Quote:
Originally Posted by smac999
Sounds like you don’t have galvanic isolators. Or they are being bypassed.
Take a reading with boat not plugged in. This is your Baseline. Then plugged in main ac breaker off (double pole Breaking the neutral?) . Then ac breaker on. . Reading Should never change.
I would look at the magnum netreal wiring. The Input and output neutreals need to be separated. When the inverter does not have input power it will join the netreal to ground. Which will then bypass the galvanic isolator if there a neutreal connection to the dock and the output neutrals are not separated. Once you turn power (hot) to the magum it opens that bond and the galvanic isolator is no longer bypassed. Which is maybe the reason you see change with certain ac breakers.
Pretty common to see the inverter netreaul wiring wrong. (All common) That only causes the isolator to be byosssed for 30 secs each time the boat is plugged in. And Likly not causing zinc issues. That issue will blow gfci / elci. Breakers though.
|
Thanks for responding, when I made post you are one of the people that I had would take a look.
We do have a Dairyland Galvanic Isolator, I checked it in December and it seemed to pass recommend test. It is a model with capacitors.
I did more readings with the Silver Cell the bonding system maintains a voltage of -.980 V with shore cords connected or disconnected seems to have no effect.
The voltage drops to about -.850 V for a few seconds when you cycle the main breaker. But then returns to -.980
It would appear that the boat is adequately protected???
I traced the power wires to the
charger inverter. The neutrals both terminate on the neutral strip at the main panel. The power comes from the power bus of the main panel. the power feed from the inverter goes to main panel feeding the port and starboard outlets but not
water heater.
Before leaving for the
Caribbean we plugged into a marina in
florida and tripped their new ground fault
equipment. On investigation we found that as long as only one cord at time was plugged in we did not trip it.
I found that the wrong rotary switch had been installed separating the neutrals from each other. I replaced with proper switch now in generator setting the
shore power hot and neutrals are all kept separate.
I have not been back to a marina with ground fault equipment since that change.
I also just put my DC clamp meeter on the ground wire at the Galvonic isolator. and am getting reading of .05 to .03 Amp . I assume that is too high????
Shut all AC circuits off and still get the same reading.
Thanks for taking time to read!
Bob