Old 04-07-2022, 12:57   #91
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
Thank you. I respect your opinion. And that you have acknowledged that grounding does offer enhanced safety, but that you consider the benefits of this are so small as to be outweighed by the other considerations, like potential galvanic corrosion. Good stuff. Useful. Complete.

"Oh Lo-ord it's hard to be humble..."

Most independent experts manage to offer useful information and advice without being absolutist about it, claiming superior authority, or slagging the dominant standards bodies. And making some mistakes, while inferring their infallability. Just sayin.
ISO is the dominant standards body even now ABYC is essentially homologating it’s new standards to ISO. this is necessarily a great thing in my view as ABYCs thinking is now an influence in ISO.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 13:29   #92
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
From ISO 13297

3.8
isolation transformer
transformer installed in the shore power supply circuit on a craft to electrically isolate all the normally live conductors (3.11) and the protective conductor (3.10) on the craft from the AC system conductors of the shore power supply

Thank you.
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 13:47   #93
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by s/v Jedi View Post
I call the diagram that I posted authoritative not because I made it but because it is the preferred setup worldwide. Even in the US where the big installers all say “yes, ABYC” and proceed to install Victron isolation transformers like in this diagram. And for good reason!
It is an option. Arguably the best option for fiberglass pleasure boats, especially in ISO countries, maybe less so in N America at the moment. And what about aluminum or steel hulls?

One should be a bit more restrained about calling something "authoritative", at least without all the caveats.

Quote:
Originally Posted by goboatingnow
Once you have a discontinuous( isolated) ground , seawater simply cannot become a fault return except under bizarre conditions requiring multiple faults simultaneously

As I said a continuous ground degrades onboard safety not enhances it. It inserts metal surfaces in contact with seawater into the fault return , whereas before these where not in that circuit with an isolated ground.
Three words: "marina", and "other boats".

Other than that, I still don't know what you're driving at there.

This has devolved into hair-splitting now; the main points and opinions are all in the thread, no sense rehashing them.
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 14:14   #94
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
It is an option. Arguably the best option for fiberglass pleasure boats, especially in ISO countries, maybe less so in N America at the moment. And what about aluminum or steel hulls?

One should be a bit more restrained about calling something "authoritative", at least without all the caveats.



Three words: "marina", and "other boats".

Other than that, I still don't know what you're driving at there.

This has devolved into hair-splitting now; the main points and opinions are all in the thread, no sense rehashing them.
Unless your neighbour is baring live wires and throwing them on your deck I don’t see your point , if your neighbours boat is leaking into seawater then discontinuous ground actually helps protect you , whereas continuous ground makes your boat a conduit , to the detriment of all your underwater metals

It’s not hair splitting nick and I have long argued that ABYC has got this aspect wrong and continues to do so. As nick says you buy a victron and wire it as victron stipulate , as most in the US do , you get the ISO approved method. ( and I doubt any US insurer would quibble)

ABYC was wrong on ELCIs for years after ISO mandated them , belatedly accepting the rest of the world late in the day , it’s wrong about this too. ( ABYC is wrong about underwater bonding on GRP too but that’s another days argument )
Simples
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 14:27   #95
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

I'm content to leave this alone.
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 14:54   #96
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
I'm content to leave this alone.
By the way ABYC E-11 ( 2008) does not require continuous Earth. It does require the transformer case to be grounded to shore power , but that case is not then connected to ships ground.

Hence iso and abyc agree in this respect , earths are not connected, nicks diagram meets the salient aspects of the ABYC standard
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 15:06   #97
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
By the way ABYC E-11 ( 2008) does not require continuous Earth. It does require the transformer case to be grounded to shore power , but that case is not then connected to ships ground.

Hence iso and abyc agree in this respect , earths are not connected, nicks diagram meets the salient aspects of the ABYC standard
And I've said as much, waay back. ABYC considers both methods acceptable.

(I think you'll find that ABYC requires the metal transformer case grounded to boat ground.)
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 15:10   #98
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
And I've said as much, waay back. ABYC considers both methods acceptable.

(I think you'll find that ABYC requires the metal transformer case grounded to boat ground.)
No E-11 diagram 8 shows the case and shield only connected to shore earth not boat earth.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 15:21   #99
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
No E-11 diagram 8 shows the case and shield only connected to shore earth not boat earth.
Sorry, nope.

Think about it; on the boat, where the shorepower AC and ground are isolated from the rest of the boat, then the remaining source of shock hazard is the secondary side of the transformer.
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 15:32   #100
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
Sorry, nope.

Think about it; on the boat, where the shorepower AC and ground are isolated from the rest of the boat, then the remaining source of shock hazard is the secondary side of the transformer.
See diagram 6 , stick the victron in a big plastic box. Disconnected grounds are ABYC ok.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 15:36   #101
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
Disconnected grounds are ABYC ok.
For the umpteenth time, we've already agreed on that. What IS your problem??
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 15:41   #102
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by Lake-Effect View Post
For the umpteenth time, we've already agreed on that. What IS your problem??
You , arguing connected grounds, were safer
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2022, 15:49   #103
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,548
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
You , arguing connected grounds, were safer

Ah... a warm sunset, a little retsina.... Someone's ready for bed, hmmm? Nite nite.
Lake-Effect is offline   Reply With Quote
Old 04-07-2022, 21:05   #104
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Shore Ground NOT Connected to Isolation Transformer

GBN #98
I caution you against using a 14 year old document that is updated every year as a valid source of information.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 05-07-2022, 11:09   #105
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Shore Ground NOT Connected to Isolation Transformer

Quote:
Originally Posted by goboatingnow View Post
Given here RCBOs are cheap I would always have one fitted right behind my shore power cable entry. If fitted this allows no shore earth to come in contact with an isolation transformer.

RCBOs can be less usefully fitted to the output side of the transformer as the existence of sneak return paths is virtually eliminated by taking earth ground out of the equation. But I’d still fit them anyway albeit they are less effective. MCBs of course should be fitted to the output side
So I switched over to a new 100ft Shore cable yesterday from my somewhat frayed old one..... this cable was spliced on to a 50ft extension by the Shipyard before plugging into the shore pedestal
AT THE SPLICE THE ELECTRICIAN HAD NOT CONNECTED THE GROUND WIRE ...Just L & N
Part of my querie on first post .

So I was planning on installing the new RCBO before the onboard Junction box and Isolation Transformer today.....

But does that do anything given the way the yard wired the splice??
Pelagic is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Victron Isolation Transformer and Ground Fault Issue mdsilvers Electrical: Batteries, Generators & Solar 11 22-02-2021 13:05
shore power charger as isolation transformer jaed Electrical: Batteries, Generators & Solar 0 23-06-2012 03:14
Isolation Transformer to also Provide Dual Voltage Shore Power ? SvenG Electrical: Batteries, Generators & Solar 21 04-03-2011 07:47
Isolation Transformer and SSB Sailabel Marine Electronics 3 02-04-2010 16:30
Isolation transformer Pa La O La Construction, Maintenance & Refit 11 12-08-2008 13:14

Advertise Here


All times are GMT -7. The time now is 09:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.