Re: Using copper flat bar to connect the batteries in a battery bank

I have used flattened copper pipe for bussing fuse blocks with absolutely no problems. Going strong 20 years later. Cost pennies. Smash it, drill it. Grind off rough edges. Done.

I use cable for battery ties.
svJasmine is offline   Reply With Quote
Old 08-01-2017, 10:20   #17
Registered User

Join Date: Oct 2015
Location: Minnesota / Florida
Boat: Westerly Fulmar 32
Posts: 475
Re: Using copper flat bar to connect the batteries in a battery bank

If your worried about the mechanical stresses setup by the rigid system then bend a 'Z' into the bar so it is now its length is somewhat flexible.

I like the idea of a bussed battery but not the uninsulated part.
Steven UK is offline   Reply With Quote
Old 08-01-2017, 10:29   #18
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Using copper flat bar to connect the batteries in a battery bank

The problem I see is corrosion. Tinned cable of the correct gauge with closed lugs and heat shrink is a lot better than bare copper bar. I also agree with the need for movement however slight that cable allows but the bar will not allow.

Fuse the main positive of the bank - not need to fuse each battery in a bank.

Never fuse the negative.
mitiempo is offline   Reply With Quote
Old 08-01-2017, 10:35   #19
Marine Service Provider

Join Date: Jul 2004
Posts: 193
Re: Using copper flat bar to connect the batteries in a battery bank

Cover the copper with large heat shrink for insulation.



Quote:
Originally Posted by Steven UK View Post
If your worried about the mechanical stresses setup by the rigid system then bend a 'Z' into the bar so it is now its length is somewhat flexible.

I like the idea of a bussed battery but not the uninsulated part.
svJasmine is offline   Reply With Quote
Old 08-01-2017, 10:36   #20
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by svJasmine View Post
Cover the copper with large heat shrink for insulation.
The ends will corrode if not tinned.
mitiempo is offline   Reply With Quote
Old 08-01-2017, 10:36   #21
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Using copper flat bar to connect the batteries in a battery bank

I agree with the need to allow for expansion.
Mechanical stress due to expansion is the primary reason for bad circuit board connections in electronic equipment.
That's why a decently designed board uses U shaped lead wires from components which generate any significant amounts of heat.
My Autohelm 4000 is a perfect example of the designer's failure to do that.
I have to resolder all twelve leads on the four MOSFET transistors every few years.
The leads are very short and direct to the board.
Further, there's not enough room to replace them with new transistors with longer leads shaped into a curve to allow for expansion.

Whenever you read a thread about these autopilots going hard over all of a sudden, that's usually the fix.
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 08-01-2017, 10:56   #22
Registered User

Join Date: Sep 2007
Location: Delray Beach, Fl
Boat: 1998 Rosborough 246 LSV
Posts: 563
Re: Using copper flat bar to connect the batteries in a battery bank

I used 1" wide "grounding bar" taken from old phone company installation and bought for the weight of the copper for about $10 for the job. Each piece was 1" wide, 6" long and was, they claimed, 8 gauge copper.

I ran a 16,000 btu/hr air conditioner on the bank of 8 6 volt batteries rated, in total, at 950 Ah for 12 volts.

The replacement of jumper cables with bus bar reduced my voltage drop by 0.08 Amp (measured with a shunt and oscilloscope) during the first few milliseconds of air conditioner start.

I was unable to measure any difference between the shunt wires and the bus bar during any "normal" operation. Each end of the bus bar had a copper washer (on the battery side) and a copper plus stainless washer on the bolt side. The battery posts were, I think, M6 posts that are drilled and taped for allen screws.

The thing looked like a battleship - and since there was very low effective resistance, the bus bars had no measurable heating.

Since I routinely drew well over 100 Amps when running the inverter and air conditioner (or washer/dryer), the lower loss of the bus bar mattered. For other reasons, I don't believe any longer this was a wise idea, but it did for for 5 years with only replacing the alternators (I have 4), the drive belts (I had 6) and the engine (I had two).

If you want this much power on your boat, buy a generator - Tesla was right!
__________________
Capt. Stuart Bell
Rosborough 246 LSV Shearwater V
stu@shearwater-sailing.com
captstu is offline   Reply With Quote
Old 08-01-2017, 11:09   #23
Zai
Registered User

Join Date: Mar 2011
Location: Athens
Boat: 2011 Bavaria 36 Cruiser
Posts: 225
Re: Using copper flat bar to connect the batteries in a battery bank

What about using something like these?

Flexible Insulated Busbar – Maxiflex

or these?

http://stormpowercomponents.com/shop-our-stock/braid
Zai is offline   Reply With Quote
Old 08-01-2017, 11:46   #24
Registered User
 
Rigdaddy's Avatar

Join Date: Nov 2012
Location: Matagorda, TX catching my breath
Boat: Hans Christian 41 T
Posts: 143
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by jeepbluetj View Post
ABYC says to fuse the batteries. I think fusing the batteries is a phenomenally good idea.

As usual, Maine Sail has a good article about it: Battery Bank Fusing Photo Gallery by Compass Marine How To at pbase.com
Thanks for the link to Maine Sail's article.
__________________
Timing is everything
Rigdaddy is offline   Reply With Quote
Old 08-01-2017, 12:08   #25
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by Zai View Post
The first still has the problem of corrosion in a marine environment.

The second looks ok but surely more expensive than a proper tinned cable, closed lugs, and heat shrink.
mitiempo is offline   Reply With Quote
Old 08-01-2017, 12:09   #26
Registered User

Join Date: Dec 2016
Location: Houston, TX
Posts: 13
Re: Using copper flat bar to connect the batteries in a battery bank

[QUOTE=funjohnson;2298255]? How does voltage not play into the resistance? Isn't that part of Ohm's Law?

Voltage is, indeed, a part of Ohm's Law. However, under discussion here is ampacity not amperes.

A conductor of a known material and size (copper buss bar in this case) can carry a certain current for a given temperature rise (ampacity). The buss bar doesn't care if the current is 100A at 12V or if the current is 100A at 24V; all the buss bar "cares" about is the actual current flowing through it. As mentioned earlier, voltage comes into play for specifying conductors when insulation of the conductor is specified.
mickeyelam is offline   Reply With Quote
Old 08-01-2017, 12:42   #27
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by funjohnson View Post
? How does voltage not play into the resistance? Isn't that part of Ohm's Law?

Matt
Voltage is part of ohm's law but a fixed resistance is the same regardless of voltage.

Imagine a resistor sitting on a bench. Imagine it is color coded (marked) ten ohms. It has ten ohms of resistance regardless. It doesn't have to be connected to a circuit to have ten ohms of resistance.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 08-01-2017, 12:47   #28
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Using copper flat bar to connect the batteries in a battery bank

Quote:
Originally Posted by jeepbluetj View Post
ABYC says to fuse the batteries. I think fusing the batteries is a phenomenally good idea.
That is only partially true and misleading. A circuit feeding the starter motor doesn't have to have overcurrent protection.


The house bank should have overcurrent protection as close to the positive battery terminal as possible.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 08-01-2017, 12:47   #29
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,521
Re: Using copper flat bar to connect the batteries in a battery bank

If you do I would make them U shaped to avoid stresses...
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 08-01-2017, 12:49   #30
Registered User

Join Date: Apr 2016
Posts: 178
Re: Using copper flat bar to connect the batteries in a battery bank

holy cow. So many reasons not to use bars. One in particular is that they are not insulated. In building and outfitting a boat real problems show up, difficult decisions need to be made, but how to connect batteries is not one of them. Go with the flow and do what everybody else does.
pdenton
pdenton is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where to Find Bronze Flat Bar for Chainplates ? seandepagnier Construction, Maintenance & Refit 32 15-03-2021 08:57
Grounding Copper Bar for Perkins 4-108 Starter? swami maximus Engines and Propulsion Systems 14 15-02-2010 20:24

Advertise Here


All times are GMT -7. The time now is 14:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.