Newby requesting advice about 120/ 240 volt wiring

I'm in the process of buying a new (old) boat. The owner sent me a 2005 survey which I would like to quote. "... Ensure that all AC voltage wiring throughout the vessel is sized for 120- volt AC voltage/30-amp service- vessel was wired for 240-volt service and as such wiring is smaller and must be upgraded..."

The owner hasn't "upgraded" the wiring. Some of you have European built boats. Did you upgrade yours? How serious is this as a fire hazard? Should I walk away from the deal if he refuses to rewrite the boat?
TIA
Bob
Menby is offline   Reply With Quote
Old 15-06-2012, 16:58   #2
Registered User
 
mikefossl's Avatar

Join Date: Aug 2008
Location: Hawaii
Boat: CS 40
Posts: 171
Re: Newby requesting advice about 120/ 240 volt wiring

It really depends on how extensive the AC wiring is and the expected loads. In our case we have 4 AC outlets. Re-wiring the AC would not be a huge job.
__________________
Michael Fössl
S/V Second Jump
British Columbia
mikefossl is offline   Reply With Quote
Old 15-06-2012, 17:44   #3
Registered User
 
jeremiason's Avatar

Join Date: Oct 2010
Location: Punta Gorda, Florida
Boat: Cruisers Yachts 420 Express
Posts: 1,429
Images: 2
Send a message via ICQ to jeremiason Send a message via Yahoo to jeremiason Send a message via Skype™ to jeremiason
Re: Newby requesting advice about 120/ 240 volt wiring

If you get serious about this boat... DO NOT trust a survey from 2005. Pardon the pun, but a lot of water has passed under the keel in seven years and their maybe more problems...

I am no electrician, but higher voltage means lighter wire... So converting lighter wire to lower voltage means more resistance and higher heat or in other words FIRE!

Yes, it is easy to replace AC wiring, if you know what you are doing. If not depending on wher eyou live it will cost $60-$100 per hours to pay an electrician to do it. Depending on your wiring, you can figure the hours involved, not to mention the cost of materials.
__________________
Tom Jeremiason
Punta Gorda, Florida

jeremiason is offline   Reply With Quote
Old 15-06-2012, 18:03   #4
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,436
Re: Newby requesting advice about 120/ 240 volt wiring

Quote:
Originally Posted by Menby View Post
I'm in the process of buying a new (old) boat. The owner sent me a 2005 survey which I would like to quote. "... Ensure that all AC voltage wiring throughout the vessel is sized for 120- volt AC voltage/30-amp service- vessel was wired for 240-volt service and as such wiring is smaller and must be upgraded..."

The owner hasn't "upgraded" the wiring. Some of you have European built boats. Did you upgrade yours? How serious is this as a fire hazard? Should I walk away from the deal if he refuses to rewrite the boat?
TIA
Bob
Welcome aboard Menby.

Bit difficult to give detailed advice as not enough data has been supplied but as a generalisation, this is a potential fire hazard. The degree of risk is in the detail!

Should you walk away? Well that is even more difficult. Is this the only sticking point, how much do you want this particular boat? Is it just a matter of dollars?

Previous posts are spot on IMO.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 15-06-2012, 18:51   #5
Registered User

Join Date: Jan 2012
Location: CHARLESTON, SC
Boat: Schucker 436
Posts: 112
Re: Newby requesting advice about 120/ 240 volt wiring

If the surveyor said it needs to be changed, factor that into the reduction of the price. Most European boats are well built, but the AC loads are half the current we use in the U.S. The circuit breakers may protect what ever load current is expected for the wire, but that may be half what you need for 120 Volt outlets, like an electrical cooking device that needs over 10 amps. Like previously said, if you can't do the work yourself, expect a big bill. Most older boats are overdue for new wiring and an updated 120 volt AC panel that shows reverse polarity, new breakers, and meters. If you only have 5 or 6 outlets this may be easier than you thought. Calculte from the shore power outlet to the panel, new AC panel, and marine boat cable all the way to the outlets. Even the European outlet boxes will not fit U.S. outlets, GFCI, and covers. If you plan on getting insurance, most good surveyors will require wiring that meets ABYC electrical standards. Good luck.
RUSTYNAIL is offline   Reply With Quote
Old 15-06-2012, 18:59   #6
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Newby requesting advice about 120/ 240 volt wiring

Normal household voltage has nothing to due with the size of the wire required, it's the size of the current draw through a wire that dictates it's size. If the original wiring for the branch circuits are protected with properly size circuit breakers, it doesn't matter if you run 120v or 230v through the wire.

If the boat was wired for 230v 16a shore power, shore power to circuit breaker box wiring will need to be upgraded for 30a or 50a to be used at most US marinas.
DotDun is offline   Reply With Quote
Old 15-06-2012, 19:29   #7
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,436
Re: Newby requesting advice about 120/ 240 volt wiring

Quote:
Originally Posted by DotDun View Post
Normal household voltage has nothing to due with the size of the wire required, it's the size of the current draw through a wire that dictates it's size. If the original wiring for the branch circuits are protected with properly size circuit breakers, it doesn't matter if you run 120v or 230v through the wire.

If the boat was wired for 230v 16a shore power, shore power to circuit breaker box wiring will need to be upgraded for 30a or 50a to be used at most US marinas.
While correct in as far as you go, one must remember the load (power rating) of the appliances that you intend to use.

For instance, 2000W hot water jug requires 2000W regardless of whether is made in European or USA. Your USA appliance will be drawing twice the current compared with a 230 V unit. So add a couple of appliances to the circuit and you will find the breaker popping!
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 15-06-2012, 20:04   #8
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Newby requesting advice about 120/ 240 volt wiring

Quote:
Originally Posted by Wotname View Post
While correct in as far as you go, one must remember the load (power rating) of the appliances that you intend to use.

For instance, 2000W hot water jug requires 2000W regardless of whether is made in European or USA. Your USA appliance will be drawing twice the current compared with a 230 V unit. So add a couple of appliances to the circuit and you will find the breaker popping!
1) You are absolutely correct that one must consider the power required on each branch circuit to determine if that wire/breaker is suitable for the task.

2) If by 'water jug' you mean water heater, your example is flawed. Keeping the same 2000watt @ 230v resistive water heater, it will magically become a 544watt @ 120v resistive water heater and fit well within the power delivered on the original wiring. It'll simply take longer to heat water.

My boat was wired to EU standards using 10a and 16a breakers on the branch circuits. Each circuit with receptacles carried a 16a breaker with appropriate wire gauge. Works fine with 120v, albeit each circuit is now only capable of 1920w/va vs. the original 3680w/va.
DotDun is offline   Reply With Quote
Old 15-06-2012, 21:17   #9
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,436
Re: Newby requesting advice about 120/ 240 volt wiring

Quote:
Originally Posted by DotDun View Post
1) .....

2) If by 'water jug' you mean water heater, your example is flawed. Keeping the same 2000watt @ 230v resistive water heater, it will magically become a 544watt @ 120v resistive water heater and fit well within the power delivered on the original wiring. It'll simply take longer to heat water.
.......
I see we are comparing apples and oranges .

You are taking the 230V (2000W) water heater and supplying it with 120V and so your figures are correct.

I was thinking more of the electric kettle and plugging in a 120 V (2000W) USA unit into this boat. Thus the current draw will be double (rounded off figures) when compared with a 230 V (2000W) European unit.

__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 16-06-2012, 08:14   #10
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by Wotname
I see we are comparing apples and oranges .

You are taking the 230V (2000W) water heater and supplying it with 120V and so your figures are correct.

I was thinking more of the electric kettle and plugging in a 120 V (2000W) USA unit into this boat. Thus the current draw will be double (rounded off figures) when compared with a 230 V (2000W) European unit.

Most conventional EUropean outlets a rated at 3000w. Hence the wiring is good for about 15 amps. ( in fact it is usually rated for more ) hence you have outlets of about 1600w in 110 land without wiring changes. This may be more then enough for most people. That would mean just rewiring any high power consumers like water heating etc

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 16-06-2012, 08:22   #11
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: Newby requesting advice about 120/ 240 volt wiring

Why not simply look at ther size of the wires that are there, and compare them to what should be there for USA current? THEN and only then will you know.
Stu Jackson is offline   Reply With Quote
Old 16-06-2012, 08:45   #12
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,521
Re: Newby requesting advice about 120/ 240 volt wiring

Quote:
Originally Posted by Stu Jackson View Post
Why not simply look at ther size of the wires that are there, and compare them to what should be there for USA current? THEN and only then will you know.
Yes, although it sounds like the surveyor already looked. At any rate, it's probably one of the easier items to redo compared with other boat problems! How extensively do you use AC? If you're not running a heater or heavy load the wiring may be fine. Find what size it is and approx lengths and determine your maximum loading with what you have. If I remember right much house wiring is 15-20 amps.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 16-06-2012, 08:50   #13
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by Cheechako
Yes, although it sounds like the surveyor already looked. At any rate, it's probably one of the easier items to redo compared with other boat problems! How extensively do you use AC? If you're not running a heater or heavy load the wiring may be fine. Find what size it is and approx lengths and determine your maximum loading with what you have. If I remember right much house wiring is 15-20 amps.
Some European boats are wired as ring main circuits. Hence the ring could have 40-60 amp capacity. This gives you far more lee-way. The previous posters are correct. You need to actually look at what you've got.

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 23-06-2012, 15:19   #14
Marine Service Provider

Join Date: Apr 2010
Location: South Florida and the Caribbean
Boat: Former owner of a 2001 34' Gemini 105MC Catamaran
Posts: 158
Re: Newby requesting advice about 120/ 240 volt wiring

This is a very loaded question about the suitability and condition of the AC electrical system. I for one, would spend alot of time going through the vessel looking at the electrical system making sure things were complaint with CFR and ABYC E-11 reccomendations. One thing I will do at the stsart of the inspection is power everything up on the panel to see if any breakers pop. Some boat owners will over amp the circuits with upgrades and will place stickers on the panel so as to not run one thing with another.. Very dangerous and good way to short a circuit out or even cause a boat fire. I normally will spend hours inspecting these systems on bigger yachts, especially older ones. I have hundreds of pictures of "home projects" where I was amazed no one got killed on the boat prior to the survey.
__________________
Capt. John Banister, AMS®
SAMS® Accredited Marine Surveyor
Palm Beach Gardens, Florida
SuenosAzules is offline   Reply With Quote
Old 01-07-2012, 08:02   #15
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
My boat is 220 wired and the survey said the same thing. Then I started thinking about it. Why go 110? It's worked fine for almost 30 years. I can order any appliance I want in 220 v so just leave it alone. I have a step down transformer from 220 to 110 when required and a couple of 12 v to 110 for small things. Now as things go bad or if I have to replace wires I will replace with heaver wire so that one day I might decide to switch it over and it will just require breaker changes. but so far, no problems.
DSDman is offline   Reply With Quote
Reply

Tags
wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 10:10.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.