Presuming you do have good float settings available the water should be ok, ( temp compensated around 13v, "Should" ,,,, But I would check sg & levels every few months if possible)
I look after a few off grid solar systems using FLA's, As the Island I live on is seasonal & a lot of the properties are empty for 6 months in
winter I have a similar problems, Some have float capability (panels) some do not,
My " best winter practice" is similar to a float battery (big UPS, telecoms backup, etc), In a float battery it would be every 6 months (EQ approx every 100 cycles in off grid), In our case end of season,
Charge batteries fully until SG's stop rising at normal voltage, EQ batteries untill SG's stop rising, (top up water half hour before end to correct levels, half hour before gives it time to mix) check and spray grease all connections, If you have float, turn it on, If not disconnect all connections to them, Keep in mind that batteries will freeze if you store them in cold climates (lower charged, more easily) If you can, Check them every few months, SG's & water,
Start of season, remove, clean, grease all connections & reassemble,check water, Do not top right up now, it will expand during charge and make a mess, If you have had decent float, The SOC/SG's should still be high, If no float, recharge at normal voltage to full,
Next bit, difficult to give numbers but the idea is to drain the batteries down to %50 SOC with a C/5 load, (make them
work hard) The purpose being to combat sulphation which occurs when batteries stand idle or are under used, Crystals block pores, Good hard discharge / recharge clears them, Deep cycle batteries,,, well the clue is in the name, They NEED to be deep cycled occasionally, Drain batteries to around 50% / 1.200sg, (I use
electric heaters) allow to rest depending on temp, Recharge at normal voltage & EQ, The final EQ as well as combating Sulphation sorts out the stratification that has happened in
storage (heavy "acid" sinks to bottom)
Tim