Preventing LFP bank from being fully charged

Hi everyone,

I'm a full time live aboard and planning to leave the boat in a marina for a couple weeks. I'm going to leave the DC fridge and a few other things running while I'm away.

The issue is I have a LFP house bank and I'd like to prevent it from getting fully charged. I can't simply disconnect part of my solar panels because if there are several cloudy days in a row (normal as we're in the rainy season) I could end up depleting the house bank. I have victron mppts and a BMV-712 monitor. Is there any way I can use them to achieve that?

Thanks in advance!
LifesBetterWhenYoureBeating is offline   Reply With Quote
Old 29-05-2023, 10:10   #2
Registered User

Join Date: Nov 2019
Location: Vancouver
Boat: Ericson 27
Posts: 516
Re: Preventing LFP bank from being fully charged

Are you using a GX device (such as a Cerbo GX) and DVCC? If so, it’s easy. Just go onto your Cerbo and set an override on the DVCC voltage. When my boat is alongside for king periods of time, I usually set this to 13.2v or 13.3v which translates to an SoC of around 60%. I colloquially refer to this as “Storage Mode” and will then remote in the day before I intend to use the boat, remove the override, and let it come back up to 100% charge.

If you don’t have this kind of a setup, just adjust the configuration on your charging sources directly, and limit the voltage that way.
hjohnson is offline   Reply With Quote
Old 29-05-2023, 10:16   #3
Registered User

Join Date: Jan 2015
Location: Victoria BC
Boat: Rafiki 37
Posts: 1,390
Re: Preventing LFP bank from being fully charged

Yeah I do something similar with my cerbo and DVCC, except my rec BMS controls it so I can just adjust one value on the BMS and it'll sit at 65% indefinitely at the dock.

I don't think you can use BMV to control DVCC so you'll have to go into each MPPT and change them all individually
__________________
www.saildivefish.ca
alctel is offline   Reply With Quote
Old 29-05-2023, 10:45   #4
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 960
Re: Preventing LFP bank from being fully charged

As others have said voltage corresponds to SoC% and a battery can't be charged to a higher voltage than the charger puts out.

Note while most LFP cells can be charged to 3.65V per cell (14.6V for "12V" battery) it doesn't have to. In fact in most cases one can get away with a lot less and that improves battery longevity.

You may also want to check the absorption time. Most chargers will charge LFP to an excessive long time in absorption which while not terrible is going to result in SoC% rising.

Depending on your setup you may be able to set everything in a central controller like CerboGX or will need to do it seperately in each charging source.
Statistical is offline   Reply With Quote
Old 29-05-2023, 11:51   #5
Senior Cruiser

Cruisers Forum Supporter

Join Date: May 2021
Boat: Passport 41
Posts: 376
Re: Preventing LFP bank from being fully charged

Quote:
Originally Posted by Statistical View Post
As others have said voltage corresponds to SoC% and a battery can't be charged to a higher voltage than the charger puts out.

Note while most LFP cells can be charged to 3.65V per cell (14.6V for "12V" battery) it doesn't have to. In fact in most cases one can get away with a lot less and that improves battery longevity.

You may also want to check the absorption time. Most chargers will charge LFP to an excessive long time in absorption which while not terrible is going to result in SoC% rising.

Depending on your setup you may be able to set everything in a central controller like CerboGX or will need to do it seperately in each charging source.
I'll have to change it on each charging source.

So I'd just set the absorption voltage to something like 13.4? Do I need to change the float voltage as well?
LifesBetterWhenYoureBeating is offline   Reply With Quote
Old 29-05-2023, 11:56   #6
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 960
Re: Preventing LFP bank from being fully charged

Quote:
Originally Posted by LifesBetterWhenYoureBeating View Post
I'll have to change it on each charging source.

So I'd just set the absorption voltage to something like 13.4? Do I need to change the float voltage as well?
Yes. Sometimes chargers have separate bulk and absorption numbers if so change both to the same lower value. Sometimes they just have a single absorption value which controls both bulk and absorption. If there is an absorption time it may be very high (like 4+ hours) which will cause the Soc to rise significantly so you may want to reduce that as well down to 15 minute to an hour depending on the charger output compared to battery capacity.

Ideally float voltage is already down around 13.4V or lower. LFP don't really like to float charge. So "float" isn't really being used to charge the battery but rather power low always on loads so the battery doesn't discharge.

Resting voltage of LFP is around 13.4V. Even if you charge it to beyond that and the battery voltage rises higher (13.5V to 14.6V measured when resting = no charge or loads) that ends up being a surface charge which quickly bleeds away and the voltage falls back to around 13.4V once charging source and loads are removed usually within a few hours but at most 24 hours.

So 13.4V or even 13.2V "float" is a good value for LFP. It is right at or just below the resting voltage of the battery and very likely will never charge the battery just ensure it doesn't discharge. If heavy loads come on the float output won't be enough to cover them and then energy will flow out of the battery so voltage will drop causing the charger to go back to bulk/asborb to refill the used capacity.
Statistical is offline   Reply With Quote
Old 29-05-2023, 16:27   #7
Registered User

Join Date: Nov 2019
Location: Vancouver
Boat: Ericson 27
Posts: 516
Re: Preventing LFP bank from being fully charged

Quote:
Originally Posted by alctel View Post
Yeah I do something similar with my cerbo and DVCC, except my rec BMS controls it so I can just adjust one value on the BMS and it'll sit at 65% indefinitely at the dock.

I don't think you can use BMV to control DVCC so you'll have to go into each MPPT and change them all individually
I’m using a REC ABMS myself, but thought you could use a BMV or Smartshunt as your system controller as well. I could easily be wrong on that.
hjohnson is offline   Reply With Quote
Old 29-05-2023, 16:46   #8
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 960
Re: Preventing LFP bank from being fully charged

Quote:
Originally Posted by hjohnson View Post
I’m using a REC ABMS myself, but thought you could use a BMV or Smartshunt as your system controller as well. I could easily be wrong on that.
BMV can provide data but it can't control anything. For DVCC you need a Cerbo GX. Granted in any simple system with 1 inverter/charger and 1 or 2 solar charge controller it isn't that hard to just set them all.
Statistical is offline   Reply With Quote
Old 30-05-2023, 22:49   #9
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,633
Re: Preventing LFP bank from being fully charged

you can lower the bulk / absorb voltage in the mppt's 13.5v or so while away
smac999 is offline   Reply With Quote
Old 31-05-2023, 04:45   #10
S/V rubber ducky
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: heading "south"
Boat: Hunter 410
Posts: 20,362
Re: Preventing LFP bank from being fully charged

Quote:
Originally Posted by LifesBetterWhenYoureBeating View Post
Hi everyone,

I'm a full time live aboard and planning to leave the boat in a marina for a couple weeks. I'm going to leave the DC fridge and a few other things running while I'm away.

The issue is I have a LFP house bank and I'd like to prevent it from getting fully charged. I can't simply disconnect part of my solar panels because if there are several cloudy days in a row (normal as we're in the rainy season) I could end up depleting the house bank. I have victron mppts and a BMV-712 monitor. Is there any way I can use them to achieve that?

Thanks in advance!
I just lowered my solar setpoints
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Frequency of getting LFP batteries fully charged sailorboy1 Lithium Power Systems 24 04-02-2023 07:50
24V bank being charged by outboard alternator? Onebadlarry Electrical: Batteries, Generators & Solar 2 27-08-2020 22:23
Lifeline AGM's Fully Charged Voltage? frankson Electrical: Batteries, Generators & Solar 61 12-10-2018 12:54
Flashing "Charge light" when batteries fully charged gspeak Electrical: Batteries, Generators & Solar 3 17-06-2014 06:51
12.5 Volts Fully Charged? Meck Electrical: Batteries, Generators & Solar 7 18-09-2009 08:12

Advertise Here


All times are GMT -7. The time now is 20:32.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.