Thought I would resurrect this thread since great info was being shared, specifically for Firefly Oasis, and then stopped.
Since these batteries are a specialized
AGM but in many ways behave like low resistance
Lithium - definitely somewhat unique - and they are expensive, I was hoping that Firefly would provide more clarity with instructions, something akin to Battle Born Batteries' excellent solar charge setup instructions (Victron examples
https://battlebornbatteries.com/prog...ge-controller/ and
https://battlebornbatteries.com/conf...etooth-dongle/ ). But that's not the case.
I'll condense requests I've sent to Firefly, eMarine and Ocean Planet Energy - since I seemingly experience early float with my 900Ah bank of six FF Oasis L15+ at 4V each. The six batteries are set up 3+3 series parallel. In the 3 months since install they've clocked only 5 cycles, with most daily SoC varying between 85% overnight to 100% mid to late morning.
I am open to the suggestion that I simply don't have enough charging capability for the size of FF Oasis bank.
Solar panels are 12 years old and replacing with modern higher yield
panels can more than double installed capacity to over 2000W in the same footprint.
Charging infrastructure is
Victron apart from alternators, everything running latest available firmware. My
Victron Centaur battery chargers (100A + 50A) are not programmable with only a basic
AGM dip setting being used. However, the battery bank spends 99% of it's life being charged by a Victron SmartSolar 150/80
MPPT charge controller with a Victron BMV-712 battery
monitor combined on a Victron VE Smart
Network with temperature
sensor. My
solar panels will typically produce an actual maximum of around 700-750W around mid day at the moment (early March in Bahamas).
I also have a
Balmar SG200 monitor on board, recently installed to get a second set of eyes on the bank since it has a carbon foam battery preset, and hopefully give me a decent SoH calculation. At the moment, with typical shallow discharges of 10-15% overnight the SG200 tracks the Victron BMV closely.
Basic
MPPT setup follows the "Firefly User’s Manual for the “OASIS” G31 & the L15+ June 2019" document provided to me by eMarine who provided the batteries (but also available on Cruisersforum in various threads). It is set up with absorption voltage at 14.4V and float voltage 13.4V. I currently have absorption stage set to adaptive with maximum absorption set to 5 hours and tail current set to 6 Amps, half the recommendation (the user manual states 6 Amps for the L15+ at 4V which would be 12 amps for my 12V series/parallel bank, but this lower tail current is an attempt to avoid early float).
The BMV-712 has a charged voltage of 14.2V, tail current at 1.3% (which corresponds to a 12A tail current - pretty meaningless anyways as the boat's base load varies between 5 and 20 amps depending on which of 3 fridges are running and two 2000 inverters sucking up some juice in the background), and charge detection 10 minutes. These are the current settings, I tinker with them basically weekly.
I find that my solar MPPT controller typically goes into float:
(1) If the bank is drawn down to 60% SoC for example, float happens while the BMV still reports only 80-85% state of charge. The BMV usually syncs to 100%, but after these deeper discharges it will show SoC slowly build to 80-85% and then, boom, sync to 100%. I've not had a deeper than 80% SoC discharge since installing the
Balmar SG200 and cannot compare it's behavior.
(2) If the bank is drawn down 10-15% overnight (which is typical), float happens mid-to-late morning but a few times when I changed the MPPT's float voltage to the 14.4V absorption level - for the sake of experimenting - the batteries would sometimes soak up the full 50-60 amps from my charge controller - which to me looks like they did not spend enough time in absorption.
I guess I'm looking for some recent learnings from other Victron MPPT and FF Oasis owners, specifically around absorption and float settings and behavior.