Solar Controller for Low Voltage Panels? Not Victron!

I'm looking for recommendations on a new solar controller for charging my 12v AGM batteries. I've got Renogy 100 watt panels, 3 years old, which unfortunately are no longer putting out their rated open circuit voltage. From a factory specified 21.2v its now 19.5v, consistent for each panel individually and when paralleled (no loss through the connections to the controller input). They've got to be paralleled because shading from the mast, sails, etc. is unavoidable.

My three year old Victron MPPT controller was doing its job and the system was working fine with the higher panel open panel voltage, but not any more. Now there is no charging at all. This is because Victron hard programs MPPT controllers to require a substantial difference between panel and battery voltages, and my system no longer satisfies that arithmetic. Victron literature says the differential is 5v to start charging, but that's not the whole story. There's a voltage drop caused by the controller itself, and in my system that's about 3v. The result is the panel-battery differential is not enough to start charging.

I'm hopeful that other sailors (those who can't wire in series) have dealt with low voltage panels and have found controllers to do the job. Any suggestions?

Note, new solar panels is not now an option. Thanks for any ideas.
Msailor is offline   Reply With Quote
Old 14-03-2023, 16:03   #2
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Solar Controller for Low Voltage Panels? Not Victron!

Welcome to the forum Msailor.

The Victron controllers will look at the input voltage. Before the charging begins the current will be zero therefore any resistance in the wires and the connections will not produce any voltage drop. 19.5v should be OK providing there are not any other charge sources raising the battery voltage. Once charging commences the input voltage only has to be around 1v above battery voltage for charging to continue.

The factory specified 21.2v is for a solar cell temperature of 25° C. As the solar cells heat up the Voc drops and solar cell temperature is always well above the ambient temperature. A Voc of 19.5v is quite good in practice.

In short, I doubt the 19.5v you are measuring is the cause of the problem. I would at least measure the Isc (short circuit current) to see if the panels are capable of producing useful current before contemplating new controllers.
noelex 77 is offline   Reply With Quote
Old 14-03-2023, 18:19   #3
Registered User

Join Date: Mar 2023
Posts: 9
Re: Solar Controller for Low Voltage Panels? Not Victron!

Thanks for the analysis. A bit more info may be of help. The 3v drop occurs when the panels are connected to the controller, and is shown by the controller's software readings transmitted via bluetooth. The software measures what Victron calls "Solar Voltage," which moves around a bit, but averages about 16.5v. A few times it has hit 17 plus mid-day in perfect conditions (I'm in Florida), and that started a charging cycle, but most days I get no charging at all.

I'd like to measure short circuit amps but my current multi-meter doesn't have the capacity. However, I think it unlikely that all three panels would have the same VOC reading if one (or more) was deficient in producing current. It does seem that the panels are simply aging, perhaps more rapidly then expected, and so panel VOC has deteriorated.

Waiting for the sun angle to increase is one thing for a charging system, requiring perfect conditions is quit another. The bottom line for me is that Victron's voltage differential requirement is too restrictive for my panels.
Msailor is offline   Reply With Quote
Old 14-03-2023, 19:01   #4
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by Msailor View Post
The 3v drop occurs when the panels are connected to the controller, and is shown by the controller's software readings transmitted via bluetooth. The software measures what Victron calls "Solar Voltage," which moves around a bit, but averages about 16.5v. A few times it has hit 17 plus mid-day in perfect conditions (I'm in Florida), and that started a charging cycle, but most days I get no charging at all.
The solar voltage of 16.5v is the Vmp or the maximium powerpoint voltage. A 16.5v Vmp is typical of “12 v “ panels in the real world. This is not the voltage that the Victron controller uses to decide if it should start charging. The voltage that initiates the start of charging is the Voc which you have measured at 19.5v as long as the battery voltage is lower than 5v below 19.5v (14.5 v) in the morning when the solar charger wakes up it will try to start charging and as long as the battery voltage is lower than 1v below the Vmp which is reported as 16.5v (so 15.5v) the controller will continue to charge.

What status is the controller reporting around the middle of the day? The status can be found on the Bluetooth app. If you could take a screenshot around midday the other values are also helpful.
Attached Thumbnails
Click image for larger version

Name:	92121094-D9E0-467F-81CD-D992014BE3F3.jpg
Views:	118
Size:	191.7 KB
ID:	272790  
noelex 77 is offline   Reply With Quote
Old 14-03-2023, 20:51   #5
Registered User

Join Date: Mar 2023
Posts: 9
Re: Solar Controller for Low Voltage Panels? Not Victron!

Thanks again for your response. "Solar Voltage" may measure available controller output, but I can't find where Victron says that. 19.5 volts open circuit may be real world good, but it is less than when the panels were new and when the controller charged dawn to dusk.

Still interested in suggestions for a "low voltage" controller.
Msailor is offline   Reply With Quote
Old 15-03-2023, 04:53   #6
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Solar Controller for Low Voltage Panels? Not Victron!

Victron are the only MPPT controllers that use a +5 v wake up voltage. Most companies do not publish their wake up voltage, but around +2 to 3v would be typical. There is not much difference between brands other than Victron. Some of the expensive controllers such as Outback and Midnite have adjustable start up parameters, but few people understand this feature and it is rarely adjusted from the default setting, which is a pity. Both waking up too early and too late wastes some energy.

When running, all MPPT controllers are similar (including Victron), requiring an input voltage around 1v higher than battery voltage to keep charging, so there is almost no difference with different brands of controller once the wake sequence has been triggered.

There are a small number of MPPT controllers that will boost voltage. They are usually designed for using 6v or 9v panels on a 12v bank. Genasun are the major manufacturer. However, having this boost feature reduces the efficiency when the solar panel voltage is high so this is not something that is a good idea for most systems.

The final option is to select a non MPPT or so called PWM solar controller. These will start and continue to work when the potential input voltage is only a fraction above battery voltage. There is some loss of efficiency when the solar panel voltage is high, but they are slightly more efficient when the solar panel voltage is low. This is a very rare situation for most systems, but as this is your concern they would be ideal.

If you are convinced that low solar panel voltage is the cause of your problem (I am doubtful this is the real issue) a PWM controller would be the best solution. There are many inexpensive brands of PWM controllers. As the electronics in this type of controller is very simple these cheap units are often OK, unlike inexpensive MPPT controllers that are usually poor. If you want a good quality PWM controller Plasmatronics make very good units.

As a test you can try connecting the solar panels in parallel directly to the battery bank (use a suitable fuse). This is exactly what a PWM controller will do when the batteries are not at a high state of charge. Monitor the battery voltage and check it does not climb too high while the panels are connected this way (it will only climb slowly so there is plenty of time to disconnect providing it is monitored). If this does not charge the batteries with reasonable current no conventional (non voltage boosting) MPPT or PWM controller will work in your system and its faults.

This above test (or measuring Isc) will show if the fault is really low solar panel voltage before spending money on new controllers.
noelex 77 is offline   Reply With Quote
Old 15-03-2023, 06:52   #7
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: Solar Controller for Low Voltage Panels? Not Victron!

If the bypass diodes in your panels are intact, you should try putting them in series and see what happens during partial shading.

If you lose output during partial shading, maybe you can repair the panels by replacing the diodes. I have had panels that gave simple access to the diodes but also ones with sealed connections.

Edit: worst case you can add external bypass diodes that bypass the whole panel that has partial shading… which happens with parallel setup anyway.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 15-03-2023, 07:59   #8
Registered User
 
Nicholson58's Avatar

Cruisers Forum Supporter

Join Date: Jan 2011
Location: Caribbean live aboard
Boat: Camper & Nicholson58 Ketch - ROXY Traverse City, Michigan No.668283
Posts: 6,369
Images: 84
Re: Solar Controller for Low Voltage Panels? Not Victron!

I think a better solution is new panels!

New panel will have higher efficiency, greater output. Don’t skimp.

Our 3 Sanyo 220HT BTW are 8 years old and still capable of exceeding full rated output. Name plate says 660 watts max.
Attached Thumbnails
Click image for larger version

Name:	720B5D2E-94D9-460C-ACA8-68CC2476A39F.jpg
Views:	80
Size:	404.2 KB
ID:	272824  
Nicholson58 is offline   Reply With Quote
Old 15-03-2023, 18:41   #9
Registered User

Join Date: Aug 2007
Location: Minneapolis MN
Boat: Delphia 37
Posts: 221
Re: Solar Controller for Low Voltage Panels? Not Victron!

Thanks for this discussion, I've always been perplexed by Victron's stance/description on how all this works and truthfully I still am. For my initial solar install a few years back, with flexible panels on a bimini, the the difference of the +5v was a razor thin margin. I could never get over what seems like a big deal and went with a different controller at the time.

I'm going to expand my system this year (installed davits so getting a proper fixed panel also) and need to re-visit this whole conversation. Victron is naturally the price/feature/performance winner these days for small controllers and I'll need to find a way to put my mind at ease with all this again
marty9876 is offline   Reply With Quote
Old 16-03-2023, 07:25   #10
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by marty9876 View Post
Thanks for this discussion, I've always been perplexed by Victron's stance/description on how all this works and truthfully I still am. For my initial solar install a few years back, with flexible panels on a bimini, the the difference of the +5v was a razor thin margin. I could never get over what seems like a big deal and went with a different controller at the time.

I'm going to expand my system this year (installed davits so getting a proper fixed panel also) and need to re-visit this whole conversation. Victron is naturally the price/feature/performance winner these days for small controllers and I'll need to find a way to put my mind at ease with all this again
There are many reasons to get the array voltage up much higher than the 5V above battery voltage. I had a 120V DC array before a hurricane ripped it off and am considering a 250V array as replacement. In that case, while underway I will slide two panels underneath three other panels, which is the ultimate shading and still expect the other panels to perform with all five of them in series
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 16-03-2023, 08:01   #11
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by marty9876 View Post
Thanks for this discussion, I've always been perplexed by Victron's stance/description on how all this works and truthfully I still am.
In practice it does not seem to be an issue. However, I would be cautious about using the Victron controllers in a parallel or single controller per panel system with “12 v“ panels where the Voc of the panels was on the low end of what is typical. This is especially true if there are alternate charge sources (such as wind) that may raise the battery voltage first thing in the morning. It is also potentially more of an issue in hot climates or situations where the panels do not receive much ventilation, such as flexible panels attached to the deck.

It should also be noted that the opposite problem occurs with solar controllers waking up too early before the solar panels are capable of delivering enough current to compensate for self consumption of the MPPT controller.

It is easy to see if your controller is waking up too early or too late although it means staring at electrical gauges instead of enjoying the early morning light. Ideally the solar controller would wake up just at the point where the solar panel production equals the self consumption of controller (or strictly speaking the extra consumption involved in supplying the tracking circuits). So at the point of waking up if the contribution of the solar controller is negative (ie it is consuming power) the controller has woken up too early. If at the point of waking up, the contribution of the solar controller is positive (ie it is producing power) the controller has woken up too late. You can also gauge how significant this error is by estimating the amount of energy wasted by a late or early start. This should be very small.

Unfortunately, if you do this test on 99% of controllers there is nothing you can do to adjust the wake up parameters. These are set by the manufacturer of the controller and are not user adjustable. If you did identify a severe issue of the controller starting late you can change the wiring to series, or as a temporary measure “fool” the controller into starting each morning by adding a brief high load.
noelex 77 is offline   Reply With Quote
Old 16-03-2023, 16:00   #12
Registered User

Join Date: Mar 2023
Posts: 9
Re: Solar Controller for Low Voltage Panels? Not Victron!

First, thank you Noelex for the market survey on controllers. Hopefully someone will get on this thread and tell us about their experience with low voltage systems that use some of these products.

A couple of points: Serial wiring pros and cons are well known, as are the practicalities and realities of putting panels on a sailboat--particularly smallish monohulls. As a way of illustrating, I'll add to this thread the results of the new test of serial wiring of my panels. With the same Victron controller model and the same panel installation, instead of the usual mid-day 15-20 amps I would get with the panels paralleled, I'm now seeing only 2-6 amps mid-day, and that's with the sails down and the boat oriented to minimize shading. My new trickle charge system.

Another point, for finding an installed system's starting voltage, I held test probes to the controller input terminals and monitored both the external voltmeter and Victron Connect "Solar Voltage." They were virtually the same (in the approximate 14 to 17 amp range) and so I think either works for determining voltage drop. For observing commencement of charging, Victron Connect shows charging status and battery voltage in the same view as Solar Voltage. I found charging on my system started when the Solar Voltage/battery voltage delta reached 5.

So, serial wiring and the fine points of Victron software are really not where this discussion should go. It should be about controllers which work well with panels that are on the low voltage side.
Msailor is offline   Reply With Quote
Old 16-03-2023, 16:30   #13
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by Msailor View Post
With the same Victron controller model and the same panel installation, instead of the usual mid-day 15-20 amps I would get with the panels paralleled, I'm now seeing only 2-6 amps mid-day, and that's with the sails down and the boat oriented to minimize shading. My new trickle charge system.
Parallel connection is generally better on a sailboat than series connection, but the difference should not be as drastic as you are finding. I suspect you have some blown bypass diodes.

Quote:
Originally Posted by Msailor View Post
Another point, for finding an installed system's starting voltage, I held test probes to the controller input terminals and monitored both the external voltmeter and Victron Connect "Solar Voltage." They were virtually the same (in the approximate 14 to 17 amp range) and so I think either works for determining voltage drop.
The Victron controllers are normally reasonably accurate so it is not surprising that the input voltage you are measuring matches the results the controller is reporting, but this is not “voltage drop”. The controller is adjusting the output voltage of the solar panel to maximise the power production. This is the Vmp. It is different to the voltage that determines if the solar controller is going to “wake up” this is Voc, or open circuit voltage ie when no current is flowing. Voc is typically around 3-4v higher than the Vmp in the real world for “12v" panels, but this difference will vary depending on conditions and other factors. Voc is only reported by the solar controller before wake up.

Quote:
Originally Posted by Msailor View Post
Victron Connect shows charging status and battery voltage in the same view as Solar Voltage. I found charging on my system started when the Solar Voltage/battery voltage delta reached 5.
This is exactly what it should be and this is typically spot on. More important is what current is the system producing at wake up. This will tell you if the wake up sequence is starting too late or too early in your system.
noelex 77 is offline   Reply With Quote
Old 16-03-2023, 17:36   #14
Registered User

Join Date: Aug 2007
Location: Minneapolis MN
Boat: Delphia 37
Posts: 221
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by noelex 77 View Post
In practice it does not seem to be an issue. However, I would be cautious about using the Victron controllers in a parallel or single controller per panel system with “12 v“ panels where the Voc of the panels was on the low end of what is typical.
Thanks for confirming I’m not crazy and my analysis paralysis was pretty accurate - you hit my initial setup spot on - pair of flex panels in parallel. From memory, rigid panels I think tend run a little higher voltage than flex but naturally the parallel is the real killer. Based on your other comment perhaps I should revisit the serial vs parallel decision. I understand the benefits if higher voltage, the sailor in me went with the conservative approach

Ironically I was looking into using my current controller/pair of flex panels in parallel and adding a rigid but once I understood the potential power generation I’d be giving up (the flex were much lower voltage than possible rigid) that killed that idea quickly. I had all the right pieces just not put together in the right order in my head.
marty9876 is offline   Reply With Quote
Old 16-03-2023, 18:07   #15
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: Solar Controller for Low Voltage Panels? Not Victron!

Quote:
Originally Posted by Msailor View Post

Still interested in suggestions for a "low voltage" controller.

if the panels can't get enough voltage your only option would probably be a pwm controller. I'm betting any mppt will want higher voltage.

I would stick in series and see what happens. even just to test and see if you get any power out of them. less ideal is still better then your current nothing.
smac999 is offline   Reply With Quote
Reply

Tags
panels, solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Victron solar controller high charge voltage mikedefieslife Electrical: Batteries, Generators & Solar 28 23-12-2018 06:27
[SOLD] 4x50wts Solartech MARINE solar panels+ Victron MPPT controller+ othr $550 Fort Lauder Beatdizzy General Classifieds (no boats) 0 17-01-2018 09:47
Low voltage vs higer voltage solar Singleprop Electrical: Batteries, Generators & Solar 11 06-07-2015 19:35
Low Voltage on Solar Panels Meck Electrical: Batteries, Generators & Solar 7 31-03-2011 17:03
Low Voltage Solar Panels SeaKing Electrical: Batteries, Generators & Solar 8 31-08-2010 12:52

Advertise Here


All times are GMT -7. The time now is 06:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.