Quote:
Originally Posted by s/v Jedi
Or, alternatively, you do it like I (and Victron) recommend: keep the system at 240V/60Hz all the way incl. inverter/chargers, then add an autotransformer right at the distribution breaker panel to create a new Neutral.
The attached diagram shows two distribution groups, each with it’s own autotransformer: you can delete one for a smaller system.
|
Indeed yes
240 to 120 or 120 to 240 is fine. What’s not fine is trying to do both in the same transformer as the OP is trying to achieve.