Inverter / Charger Not Charging Off the Genset

I installed a Freedom SW 2000 Inverter charger. I am aware of problems with customer service, but it was a budget decision when my old charger died unexpectedly. Works great on shore power, charges, inverts and allows current pass through. On the generator, it doesn't work. It doesn't charge, and it won't allow current to pass through. It will still invert. The display reads 000, and the charge light does't go on. I have 108 V at the breaker, and all other electric works. The manual has a range of 85v to 140v for the charger to work. The outlets are isolated at the panel, and are the only items connected to the inverter. The generator will run a hotwater heater and AC. It is as if the inverter isn't sensing the current from the generator.
keepondancin is offline   Reply With Quote
Old 27-06-2010, 09:08   #2
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
What kind of generator? If it's a small 2-pole one, like my NextGen 3.5KW, it may put out "dirty power" until it has a resistive load on it.

Mine is so bad that the Victron MultiPlus inverter/charger behaves the same as your Freedom 2000, i.e., it won't either pass AC or charge until I put enough resistive load on the generator to smooth out its output.

I posted some oscilloscope pix of this a few months back...not sure where.

Bill
btrayfors is offline   Reply With Quote
Old 27-06-2010, 09:31   #3
Registered User

Join Date: Nov 2005
Location: 5 Mile River
Boat: Bristol 41.1 Keep on Dancin'
Posts: 838
Generator is an older Westerbeke 4kw, nothing fancy, just an older one.
keepondancin is offline   Reply With Quote
Old 27-06-2010, 10:14   #4
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Will the Freedom charger work when the hot water heater is on?
btrayfors is offline   Reply With Quote
Old 27-06-2010, 10:22   #5
Registered User

Join Date: Nov 2005
Location: 5 Mile River
Boat: Bristol 41.1 Keep on Dancin'
Posts: 838
No. The h2o heater is seperated so it isn't through the inverter, but the heater and the AC work on the genset. The inverter won't charge or allow 110 to pass through to the outlets. Everything is good on shore power, and there is a selector switch to go between shore power and genset.
keepondancin is offline   Reply With Quote
Old 27-06-2010, 12:44   #6
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
OK. Presumably, the heater or AC would put enough load on the generator to clean up it's output so the Freedom would be happy.

Soooo....hard to diagnose from a distance, but maybe the genset's frequency regulation is off enough so the Freedom doesn't like it? If you could put a frequency meter on its output and, perhaps, an oscilloscope as well, that might give some clues as to what's wrong.

Beyond that, I'd say you need to find a good marine electrician.

Bill
btrayfors is offline   Reply With Quote
Old 27-06-2010, 13:04   #7
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,534
Bill is correct about ensuring qualified power is available; however, there is an old Xantrex Technical Note attached that will show that your genset is too small. You may be able to reduce the power sharing function so that only 10 or 15 amps of incoming power is available for charging but I do not hold out much hope.

Inverter-Charger Genset Sizing.pdf

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 27-06-2010, 13:13   #8
Registered User
 
amarinesurveyor's Avatar

Join Date: Jan 2008
Location: Jupiter, FL
Posts: 169
If the inverter is wired for pass thru operation on shore, the shore power usually goes to the inverter before it goes to the electrical panel, in which case when you select power supply from the gererator, the inverter is not getting any power. I would first check the path of the shore power from the inlet and see where it goes first. If it goes to the inverter first, that is your problem. The shore power should first go to the power selector switch, then to the inverter, and then to the panel, so that whether you have power from shore or from the generator, it passes through the inverter and allows it to charge.
Hope this helps,
Brian
amarinesurveyor is online now   Reply With Quote
Old 27-06-2010, 15:45   #9
Registered User
 
Blue Stocking's Avatar

Join Date: Dec 2008
Location: St. Georges, Bda
Boat: Rhodes Reliant 41ft
Posts: 4,131
Exactly Brian,

That reference to the selector switch type in post 5 got me scratching my head.
__________________
so many projects--so little time !!
Blue Stocking is offline   Reply With Quote
Old 27-06-2010, 16:00   #10
Registered User

Join Date: Nov 2005
Location: 5 Mile River
Boat: Bristol 41.1 Keep on Dancin'
Posts: 838
The selecter switch is a mechanical switch, by Westerbeke that has Shore Power, Off, Ship's Gen. Everything works properly on shore power. Prior to the installation of the SW2000, all appliances (calling a recepticle an appliance) worked with both sources. I split off the recepticles from the panel so as to not be able to attempt to run AC or heater through the inverter, also, so that the inverter was being back fed. There is a 30 amp breaker for the inverter, which works as the power to the inverter. That is on the original panel.

I believe that there is automatic power sharing, so that the charger would run at a lower output, with less amperage. Even if there isn't, the power should pass through the inverter to power the recepticle when on the Gen. setting on the selecter switch.

I won't be back to the boat until next weekend, and at that time I will do a physical trace of the wiring from both the shore power input recepticle, and trace the wiring from the genset, to see if somehow the neutral isn't connected.

I do have 108v at the breaker when the gen is running. I haven't tested it at the inverter, but am confident that it is to the inverter, because it is when shore power is on. Same breaker and cabling.
keepondancin is offline   Reply With Quote
Old 03-07-2010, 06:19   #11
Registered User

Join Date: Nov 2005
Location: 5 Mile River
Boat: Bristol 41.1 Keep on Dancin'
Posts: 838
Checked the output of the generator and the frequency is off the charts, about 210hz. shore power checks out at 60hz as it should be, so it is not my meter. That's the problem why the inverter rejects the power source. What can cause this to be so far off? Would that be the Bridge Rectifier? Can't call customer service til tuesday, but looking for input.
keepondancin is offline   Reply With Quote
Old 03-07-2010, 06:41   #12
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,337
Images: 241
Generally, frequency is a direct result of generator speed. When the generator is driven at 1800 RPM, the AC output frequency is 60 Hz. Run at 1500 RPM the gen puts out 50 Hz.

Westerbeke Generator Manuals
westerbeke, marine generators, engines, Official Site
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 03-07-2010, 06:45   #13
Registered User

Join Date: Nov 2005
Location: 5 Mile River
Boat: Bristol 41.1 Keep on Dancin'
Posts: 838
Going to borrow a tach and check engine speed, but the voltage output is about 109 to 112, and that is speed related also. It is inconsistant that voltage is low and frequency is high.
keepondancin is offline   Reply With Quote
Old 03-07-2010, 07:08   #14
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Quote:
Originally Posted by keepondancin View Post
Checked the output of the generator and the frequency is off the charts, about 210hz. shore power checks out at 60hz as it should be, so it is not my meter. That's the problem why the inverter rejects the power source. What can cause this to be so far off? Would that be the Bridge Rectifier? Can't call customer service til tuesday, but looking for input.
If the power output is dirty (common), you won't get a true frequency measurement with a typical multimeter. If a non-resistive load is applied while measuring (battery charger?), this will make the readings look high.

Apply a resistive load like a water heater and see if the frequency returns to normal. Also make sure all other loads are off.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 03-07-2010, 07:39   #15
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
I agree with Mark. Small 2-pole generators -- which often at 3600RPM -- are prone to dirty power output when they're not loaded.

As Mark said, put a resistive load on it and see what you get.

My NextGen 3.5KW went from 86.4 Hz with no load (measured on a digital storage oscilloscope) to 63.7 Hz with a 20A load. Still a bit high...I need to adjust it...but MUCH better.

By the way, the NextGen uses a belt system and runs at 2800RPM.

Bill
btrayfors is offline   Reply With Quote
Reply

Tags
inverter

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Genset / Alternator / Inverter / Charger Questions bobox Electrical: Batteries, Generators & Solar 15 02-08-2010 05:32
Inverter / Charger vs Seperates bobfnbw Electrical: Batteries, Generators & Solar 12 14-10-2009 22:41
Inverter / Charger keepondancin Electrical: Batteries, Generators & Solar 10 16-06-2009 09:40
Freedom 10 Inverter / Charger gulfstar1 Electrical: Batteries, Generators & Solar 6 14-05-2009 18:41
inverter/charger consprenger Electrical: Batteries, Generators & Solar 0 15-02-2008 05:17

Advertise Here


All times are GMT -7. The time now is 05:54.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.