Solar - questions on cabling and fuses

See attached (some may recognize - I posted a question on MPPT controllers a couple days ago). Panels are on a hard top of trawler, panel is a 20-foot one way run to MPPT/solar control panel with breakers. I'm hoping for knowledgeable guidance on following questions.

1. 6awg cable appears to be fine for the 14A/27V run from the panel pairs (series) to the MPPT controller 20 feet away. I don't have the equipment on front of me - are the lugs on a modern MPPT large enough for 6awg cable? Of not, how are these connections made up? Obviously, stripping some strands would physically work, but wondering if there's a better practice. Also, the pigtails off the panel appear to be 10awg. Best practice in connecting two dissimilar sized wires that are partially exposed to weather?

2. Fusing of panels. In reading another active thread, there was conflicting opinion about fusing the panels. One post by a knowledgeable person seemed to suggest it was not needed if just a single panel, but if there were three, it became important, and should be done at the panel. Questions: should I install fuses between the MPPT and the panel? If so, a single fuse per string, or a single fuse per panel? Maybe an inline fuse in the 10awg pigtail for each panel (making sure each are reasonably accessible)?

Thanks in advance

Peter
__________________
_______________________________________
Cruising our 36-foot trawler from California to Florida
Join our Instagram page @MVWeebles to follow along
mvweebles is offline   Reply With Quote
Old 31-01-2021, 04:31   #2
Registered User

Join Date: Jun 2019
Posts: 2,734
Re: Solar - questions on cabling and fuses

Dang it. Forgot to attach diagram Click image for larger version

Name:	Screenshot_20210131-050512.jpeg
Views:	264
Size:	35.9 KB
ID:	231650
__________________
_______________________________________
Cruising our 36-foot trawler from California to Florida
Join our Instagram page @MVWeebles to follow along
mvweebles is offline   Reply With Quote
Old 31-01-2021, 05:01   #3
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,466
Images: 22
Re: Solar - questions on cabling and fuses

Peter, which model Victron MPPT do you have? The smaller models up to 100/20 have 6mm2 cable size limits. Larger ones bigger.

Quote:
Originally Posted by mvweebles View Post
In reading another active thread, there was conflicting opinion about fusing the panels. One post by a knowledgeable person seemed to suggest it was not needed if just a single panel, but if there were three, it became important, Peter

I think the important word was "String". Now I think I have 3 strings in my panel, but need to go and see it to be sure. However, I did fit a circuit breaker in between the panel and the MPPT. Not exactly cheap but it is a useful way of switching off the panel from the MPPT and therefore the charge in the battery leads if you want to do some work on the batteries. Otherwise those loose leads are still live even if disconnected from the battery.

Pete
Attached Thumbnails
Click image for larger version

Name:	s-l300.jpg
Views:	96
Size:	10.8 KB
ID:	231651  
Pete7 is online now   Reply With Quote
Old 31-01-2021, 05:14   #4
Registered User

Join Date: Aug 2015
Location: Jacksonville, FL
Boat: Pearson 367
Posts: 550
Re: Solar - questions on cabling and fuses

I have a victron 100/30 and it fits 6awg cable and it seems to be the max.
__________________
I started with nothing and I still have most of it left.
LLCoolDave is offline   Reply With Quote
Old 31-01-2021, 05:51   #5
Registered User

Join Date: Dec 2013
Boat: Nauticat 33
Posts: 153
Re: Solar - questions on cabling and fuses

Southwire has an app called Voltage Drop that is helpful when estimating wire size needed. For your application they recommend 10AWG. So you might be adding unnecessary headaches and costs.
cofc is offline   Reply With Quote
Old 31-01-2021, 06:08   #6
Registered User

Join Date: Apr 2017
Location: NYC
Boat: Adams 45
Posts: 249
Re: Solar - questions on cabling and fuses

10AWG is safe for the wire, but gives 10% voltage drop meaning 10% of the generated power is dissipated in the wire. 6AWG is 5% voltage drop and the reduced losses might be worthwhile.
pjShap is online now   Reply With Quote
Old 31-01-2021, 06:20   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,448
Images: 241
Re: Solar - questions on cabling and fuses


FWIW:
The Blue Sea Systems "T-1" Circuit Breaker (surface-mount part nos. 7120 to 7133; panel-mount part nos. 7020 to 7033), has been recalled effective May 2003.
If you still have a T-1 circuit breaker, please contact Blue Sea Systems for a replacement. It will be replaced with a Bussmann 187 Circuit Breaker (Panel Mount or Surface Mount), which is a direct replacement.
The company received no reports of any incidents, but apparently found, through its own research, that “there is a possible fire risk if the operator holds the circuit breaker handle in the ‘on’ position, after the unit has tripped, causing the contacts to weld together.”
https://www.bluesea.com/resources/541
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 31-01-2021, 06:22   #8
Registered User

Join Date: Nov 2016
Location: Sarnia ON
Boat: S2 9.1
Posts: 267
Re: Solar - questions on cabling and fuses

Those numbers look a little high. For 15 amps at 7 meters using #10 I get a 2.5% drop and with #6 I get a 1% drop.
I would go with #8 my self.
Gary Mc is offline   Reply With Quote
Old 31-01-2021, 06:32   #9
Registered User

Join Date: Jun 2019
Posts: 2,734
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by Pete7 View Post
Peter, which model Victron MPPT do you have? The smaller models up to 100/20 have 6mm2 cable size limits. Larger ones bigger.

I think the important word was "String". Now I think I have 3 strings in my panel, but need to go and see it to be sure. However, I did fit a circuit breaker in between the panel and the MPPT. Not exactly cheap but it is a useful way of switching off the panel from the MPPT and therefore the charge in the battery leads if you want to do some work on the batteries. Otherwise those loose leads are still live even if disconnected from the battery.

Pete
Thanks Pete - I am going with 100/50 Smart MPPT controllers. With 27A on the panels in series, was just a little close for my tastes. That and the upgrade to 6AWG cable added over $250 to the install, but it's a one time cost to my eyes.

Is a fuse/CB needed between the panel and MPPT if I have a CB between the MPPT and the battery? The surface mount CBs you linked are great, though I'd have to figure out best way to mount without burying them.

Peter
mvweebles is offline   Reply With Quote
Old 31-01-2021, 06:36   #10
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,466
Images: 22
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by GordMay View Post
has been recalled effective May 2003.
Hopefully they are all out of existence now. Mine aren't Blue Seas but badged some other make.

Pete
Pete7 is online now   Reply With Quote
Old 31-01-2021, 06:40   #11
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,466
Images: 22
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by mvweebles View Post
The surface mount CBs you linked are great, though I'd have to figure out best way to mount without burying them.

Peter
I had the same problem and despite the claims that they were waterproof, I chose not to put them outside near the panels. Instead they sit next to the MPPT were I can access them and see what is going on. For me its a bit of belt and braces, but you have more panels that warrants thinking about.

Also, if you haven't thought about it, the cable from the MPPTs to the batteries may need to be a different size than the one from the panel to the MPPT, since the Ah will be higher with a lower voltage, so big beefy cables needed. There I put the fuse next to the batteries.
Pete7 is online now   Reply With Quote
Old 31-01-2021, 06:40   #12
Registered User

Join Date: Jun 2019
Posts: 2,734
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by Gary Mc View Post
Those numbers look a little high. For 15 amps at 7 meters using #10 I get a 2.5% drop and with #6 I get a 1% drop.
I would go with #8 my self.
I'm only okay with electrics. My understanding is you need to double the run due to return path. So a 20-foot run between two components is actually 40-feet overall. When I look at the BSS chart, 40-feet at 15A is pretty solidly in the 6 AWG category. Am I reading this incorrectly? No harm done of course except perhaps being more expensive than needed, but would like to know for future use.

Peter

Click image for larger version

Name:	BSS <a title=Wiring Size Diagram.jpg Views: 135 Size: 247.4 KB ID: 231660" style="margin: 2px" />
mvweebles is offline   Reply With Quote
Old 31-01-2021, 06:50   #13
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,313
Re: Solar - questions on cabling and fuses

Solar panels are a current source and one of limited capacity. In my mind, if the wiring can handle the full short circuit current of the panels feeding it without melting down and the controller can handle it as well, you don't need a fuse (as it's impossible to produce feed enough power to cause a problem that a fuse would solve).
rslifkin is online now   Reply With Quote
Old 31-01-2021, 07:02   #14
Registered User

Join Date: Jun 2019
Posts: 2,734
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by Pete7 View Post
I had the same problem and despite the claims that they were waterproof, I chose not to put them outside near the panels. Instead they sit next to the MPPT were I can access them and see what is going on. For me its a bit of belt and braces, but you have more panels that warrants thinking about.

Also, if you haven't thought about it, the cable from the MPPTs to the batteries may need to be a different size than the one from the panel to the MPPT, since the Ah will be higher with a lower voltage, so big beefy cables needed. There I put the fuse next to the batteries.
Putting them next to the MPPTs would be simple enough, but they would be a 20-feet of wire away from the panels. My understanding is best practice is to put the fuse as close to the power source as possible, but I'm not sure about this. I guess it's better than nothing.

Solar goes to a bus bar that then goes to batteries. Cables are 4-O, so pretty big.

Peter
mvweebles is offline   Reply With Quote
Old 31-01-2021, 07:33   #15
Registered User

Join Date: Nov 2016
Location: Sarnia ON
Boat: S2 9.1
Posts: 267
Re: Solar - questions on cabling and fuses

Quote:
Originally Posted by mvweebles View Post
I'm only okay with electrics. My understanding is you need to double the run due to return path. So a 20-foot run between two components is actually 40-feet overall. When I look at the BSS chart, 40-feet at 15A is pretty solidly in the 6 AWG category. Am I reading this incorrectly? No harm done of course except perhaps being more expensive than needed, but would like to know for future use.

Peter

Attachment 231660

You are correct in that if you do the calculation manually you use the total conductor length which it there and back. Essentially you take the total length, and if using feet, then you need the resistance per foot of the conductor which will give you the total resistance of the conductor. Then use the max amps times the resistance and you get the voltage drop of the conductor.


However most tables and on line calculators use the distance to the load so they are already accounting for the return leg in their calculations.
Hope this helps.
Gary Mc is offline   Reply With Quote
Reply

Tags
fuses, solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ICOM M 802 SSB Install: Cabling and Ferrites??? muttskie Marine Electronics 28 06-03-2016 15:25
Simnet or Nmea2000 cabling ? ColdEH Marine Electronics 3 16-04-2014 03:51
AIS, NMEA 0183 cabling, OpenCPN & Radar overlays Neptune's Gear Vendor Spotlight - Great Deals for CF Members! 0 01-04-2014 15:35
Battery Cabling for Parallel Bank Rustic Charm Electrical: Batteries, Generators & Solar 103 14-06-2012 16:33
Maretron N2K Cabling and Gear s/v Jedi Marine Electronics 1 16-07-2011 16:53

Advertise Here


All times are GMT -7. The time now is 14:01.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.