Onan Fault 41

I have an Onan 5 KVA diesel generator, model MDKAU.
We’ve only owned the boat for 6 months. The diesel side checked out well in a test before purchase. It’s run well since.
I now have a refusal to start. Primings sounds as normal. The engine turns over day twice, then stops.
Lights show 3 flashes. Fault code flashes 41.
I’ve checked the basics like battery and fuel. All seems fine.
The online searches I’ve done say an electrical side fault causing a shutdown.
Any suggestions very gratefully received.
Oh, I’m not an electrician or anything like it. 😄
seaskip is offline   Reply With Quote
Old 10-07-2021, 04:51   #2
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,083
Re: Onan Fault 41

Neither am I. With no specific knowledge of that engine or its error codes, I recommend that you clean every connection from the battery to the ground for the starter. It sounds like you are not getting enough current through the starter motor.
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 10-07-2021, 06:10   #3
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,139
Images: 241
Re: Onan Fault 41

‘MDKAU ‘ Service Manual
https://www.seapowermarine.com/seapo...ice-Manual.pdf
[9. Troubleshooting begins on page 49 of 66]

The genset controller provides extensive diagnostics by causing the amber status lamp on the control switch to blink.
Following a shutdown, the indicator lamp will blink 1, 2, 3, 4 or 7 times, pause, and then repeat the blinking.
The number of blinks is the shutdown code. Blinking continues for five minutes and stops. Pressing STOP three times restores blinking. (If you press STOP again, blinking stops entirely and you have to start over by pressing STOP three times.)
•One blink indicates shutdown due to high en-gine temperature.
•Two blinks indicate shutdown due to low oilpressure.

•Three blinks indicate shutdown due to a condi-tion normally requiring service by a trained andexperienced person.
To access the second-level, two-digit shutdown code, press STOP once. The two-digit code consists of 1 to 6 blinks, a brief pause, and then 1 to 9 blinks.
The first set of blinks represents the tens digit and the second set of blinks the units digit of the shutdown code number.

For example, Shut-down CodeNo. 23 blinks as follows:blink-blink—pause—blink-blink-blink—long pause—repea
t•Four blinks indicate shutdown due to a failureto start within the time allowed for cranking.
•Seven blinks indicate shutdown due to a lossof raw water flow for engine and exhaust cool-ing.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 10-07-2021, 14:22   #4
Registered User

Join Date: Dec 2015
Location: Mid north coast NSW Australia
Boat: Chamberlin 12.4m
Posts: 145
Re: Onan Fault 41

Thankyou folks. I’ll proceed as much as my limited talent allows. ��
Gordmay, that checks out how I got the 41 code. ��
I’ll keep the book though. Great resource.
seaskip is offline   Reply With Quote
Old 10-07-2021, 14:31   #5
Senior Cruiser

Cruisers Forum Supporter

Join Date: May 2013
Location: Oregon to Alaska
Boat: Wheeler Shipyard 83' ex USCG
Posts: 3,499
Re: Onan Fault 41

If the engine starts and then stops, it's usually the oil or temperature sensor has failed. When pressing the starting button the sensors are bypassed. When you release the start button the sensors become active so low oil pressure or high temp will stop the engine. The sensor usually completes a circuit by going to ground. To troubleshoot, remove the sensor wire and start. If the engine continues to run it was a bad sensor. Some engines also have an exhaust temperature sensor.
I wouldn't run a generator with the sensors disabled for anything more than a few minutes.
Lepke is offline   Reply With Quote
Old 12-07-2021, 04:35   #6
Registered User

Join Date: Dec 2015
Location: Mid north coast NSW Australia
Boat: Chamberlin 12.4m
Posts: 145
Re: Onan Fault 41

Thanks Lepke,
That’s interesting. I’ll try again tomorrow, but I’m pretty sure I’m holding the starter button down and it’s shutting down before starting.
Many thanks though.
seaskip is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan genset keeps stopping fault code 13 harvey hellman Electrical: Batteries, Generators & Solar 15 26-06-2019 03:09
Onan Generator Emergency Stop Switch trips - how to diagnose fault gstent Electrical: Batteries, Generators & Solar 3 02-03-2019 04:54
Prop Shaft Fault fishwife Engines and Propulsion Systems 1 09-09-2010 18:20
AC not working (My Fault) raymillsus Plumbing Systems and Fixtures 1 29-07-2008 13:15
Continuity Gnd. Fault Test GordMay Electrical: Batteries, Generators & Solar 0 13-10-2005 11:26

Advertise Here


All times are GMT -7. The time now is 09:33.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.