Listed Voltages of Ampere Interrupting Capacity Ratings

Could someone help me understand why AIC fuse ratings are listed as amps of varying voltages? For instance, a class T fuse is rated for 20,000A @ 125V DC, and an MRBF is rated 10,000A @ 14V DC. If I wanted to compare the AIC of these two fuses wouldn't I want to compare their interrupt capacity at the same voltages? Is there a good way to convert the AIC to make this comparison? I would imagine that increasing the voltage will decrease the interrupt capacity? So the AIC of an MRBF at 125V DC is something like 800A, and the AIC of a class T fuse at 14V DC is something like 90,000A?
expozen is offline   Reply With Quote
Old 25-08-2019, 16:08   #2
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Listed Voltages of Ampere Interrupting Capacity Ratings

AFAIK no; it's amps that burn not watts.

So at the very low end of their voltage range, tiny power watts will blow the fuse compared to at higher voltages.

My understanding is the voltage rating is a maximum, long as that circuit is below then it's just amps and time delay you need to worry about.

DC being much harder, a completely different scale from AC as well.
john61ct is offline   Reply With Quote
Old 25-08-2019, 17:26   #3
Registered User

Join Date: Jul 2017
Location: Oakland, CA USA
Boat: Ranger 33
Posts: 54
Re: Listed Voltages of Ampere Interrupting Capacity Ratings

Oh... that makes more sense.

I had come to that conclusion because the MRBF fuse is was researching listed the AIC as:

10000A @ 14V DC
5000A @ 32V DC
2000A @ 58V DC

Which made me think AIC was a function of voltage.

So, if I wanted to protect a 12V CALB CA 180 AH LFP bank that has a cell internal resistance of 0.5 milliohms, the estimated theoretical short circuit current would be (4 Cells * 3.65 V) / ((4 Cells * 0.5 MilliOhms) + 0.5 MilliOhms external resistance) = 5,840 A

Which would mean I could use either a Class T or MRBF fuse type. And the only difference would be that the Class T would break in a 10th of the time as a MRBF would? Would that be a critical characteristic in this scenario?
expozen is offline   Reply With Quote
Old 25-08-2019, 18:39   #4
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: Listed Voltages of Ampere Interrupting Capacity Ratings

The ratings decline with increased voltage because at higher voltages, the arc can jump a longer distance and potentially weld the circuit closed, thereby defeating the fuse. As a result, all fuses and breakers have both current and voltage ratings, and you need to stay below both limits.


Related to this, DC circuits are harder to break/fuse than AC because there is no zero-voltage crossing. A DC circuit will arc continuously, and as a result is much harder to extinguish. An AC circuit stops arcing every half cycle when the voltage goes to zero, the lights back up again. So any arc self-extinguishes at the zero crossing, making it easier to break the circuit and keep it broken. If you look at breaker ratings, the DC rating will pretty much always be lower than the AC rating, and the DC voltage typically much lower. High current, high voltage DC breakers can be very expensive as a result of this, and fuses are often used instead.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
capacity ratings for trailer cruisers? Divensail88 Monohull Sailboats 3 12-05-2013 08:01
Voltages vs Percentages unbusted67 Electrical: Batteries, Generators & Solar 9 21-07-2010 10:54
Voltages from a Three-Step Regulator Cheechako Electrical: Batteries, Generators & Solar 11 24-11-2009 09:30
Battery-Charging Voltages Rick Electrical: Batteries, Generators & Solar 41 05-05-2009 20:23
Gel and AGM Charging Voltages HowardZ Electrical: Batteries, Generators & Solar 16 22-04-2009 05:49

Advertise Here


All times are GMT -7. The time now is 14:03.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.