Using copper flat bar to connect the batteries in a battery bank

Does anybody know what size copper bar would I need to get the same effect as 70mm battery cables?

I have always thought that the surface area of the strands were important, so it is not as simple as to calculate the area of a cross section of flat bar. Is this true?

Any other input as to using copper flat bar would be appreciated.

Thanks!
Zai is offline   Reply With Quote
Old 08-01-2017, 04:30   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,394
Images: 241
Re: Using copper flat bar to connect the batteries in a battery bank

See ➥ https://www.copper.org/applications/...us_table3.html
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-01-2017, 04:31   #3
Registered User
 
Reefmagnet's Avatar

Join Date: May 2008
Location: puɐןsuǝǝnb 'ʎɐʞɔɐɯ
Boat: Nantucket Island 33
Posts: 4,864
Re: Using copper flat bar to connect the batteries in a battery bank

Skin effect where current travels along the surface of a conductor only becomes a consideration at high frequencies, so the same cross sectional area applies. Kind of. In reality you can use proportionally smaller barstock as it heats up less because it will have better heat dissipation because of its surface area to volume ratio and lack of insulation.
Reefmagnet is offline   Reply With Quote
Old 08-01-2017, 05:13   #4
mrm
Registered User

Join Date: Feb 2011
Location: Poland, EU
Boat: crew on Bavaria 38 Cruiser
Posts: 654
Re: Using copper flat bar to connect the batteries in a battery bank

Seems like a good idea, however.. think of how much mechanical stress battery terminals will be subjected to because of thermal expansion and contraction of such solid bar, when batteries are firmly fixed. There is a reason solid copper interconnects used in LiFePO bank assemblies are shaped the way they are.
mrm is offline   Reply With Quote
Old 08-01-2017, 05:46   #5
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,394
Images: 241
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by mrm View Post
... think of how much mechanical stress battery terminals will be subjected to because of thermal expansion and contraction of such solid bar ...
Not much really.
The rate of thermal expansion for copper is a little less than .001" per inch of length per 100 degrees (F) delta T.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-01-2017, 06:16   #6
Registered User
 
Matt Johnson's Avatar

Join Date: Mar 2010
Location: Annapolis MD
Boat: Building a Max Cruise 44 hybrid electric cat
Posts: 3,199
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by GordMay View Post
Strange they don't list the voltage for this chart. It's for 60 Hz AC, and it should be listed as 120 volts if that's what it's for.

Matt
__________________
MJSailing - Youtube Vlog -
Matt Johnson is offline   Reply With Quote
Old 08-01-2017, 06:23   #7
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by Zai View Post
............. I have always thought that the surface area of the strands were important, so it is not as simple as to calculate the area of a cross section of flat bar. ............
What makes you think that? Did you see that on a boating forum?

A copper bar will be rigid and if there is any movement of the batteries, there will be stress on the terminals. If it was a good idea, boat manufacturers would be using copper bars. They are not.

Use cable like everyone else.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 08-01-2017, 06:24   #8
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,394
Images: 241
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by funjohnson View Post
Strange they don't list the voltage for this chart. It's for 60 Hz AC, and it should be listed as 120 volts if that's what it's for.
Matt
The only part Voltage plays in conductor ratings is insulation, not ampacity.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-01-2017, 07:36   #9
mrm
Registered User

Join Date: Feb 2011
Location: Poland, EU
Boat: crew on Bavaria 38 Cruiser
Posts: 654
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by GordMay View Post
Not much really.
The rate of thermal expansion for copper is a little less than .001" per inch of length per 100 degrees (F) delta T.
Gord, I know that the dimension change will be minuscule, nevertheless the forces involved will still be substantial. I will try to illustrate my thinking with a mental experiment. Let us imagine a piece of metal (copper) bar placed between two absolutely unyielding surfaces. When the temperature rises, the metal tries to expand, however surfaces it is trapped between do not yield, therefore that dimension remains unchanged. Am I wrong in thinking, that for that condition to be met, the stress the metal is subject to has to reach the yield strength of the metal? For copper this would be approx. 70 MPa. Am I correct calculating, that for a sample copper bar with a cross section of 0.04 x 0.01 m (4 x 1 cm) the force acting on terminals (should they not yield) would be 70 * 10^6 * 0.0004 = 28000 N ?

Edit: what Rwidman wrote above is probably a better way of expressing what I tried. Battery posts are not designed for stresses coming from attachment to rigid bars, be it from thermal expansion or more likely from battery movement.
mrm is offline   Reply With Quote
Old 08-01-2017, 07:48   #10
Registered User
 
Cavalier's Avatar

Join Date: Dec 2010
Location: Houston, TX
Boat: Beneteau 461 47'
Posts: 927
Images: 1
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by mrm View Post
Gord, I know that the dimension change will be minuscule, nevertheless the forces involved will still be substantial. I will try to illustrate my thinking with a mental experiment. Let us imagine a piece of metal (copper) bar placed between two absolutely unyielding surfaces. When the temperature rises, the metal tries to expand, however surfaces it is trapped between do not yield, therefore that dimension remains unchanged. Am I wrong in thinking, that for that condition to be met, the stress the metal is subject to has to reach the yield strength of the metal? For copper this would be approx. 70 MPa. Am I correct calculating, that for a sample copper bar with a cross section of 0.04 x 0.01 m (4 x 1 cm) the force acting on terminals (should they not yield) would be 70 * 10^6 * 0.0004 = 28000 N ?



Edit: what Rwidman wrote above is probably a better way of expressing what I tried. Battery posts are not designed for stresses coming from attachment to rigid bars, be it from thermal expansion or more likely from battery movement.
The biggest issue is not going to be the linear thermal expansion of the bus bar, but the near inability to perfectly secure the batteries. Any motion of the boat will lead to differences in position between the terminals and the [yielding] plastic of the battery housing that is probably being used to clamp said battery in position. As mentioned above, the cyclic shear loads on the base of the terminals over time will lead to fatigue outside of the design parameters of the terminals themselves. One benefit of [curved] battery cables between terminals of different batteries is that they act as strain relievers for the terminals themselves.

Sent from mTalk
__________________
"By day the hot sun fermented us; and we were dizzied by the beating wind. At night we were stained by dew, and shamed into pettiness by the innumerable silences of stars."
Cavalier is offline   Reply With Quote
Old 08-01-2017, 08:33   #11
Zai
Registered User

Join Date: Mar 2011
Location: Athens
Boat: 2011 Bavaria 36 Cruiser
Posts: 225
Re: Using copper flat bar to connect the batteries in a battery bank

Wow!
Thanks for all of the useful information.
The reason I am considering this is because of the cramped quarters in the battery compartment.
The batteries are good and tight in place, but there is of course the likelihood that they will wiggle a bit from time to time.
If I go ahead this idea I think I will get some bars cut with high pressure water with a couple of s shapes in them. That should take care of the physical stress.

On a related matter, what\s the consensus on battery fuses?
Is it a consensus to use a fuse on each battery or will one suffice at the ground terminal?
Zai is offline   Reply With Quote
Old 08-01-2017, 09:39   #12
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,661
Re: Using copper flat bar to connect the batteries in a battery bank

batteries move. use wire and leave enough bend in it so they can move.
smac999 is online now   Reply With Quote
Old 08-01-2017, 09:50   #13
Registered User

Join Date: May 2016
Posts: 84
Re: Using copper flat bar to connect the batteries in a battery bank

Insulated cable is always used to inter connect batteries. Bus bars are used to make a battery out of individual cells. It's practically impossible to align two batteries well enough to prevent stress on the battery terminals. Use flexible insulated cable. If you make bus bars, insulate them to prevent accidents. Certainly easier and probably cheaper to use cable, unless you have free copper stock.

You will never find a concensus of opinion on battery fuses. Some say fuse everything. Some say don't fuse the battery.

Don't fuse the ground. Don't fuse the ground. Do not fuse the ground.
Redpcx is offline   Reply With Quote
Old 08-01-2017, 09:58   #14
Registered User
 
Matt Johnson's Avatar

Join Date: Mar 2010
Location: Annapolis MD
Boat: Building a Max Cruise 44 hybrid electric cat
Posts: 3,199
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by GordMay View Post
The only part Voltage plays in conductor ratings is insulation, not ampacity.

? How does voltage not play into the resistance? Isn't that part of Ohm's Law?

Matt
__________________
MJSailing - Youtube Vlog -
Matt Johnson is offline   Reply With Quote
Old 08-01-2017, 10:03   #15
Registered User

Join Date: Apr 2013
Location: So Cal
Boat: Catalina 387
Posts: 967
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by Redpcx View Post
Insulated cable is always used to inter connect batteries. Bus bars are used to make a battery out of individual cells. It's practically impossible to align two batteries well enough to prevent stress on the battery terminals. Use flexible insulated cable. If you make bus bars, insulate them to prevent accidents. Certainly easier and probably cheaper to use cable, unless you have free copper stock.

You will never find a concensus of opinion on battery fuses. Some say fuse everything. Some say don't fuse the battery.

Don't fuse the ground. Don't fuse the ground. Do not fuse the ground.
ABYC says to fuse the batteries. I think fusing the batteries is a phenomenally good idea.

As usual, Maine Sail has a good article about it: Battery Bank Fusing Photo Gallery by Compass Marine How To at pbase.com
jeepbluetj is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where to Find Bronze Flat Bar for Chainplates ? seandepagnier Construction, Maintenance & Refit 32 15-03-2021 08:57
Grounding Copper Bar for Perkins 4-108 Starter? swami maximus Engines and Propulsion Systems 14 15-02-2010 20:24

Advertise Here


All times are GMT -7. The time now is 09:36.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.