I was finally able to get back to our
boat, and I believe I've found the problem. The masterbus/canbus module on one of our MLI ultra's bit the dust.
I went back and tested each device individually, and if it worked I added the Easyview. Everything passed except for one of the
batteries which doesn't show up and interestingly neither would the Easyview when I added it for grins.
I previously said you need to wait for the masterbus to settle. This, I now believe, is wrong. The bus should settle pretty quick if all is well. I think what was happening is that the battery's masterbus module was flakey and that caused the
network to take time to settle. Now that it's finally dead, and I'm not getting any transitory behavior.
Moral of the story is I should have done individual device tests when I tested the wires. That's what happens when you've been in management too long! You forget the basics.
I'm hoping Mastervolt made the
batteries such that the masterbus module can just be replaced.