Start Air Conditioner Off Inverter Then Switch To Generator

I'd like to have a small 5000 btu domestic window air conditioner on the boat.

My 2000 watt Kipor generator would easily, run it but it may not supply enough power for the startup surge.

However, my inverter can supply it...but would drain the batteries running it.

So, is it possible to start the air con off the inverter and a few seconds later flip the manual selector switch to the generator- which of course would already be running?

I see two possible concerns.

In the instant the switch is flipped from inverter to generator, the air con compressor may lose momentum and stall? Dunno.

The inverter and generator cycles will be out of sync and have a residual affect and clash during that split second changeover period. Dunno.

I don't want to buy smart changeover switches which will cost more than the air conditioner. Nor do I want add-on hard starter kits that would void the air con warranty.

Inverter split system air cons are easy to start and run but take more space, are costlier and must be installed by a licenced person.
starcruiser is offline   Reply With Quote
Old 02-06-2016, 07:32   #2
Registered User

Join Date: Feb 2006
Location: Eastern Caribbean for the 2020 season then east coast or Panama
Boat: Lagoon 470 cat
Posts: 699
Re: Start Air Conditioner Off Inverter Then Switch To Generator

How big is your battery charger? Enough just to keep running off inverter and use generator solely to charge at same time?
Moontide is offline   Reply With Quote
Old 02-06-2016, 07:40   #3
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Most 5k ac units use about 550 watts to run so figure about 1200 watts to start. Your 2k watt Genny should have absolutely no issue with the start and running of your ac unit. As far as starting on inverter and switching No it most likely won't work . The electronics controlling the unit will see the switch off time as a power interruption thereby shutting the unit off.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 02-06-2016, 07:44   #4
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Start Air Conditioner Off Inverter Then Switch To Generator

A Honda 2K will do it easily, it will run my 12,000 BTU on my 5th wheel and my 5,000 Webasto in my Sailboat, the Sailboat 5K it will start and run in Eco mode. I could even charge batteries and run the little AC
The 5th wheel worked it pretty hard.

It helps if you turn the fan on for a few seconds and let the fan spool up, then turn the AC on.
a64pilot is offline   Reply With Quote
Old 02-06-2016, 07:50   #5
Marine Service Provider

Join Date: Dec 2009
Location: Working in St Augustine
Boat: Woods Vardo 34 Cat
Posts: 3,865
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Might need to ad a start capacitor as cheap window units probably have a cheap small capacitor. A marine air 6700 hatch mount will not start on a Honda 2000 without an ad on boost capacitor.
__________________
@mojomarine1
Boatguy30 is offline   Reply With Quote
Old 02-06-2016, 15:18   #6
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Quote:
Originally Posted by starcruiser View Post
I'd like to have a small 5000 btu domestic window air conditioner on the boat.

My 2000 watt Kipor generator would easily, run it but it may not supply enough power for the startup surge.

However, my inverter can supply it...but would drain the batteries running it.

So, is it possible to start the air con off the inverter and a few seconds later flip the manual selector switch to the generator- which of course would already be running?

I see two possible concerns.

In the instant the switch is flipped from inverter to generator, the air con compressor may lose momentum and stall? Dunno.

The inverter and generator cycles will be out of sync and have a residual affect and clash during that split second changeover period. Dunno.

I don't want to buy smart changeover switches which will cost more than the air conditioner. Nor do I want add-on hard starter kits that would void the air con warranty.

Inverter split system air cons are easy to start and run but take more space, are costlier and must be installed by a licenced person.
No, this idea will not work. The generator and inverter will not be in sync with one another which will most likely stall the compressor. That is if you can switch fast enough which you probably can't.

One solution to this problem is to use a charger/inverter that is designed to run in sync with your generator. Mastervolt and Victron make inverters that can do this. They call it Power Assist. Then you can start bigger loads with the inverter handling the startup surge and leaving the generator to handle the running condition.
transmitterdan is offline   Reply With Quote
Old 02-06-2016, 16:00   #7
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,084
Re: Start Air Conditioner Off Inverter Then Switch To Generator

We've had the same problem with an inverter being able to run but not start an apartment sized refrigerator. We'd still have 12.8 volts in the house bank, but the inverter would be screaming at us at 3:00 AM. The answer was a 2 farad capacitor - they make them for autombile audio systems - you know, the annoying BOOM BOOM BOOM at the traffic light. They're cheap, as long as you don't mind the teenager graphics on the can. We mounted it across the DC intet to the inverter, since it was pulling down voltage on the surge start-ups, and it has worked fine. If I could get to the back of the refrigerator, I'd probably mount a "soft start" capacitor.
tkeithlu is offline   Reply With Quote
Old 02-06-2016, 16:54   #8
Registered User

Join Date: Jun 2012
Location: Port Aransas, Texas
Boat: 2019 Seawind 1160 Lite
Posts: 2,126
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Quote:
Originally Posted by Boatguy30 View Post
Might need to ad a start capacitor as cheap window units probably have a cheap small capacitor. A marine air 6700 hatch mount will not start on a Honda 2000 without an ad on boost capacitor.
My 8k BTU and March pump will run with my Honda 2000. Start the Honda with OFF the eco mode, start the AC, and then switch the Honda to eco mode. Once ac running, the Honda on eco more is OK. When the compressor and pump kick on the eco mode can handle the changes in load.
Quote:
Originally Posted by transmitterdan View Post
No, this idea will not work. The generator and inverter will not be in sync with one another which will most likely stall the compressor. That is if you can switch fast enough which you probably can't.

One solution to this problem is to use a charger/inverter that is designed to run in sync with your generator. Mastervolt and Victron make inverters that can do this. They call it Power Assist. Then you can start bigger loads with the inverter handling the startup surge and leaving the generator to handle the running condition.
sailjumanji is offline   Reply With Quote
Old 02-06-2016, 16:57   #9
Registered User

Join Date: Jun 2012
Location: Victoria, Australia
Posts: 88
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Thanks for the replies, which tend to confirm my negative suspicions about the idea.

I am prepared to spend about $500 on the new air conditioner---yes, they are much more pricey and small ones are hard to get here in Australia--but I don't want to go into the expense of changeover switches, more electronics and warranty-voiding modifications.

One manufacturer's technical department told be start-up current was 6-8 times rate current.

My inverter is 1500 amps, 3500 peak --BUT non-pure sinewave, so while I'd be happy to start --if it indeed does--a new air con off that, I'd be reluctant to keep it running.
starcruiser is offline   Reply With Quote
Old 02-06-2016, 18:02   #10
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: Start Air Conditioner Off Inverter Then Switch To Generator

The reason you can't do it with the switch is that you can't have two AC sources working at the same time.

Ya think the capacitor will go boom boom? Don't try it.

Good luck, lots of good advice here.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 02-06-2016, 18:13   #11
Registered User

Join Date: Apr 2014
Boat: Beneteau Oceanis 45
Posts: 174
Re: Start Air Conditioner Off Inverter Then Switch To Generator

With a good start capacitor your genset should handle the startup just fine.
SteveInMD is offline   Reply With Quote
Old 02-06-2016, 21:36   #12
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Start Air Conditioner Off Inverter Then Switch To Generator

if you had a pass through inverter it would switch automatically for you.
smac999 is offline   Reply With Quote
Old 03-06-2016, 06:59   #13
Registered User

Join Date: Sep 2014
Location: Santa Eulalia, Ibiza
Boat: Binliner 195
Posts: 60
Re: Start Air Conditioner Off Inverter Then Switch To Generator

The "number" to be looking at/for on the compressor is LRA, Locked Rotor Amps, The amount of current it takes to start, It is on most motor rating plates or you should find it on net with motor serial number etc, Add the fan loads & you should get an idea of how close you should be,

Changeover switch, You could do as you suggested, either with manual switch or relay/contactor, The AC will not mind as long as it is quick, However running motors with non true sine wave inverters does shorten the life of some,,,,, Drastically from what I read,

New true sine wave inverter with gen assist would be probably you best

Tim
blackswan555 is offline   Reply With Quote
Old 03-06-2016, 07:19   #14
Registered User

Join Date: May 2008
Posts: 3,536
Re: Start Air Conditioner Off Inverter Then Switch To Generator

Something like this....

http://www.amazon.com/SUPCO-SPP6-Sta...ds=supco+relay
CarlF is offline   Reply With Quote
Old 03-06-2016, 09:11   #15
Registered User
 
S/V Alchemy's Avatar

Join Date: May 2008
Location: Nova Scotia until Spring 2021
Boat: Custom 41' Steel Pilothouse Cutter
Posts: 4,976
Re: Start Air Conditioner Off Inverter Then Switch To Generator

__________________
Can't sail? Read about our travels at https://alchemyonpassage.blogspot.com/. Can't sleep? Read www.alchemy2009.blogspot.com for fast relief. Can't read? Avoid www.volumesofsalt.blogspot.com, because it's just personal reviews of sea books.
S/V Alchemy is offline   Reply With Quote
Reply

Tags
generator, inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Marine Air Cabin Mate 16000btu air Conditioner formrteki Classifieds Archive 3 01-10-2012 08:52
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 03-09-2012 05:41
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 23-08-2012 00:26
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 13-08-2012 04:28
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 14-07-2012 09:04

Advertise Here


All times are GMT -7. The time now is 07:32.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.