the settings.
JBP is offline   Reply With Quote
Old 02-09-2022, 17:11   #13
Registered User

Join Date: Dec 2009
Location: Australia
Boat: BUILT!!! Roberts Mauritius 43ft
Posts: 4,153
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by jordanbigel View Post
The "load" connections on the MPPT are optional, they allow you to wire up something which will draw power directly from the controller. The only thing I have ever heard it being used for was to power an external cooling fan (presumably for keeping the MPPT cool, I guess). I suspect other people have found other uses for this which I am unaware.
I wondered what it could be used for. Maybe heating water, bilge blower......?
coopec43 is offline   Reply With Quote
Old 02-09-2022, 19:01   #14
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,790
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by coopec43 View Post
I wondered what it could be used for. Maybe heating water, bilge blower......?
on off grid houses they are used for things like outside lights. the load can be set to turn on at dusk. and stay on for a few hours. or turn off at daylight (based on the controller seeing sun)

I have never used it on a boat. I think I've read people using it for the anchor light. basically it can turn the light on and off based on if the panels see sun or not. so night time or bad weather the anchor light comes on
smac999 is online now   Reply With Quote
Old 02-09-2022, 19:06   #15
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,790
Re: Victron 150/45 for 550W 13A panel

Quote:
Originally Posted by Nor View Post
Thanks!
How should I set the limit? The batteries are car batteries and I haven't found any detailed max charge limit, only the >650 CCA.
For two 90A batteries is 30A a safe setting?
I would not limit the controller. the batteries will limit themselfs

the problem with limited the controller is it has no idea how much is going into the batteries or how much is being consumed. if you are running a bunch of stuff one day drawing 20a. and the controller is set to 30a max. then only 10a is left going into the battery, and you are limited the solar for no reason. you could have had 20a going to the batteries

generally flooded batteries take 20% and AGM take 40%. so 200ah of flooded will take 40a no issue. you will likly never see 40a from the panels and some of that will be used before it reaches the batteries anyways. lights fridge etc

the fireflys and lifelines actually want min 40%
smac999 is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
[SOLD] Victron BlueSolar 150/85 Tr MPPT Contoller geekoman General Classifieds (no boats) 4 10-04-2021 07:15
Anyone tried this 24V 13A 60bar RO pump? svseachange Plumbing Systems and Fixtures 0 05-10-2019 05:18
renogy solar panel for sale $150 newhaul Electrical: Batteries, Generators & Solar 0 07-08-2016 21:34
For Sale: Kyocera KC120 solar panel and asc contoller $150 sywhynot Classifieds Archive 4 10-03-2014 16:41
Victron Remote Panel Problem AAD Electrical: Batteries, Generators & Solar 1 08-02-2011 19:10

Advertise Here


All times are GMT -7. The time now is 22:11.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.