Linking just the negatives of two batteries in series

I am trying to clean up the spider web of cables around my battery bank. I'm building a battery box as part of the process.

The neatest way to do this is to run the outside negative through the box across the inside battery and then have 2 negative cables running to the ground on the transmission housing.

However that got me to thinking. Can't I just run the two negative terminals in series creating just one cable to ground.

I'd have two positives back to the main switch as always.

The batteries are 27 DC with 750 CCA
Attached Thumbnails
Click image for larger version

Name:	Battery.jpg
Views:	361
Size:	453.5 KB
ID:	232248  
Tmacmi is offline   Reply With Quote
Old 10-02-2021, 08:58   #2
Registered User
 
Spot's Avatar

Join Date: Jan 2019
Location: Minnesota, USA
Boat: 21' trailer sailor & 8' sailing dinghy
Posts: 1,747
Re: Linking just the negatives of two batteries in series

Negatives are linked for parallel, not series...
Attached Thumbnails
Click image for larger version

Name:	series_parallel.png
Views:	156
Size:	8.0 KB
ID:	232252  
__________________
Big dreams, small boats...
Spot is offline   Reply With Quote
Old 10-02-2021, 09:05   #3
Registered User
 
Shrew's Avatar

Join Date: Aug 2010
Posts: 3,105
Re: Linking just the negatives of two batteries in series

I see batteries in neither Series or Parallel. I see two battery banks each with a single battery.
Shrew is offline   Reply With Quote
Old 10-02-2021, 12:22   #4
Registered User
 
The Way's Avatar

Join Date: May 2011
Location: On the boat, currently Tampa Bay, Florida
Boat: Dickerson ketch, 36'
Posts: 211
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by Tmacmi View Post
I am trying to clean up the spider web of cables around my battery bank. I'm building a battery box as part of the process.

The neatest way to do this is to run the outside negative through the box across the inside battery and then have 2 negative cables running to the ground on the transmission housing.

However that got me to thinking. Can't I just run the two negative terminals in series creating just one cable to ground.

I'd have two positives back to the main switch as always.

The batteries are 27 DC with 750 CCA
Yes. Mine have been that way for years. It makes sense since there is a common ground somewhere anyway. One is the start battery, the other a deep-cycle house battery. I connect the 2 negatives with a cable, and one of the 2 to the ground with another cable.

Fair winds,
Jack
The Way is offline   Reply With Quote
Old 10-02-2021, 12:28   #5
Registered User

Join Date: Jul 2019
Location: South Haven Michigan
Boat: Beneteau 331
Posts: 381
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by Shrew View Post
I see batteries in neither Series or Parallel. I see two battery banks each with a single battery.
Yes. Exactly. That is the starting point.

The question is can I run the negative from terminal to terminal (parallel, thank you) and thence on to the ground connection.

It appears the answer is yes.

Follow up question, do I have to increase the gauge of the negative ground wire because it is now carrying increased load?
Tmacmi is offline   Reply With Quote
Old 10-02-2021, 15:07   #6
Registered User

Join Date: Mar 2020
Location: Wherever we please, GOM
Boat: 46 ft cutter
Posts: 177
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by Tmacmi View Post
Yes. Exactly. That is the starting point.

The question is can I run the negative from terminal to terminal (parallel, thank you) and thence on to the ground connection.

It appears the answer is yes.

Follow up question, do I have to increase the gauge of the negative ground wire because it is now carrying increased load?
Depends on the length of cable. Check the tables, for a very short cable, there might not be any significant voltage drop with your existing cabling, assuming re-use.
PirateGuy is offline   Reply With Quote
Old 11-02-2021, 07:23   #7
Registered User

Join Date: Jul 2019
Location: South Haven Michigan
Boat: Beneteau 331
Posts: 381
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by PirateGuy View Post
Depends on the length of cable. Check the tables, for a very short cable, there might not be any significant voltage drop with your existing cabling, assuming re-use.
I'm having all new cables made that's part of why I'm asking. The length is about 4'
Tmacmi is offline   Reply With Quote
Old 11-02-2021, 08:59   #8
Registered User

Join Date: Oct 2007
Location: Isla Saboga, Las Perlas, Panama
Boat: 1988 48' Offshore
Posts: 255
Re: Linking just the negatives of two batteries in series

If the batteries aren't part of the same bank, I think it's probably OK to 'daisy-chain' the negatives together and then run only one wire to the ground buss. Just make sure the cable is a large enough gauge.

Batteries on the same bank though should all have identical-length cables run to the busses.
oldjags is offline   Reply With Quote
Old 11-02-2021, 09:05   #9
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,044
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by Tmacmi View Post
I'm having all new cables made that's part of why I'm asking. The length is about 4'
we also need to know the existing AWG wire size and highest amperage expected to tell if the existing cable is okay... wire size charts are also easy to look up yourself, btw.
zstine is offline   Reply With Quote
Old 11-02-2021, 09:39   #10
Registered User

Join Date: Mar 2015
Location: Boston's North Shore
Boat: Pearson 10M
Posts: 839
Re: Linking just the negatives of two batteries in series

There is no harm in oversizing the common ground cable. Your highest current draw is probably starting your engine, and that's a time where minimizing voltage drop can make a noticeable difference.
I once made oversize battery cables for a car I owned (the parts were free) and the engine cranked noticeably faster.
With your current battery arrangement, you do not need to keep cable lengths the same.
There is a lot that can be learned from a good book on 12v systems.
guyrj33 is offline   Reply With Quote
Old 11-02-2021, 09:52   #11
Registered User

Join Date: Oct 2014
Posts: 7,458
Re: Linking just the negatives of two batteries in series

I see several opposite polarity wires crossing and laying in direct contact with each other which wires are NOT fuse protected such that if they short to each other there will be huge and unprotected circuit of power.

Never have opposite polarity wiring or cabling come in contact, or potential contact with each other, if such portion of the positive polarity wire or cable is not protected by circuit breaking devices, [a fuse or a circuit breaker] to the source of the power, be that source the terminal of a battery or a bus connection.

The wiring in the image is hazardous and amateurish. Makes me wonder what the rest of the wiring is like.

Question:

Is this bank of batteries:
1) two completely separate battery banks;
or are they
2) two batteries in parallel circuitry?

Answer the above question, then and only then can forum members provide guidance.

Awaiting your response.
Montanan is offline   Reply With Quote
Old 11-02-2021, 10:30   #12
Registered User

Join Date: Oct 2014
Posts: 7,458
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by Tmacmi View Post
I'm having all new cables made that's part of why I'm asking. The length is about 4'
The "length" of a circuit is its complete pathway from the positive power source and back to the negative of the power supply.

Do not calculate your gauge size based on just the length from the source to the load, or to a component within the circuit, e.g., to a common bus.

One needs to calculate the resistance and voltage drop across the entirety of the electrical circuit and each component thereof needs to have adequacy of ampacity.

THINK CIRCUIT, not partials of circuits.
Montanan is offline   Reply With Quote
Old 11-02-2021, 11:47   #13
Registered User

Join Date: Mar 2020
Posts: 35
Re: Linking just the negatives of two batteries in series

I see a number of circuits coming from those batteries that don't have a fuse at the battery. Bad idea. Plus neither battery seems to have a battery tie-down strap. Again, bad idea.

To answer your question you can connect both negatives together at the batteries and run one ground to the engine if thats where your common ground is located. It isn't parallel or series. Just a common connection.
RigBig is offline   Reply With Quote
Old 11-02-2021, 12:14   #14
Registered User
 
19thol's Avatar

Join Date: Feb 2016
Location: St.Pete Fl
Boat: Hunter 30 G
Posts: 80
Re: Linking just the negatives of two batteries in series

Geez, everyone is getting their panties in a bunch over your picture of batteries, good thing they can't see mine!! There would be a rush on the emergency room.
__________________
Tom G
19thol is offline   Reply With Quote
Old 11-02-2021, 17:54   #15
Registered User
 
Spot's Avatar

Join Date: Jan 2019
Location: Minnesota, USA
Boat: 21' trailer sailor & 8' sailing dinghy
Posts: 1,747
Re: Linking just the negatives of two batteries in series

Quote:
Originally Posted by RigBig View Post
I see a number of circuits coming from those batteries that don't have a fuse at the battery. Bad idea. Plus neither battery seems to have a battery tie-down strap. Again, bad idea.

To answer your question you can connect both negatives together at the batteries and run one ground to the engine if thats where your common ground is located. It isn't parallel or series. Just a common connection.

Not series, not parallel, common connection for ground
Attached Thumbnails
Click image for larger version

Name:	series_parallel_not.png
Views:	92
Size:	16.6 KB
ID:	232328  
__________________
Big dreams, small boats...
Spot is offline   Reply With Quote
Reply

Tags
batteries


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
any negatives on depth sounders Surrymark Monohull Sailboats 2 29-12-2014 16:34
Can I still get 12V from two 12V batteries in series Mikado Electrical: Batteries, Generators & Solar 26 29-10-2014 18:48
Series linking blue reliance water jugs for water tank Ketchgould Plumbing Systems and Fixtures 3 27-02-2013 07:54
Negatives of using stainless screws. Alan Wheeler Construction, Maintenance & Refit 4 17-04-2005 23:22

Advertise Here


All times are GMT -7. The time now is 03:42.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.