Old 08-12-2022, 10:28   #31
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by flee27 View Post
Following what you are saying about not creating an earth ground because of no grounding plate. Is is correct to say that one could not have metal through hulls or other under water metal bonded like my boat has. This basically creates an earth ground? Correct?



Thanks for lessons.



Foster


Yes in an isolating install it makes no sense to ground anything to “ earth” ax it exposes a shock risk.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 08-12-2022, 10:31   #32
Registered User

Join Date: Oct 2016
Location: Monroe, Ga
Boat: 1987 Sabre 42 C/B
Posts: 388
Images: 1
Re: How to wire and test an isolation transformer

Thanks for the answer. And the purpose in bonding metal through hulls is so you don't end up with uneven potential paths to ground?

Foster
flee27 is offline   Reply With Quote
Old 08-12-2022, 10:40   #33
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by flee27 View Post
Thanks for the answer. And the purpose in bonding metal through hulls is so you don't end up with uneven potential paths to ground?



Foster


How can that happen if ground is not a fault path
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 08-12-2022, 15:30   #34
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,961
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by goboatingnow View Post
Fault in an appliance does not pose a shock risk with an isolate. Supply. Postulating two simultaneous fault is rather “ reaching “ and RCBOs protraction will cover thst anyway
I have demonstrated how you will be killed down to ashes with the RCBO behind the transformer. You need to pick it up GBN
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 08-12-2022, 15:36   #35
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,961
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by flee27 View Post
Following what you are saying about not creating an earth ground because of no grounding plate. Is is correct to say that one could not have metal through hulls or other under water metal bonded like my boat has. This basically creates an earth ground? Correct?

Thanks for lessons.

Foster
A bonding system isn’t an AC chassis ground, although some biats have them interconnected, which is imo.

Example: my masts are bonded to underwater plates, so bonded to earth. But this isn’t connected to my AC power ground…

For bronze thru hulls in a wooden or fiberglass boat, they should have no bonding and no zincs. For a bronze prop on a stainless or Monel prop shaft, it should have a zinc because there are dissimilar metals, but again, no bonding.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 08-12-2022, 20:53   #36
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by s/v Jedi View Post
A bonding system isn’t an AC chassis ground, although some biats have them interconnected, which is imo.



Example: my masts are bonded to underwater plates, so bonded to earth. But this isn’t connected to my AC power ground…



For bronze thru hulls in a wooden or fiberglass boat, they should have no bonding and no zincs. For a bronze prop on a stainless or Monel prop shaft, it should have a zinc because there are dissimilar metals, but again, no bonding.


We agree that bonding and protective earth earth are E entirely seperate
Look the analysis analysis is not complex.

In coming shower power normally is earth referenced this means a shock path biz earth and seawater exists from live at each I Europe this will be rcbo protected on the pillar it the presence of a earth fault path especially with seawater is what opens up a shock risk

But the whole point of an isolating ttansformer is to break that ground path fault psthb

All fault current must only return tbd designated neutral of tbd isolating transformer it must never be arranged to return through shower earth or seawater

Therefore on no account should thd PE of if an isolated boat have any connection to m seawater or Shore PE

To establish a boat PE establish a pe neutral bond at the isolating transformer as it’s a “ derived “source”

Nicks diagram
showing seawater ground is funfementslky wrong and unsafe add back in fault paths and exposes boat to additional fault paths.

That does Does not mean you can’t establish a local pe but it nevrrpto idea any connection to seawater and shore ground
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 09-12-2022, 01:19   #37
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,961
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by goboatingnow View Post
Nicks diagram
showing seawater ground is funfementslky wrong and unsafe add back in fault paths and exposes boat to additional fault paths.

That does Does not mean you can’t establish a local pe but it nevrrpto idea any connection to seawater and shore ground
Are you feeling okay? Why are you writing this, do you really feel it is funny to post straight lies and accusations just because you like to kill every thread I post?

None of my diagrams show seawater ground. Now go and report me again.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-12-2022, 01:28   #38
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,961
Re: How to wire and test an isolation transformer

GBN has killed this thread with his nonsense. I am done posting helpful threads with him around and will return to using other media and posting just links here on CF.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-12-2022, 03:38   #39
Registered User

Join Date: Mar 2020
Location: currently eastern Caribbean
Boat: Catalina 42
Posts: 140
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by s/v Jedi View Post

None of my diagrams show seawater ground
This statement was important for me, thank you! The label "ship's ground" in the diagram had me thinking this was the same as ship's DC ground, which on my (and many) boats includes engine block/shaft. That this is an isolated ac ground network is an important part of the puzzle. (I assume this is correct?)

I find your posts helpful. Please don't stop.

Dan
Off Trail is offline   Reply With Quote
Old 09-12-2022, 03:58   #40
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by Off Trail View Post
This statement was important for me, thank you! The label "ship's ground" in the diagram had me thinking this was the same as ship's DC ground, which on my (and many) boats includes engine block/shaft. That this is an isolated ac ground network is an important part of the puzzle. (I assume this is correct?)

I find your posts helpful. Please don't stop.

Dan


This label confused me too as I would assume this was AC ships ground and it was my point it should not be.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 09-12-2022, 05:27   #41
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,500
How to wire and test an isolation transformer

Maybe now is the right time to offer consideration to HF radio grounds and bonding and earthing for lightning grounds. We can introduce concepts of hybrid grounding and maybe even spark gap earthing. Or, maybe not 🤯
team karst is offline   Reply With Quote
Old 09-12-2022, 06:54   #42
Registered User

Join Date: Jul 2014
Location: Southeast US
Posts: 378
Re: How to wire and test an isolation transformer

This thread has been very helpful in my understanding of this topic (installation of an isolation transformer) and it appears that some posters react with statements that are based on their mis-interpretation of the diagram and/or statements based on you misunderstanding of what you read.

GBN, and others, when you think something is wrong with a diagram or statement, please ask the writer for clarification, rather than skewer the poster (Nick or whoever) with misleading, derogatory statements.

It was very clear in his diagram that the ground is in not connected to seawater; otherwise, he would have diagramed that in. That "ships ground" is simply a bus bar to direct the AC grounding conductors back to the electrical source: the isolation transformer.

Additionally, please take a few minutes to proof read your posts and remove as many typos and misspellings as you can because it is sometimes very difficult to understand when the sentences are riddled with typographical errors. This is especially problematic with voice-to-text software. For those whose first language is not English, it is even harder to interpret misspellings.

Nick, I commend you for the patience you have with those who rebut with flawed statements and your ability to clearly explain why those statements are not applicable in an isolation transformer environment, where it is the source.

Please continue to post your diagrams and offer your advice because, with the changing technology, we cannot rely on standards like NEC and ABYC to reflect best practices because they are slow to adapt.

For the rest of y'all, if you don't have anything constructive or nice to say, please refrain from saying it.
scherzoja is offline   Reply With Quote
Old 09-12-2022, 07:50   #43
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by scherzoja View Post
This thread has been very helpful in my understanding of this topic (installation of an isolation transformer) and it appears that some posters react with statements that are based on their mis-interpretation of the diagram and/or statements based on you misunderstanding of what you read.

GBN, and others, when you think something is wrong with a diagram or statement, please ask the writer for clarification, rather than skewer the poster (Nick or whoever) with misleading, derogatory statements.

It was very clear in his diagram that the ground is in not connected to seawater; otherwise, he would have diagramed that in. That "ships ground" is simply a bus bar to direct the AC grounding conductors back to the electrical source: the isolation transformer.

Additionally, please take a few minutes to proof read your posts and remove as many typos and misspellings as you can because it is sometimes very difficult to understand when the sentences are riddled with typographical errors. This is especially problematic with voice-to-text software. For those whose first language is not English, it is even harder to interpret misspellings.

Nick, I commend you for the patience you have with those who rebut with flawed statements and your ability to clearly explain why those statements are not applicable in an isolation transformer environment, where it is the source.

Please continue to post your diagrams and offer your advice because, with the changing technology, we cannot rely on standards like NEC and ABYC to reflect best practices because they are slow to adapt.

For the rest of y'all, if you don't have anything constructive or nice to say, please refrain from saying it.


The point being presenting so “ reference diagrams “ that are misleading or convey a misplaced sense of authority does not convey the complexity of the issue properly. The “this is the only solution “
“ approach doesn’t educate the reader rather hands him fish. I want to teach people to fish. Ie understand the issues trade offs and complexity not about far fetched hazard scenarios

Otherwise all you get is another thread in a week.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 10-12-2022, 09:06   #44
Registered User

Join Date: Jul 2014
Location: Southeast US
Posts: 378
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by goboatingnow View Post
The point being presenting so “ reference diagrams “ that are misleading or convey a misplaced sense of authority does not convey the complexity of the issue properly. The “this is the only solution “
“ approach doesn’t educate the reader rather hands him fish. I want to teach people to fish. Ie understand the issues trade offs and complexity not about far fetched hazard scenarios

Otherwise all you get is another thread in a week.

Well GBN,

The thread's all yours, mate. Maybe you can post your diagram and show us how to properly cast the line, or fish on another day.
scherzoja is offline   Reply With Quote
Old 10-12-2022, 09:41   #45
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: How to wire and test an isolation transformer

Quote:
Originally Posted by scherzoja View Post
Well GBN,

The thread's all yours, mate. Maybe you can post your diagram and show us how to properly cast the line, or fish on another day.


Give me a few days and I will under a separate thread
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ELCI Breaker and Isolation Transformer Questions GrowleyMonster Electrical: Batteries, Generators & Solar 11 02-11-2021 10:49
Victron Isolation Transformer and Ground Fault Issue mdsilvers Electrical: Batteries, Generators & Solar 11 22-02-2021 13:05
ELCI and Isolation Transformer gpeacock Electrical: Batteries, Generators & Solar 12 29-04-2014 09:27
ELCI and Isolation Transformer Microship Electrical: Batteries, Generators & Solar 20 19-08-2010 15:54
Isolation Transformer and SSB Sailabel Marine Electronics 3 02-04-2010 16:30

Advertise Here


All times are GMT -7. The time now is 10:15.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.