Re: ground for AC

Quote:
Originally Posted by sailabroad View Post
In the article's example, "Live Case" the RCD's will trip when the human earths the case even without the AC to DC grounding connection, or even if the marina's shore side ground is poorly maintained.

Putting a screw through the power cable and not shorting against Neutral while energizing the metal?! not plastic case - one in a million chance Darwin award.
Not quite 1 in a million but possible. When I used to PDI new boats for delivery I found screws in wiring harnesses a number of times. Luckily they were all DC.

I think the AC grounding to DC ground bond is one of those argue forever things like which anchor is best threads. I see the reason why for both ways. That said with a RCD or similar device and a a good path to ground thru shorepower, several things would have to go really wrong for the onboard safety ground to be needed.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 22-01-2018, 11:51   #17
Registered User

Join Date: Oct 2013
Location: Italy
Boat: Beneteau Oceanis
Posts: 113
Re: ground for AC

"Over current devices" are very poor at saving lives..hence the development of RCD's.

To get electrocuted we need all of the following,

(1) Careless guy/girl screws through power cable
AND (2) doesn't somehow short to neutral (over current protection triggers)
AND (3) somehow energizes the case (now most are plastic?)
AND (4) marina has poorly maintained earth (actually would need to be disconnected)
AND (5) somehow the RCD doesn't trip.

The AC - DC grounding only prevents (4) and definitely causes a lot of really shitty corrosion problems, if there's an AC fault you also run some risk of frying all your 12 volt stuff.
sailabroad is offline   Reply With Quote
Old 22-01-2018, 12:23   #18
Senior Cruiser
 
BlackHeron's Avatar

Join Date: Jan 2016
Boat: Bathtub
Posts: 889
Images: 19
Re: ground for AC

Quote:
Originally Posted by sailabroad View Post
"Over current devices" are very poor at saving lives..hence the development of RCD's.

To get electrocuted we need all of the following,

(1) Careless guy/girl screws through power cable
AND (2) doesn't somehow short to neutral (over current protection triggers)
AND (3) somehow energizes the case
AND (4) marina has poorly maintained earth (actually would need to be disconnected)
AND (5) somehow the RCD doesn't trip.

The AC - DC grounding only prevents (4)
The overcurrent device is good at eliminating the source, and opening the circuit in the event of short cicuit or overcurrent conditions, but is only ONE part of the overall electrical system safety protocol. They may not do it fast enough for optimal life safety, but do a great job of protecting equipment from damage, and obviating the risk of fire to the maximum extent.

RCD is yet another layer of electrical safety but DOES NOT replace proper grounding practices.

I am also a big proponent of using an ELCI main breaker in marine AC panels as well as GFCI on branch circuits with receptacles where portable appliances of any unknown type could possibly be used. If someone has a corded electrical device and it is possible that it fits into the receptacle outlet you can damn well assume that eventually it will find its way into being plugged in at some point. You have no control over this regardless of how well you vet guests and their inspect their gear whenever they board your boat.

My own boat uses a Blue Sea Systems 30A ELCI main breaker panel, plus the GP receptacle circuit is protected by a GFCI outlet which is first in line and mounted right below the panel at the Nav station. I only have 2 AC circuits on the whole boat: GP receptacles and battery charger. The battery charger is not on a GFCI outlet but is protected still by the ELCI. the only receptacle for it is a single dedicated box inside the battery compartment for the charger to plug into.

BlackHeron is offline   Reply With Quote
Old 22-01-2018, 12:55   #19
Registered User

Join Date: Oct 2013
Location: Italy
Boat: Beneteau Oceanis
Posts: 113
Re: ground for AC

Hmm, Actually

(4) would have to be 'Marina has poorly maintained earth',

AND

(5) EVERY OTHER boat in the marina with a shore power connection has NO AC - DC ground connection - Currently not very likely

SO if you disconnect your AC - DC ground aboard, and you have an AC fault your neighboring boat might also ground your AC fault, triggering Over-Current-Protection &/OR your RDC
sailabroad is offline   Reply With Quote
Old 22-01-2018, 16:21   #20
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: ground for AC

Quote:
Originally Posted by sailabroad View Post
Hmm, Actually

(4) would have to be 'Marina has poorly maintained earth',

AND

(5) EVERY OTHER boat in the marina with a shore power connection has NO AC - DC ground connection - Currently not very likely

SO if you disconnect your AC - DC ground aboard, and you have an AC fault your neighboring boat might also ground your AC fault, triggering Over-Current-Protection &/OR your RDC
you're not going to get 15a flowing through the water, enough to trip the breaker.
that is why they made the ELCI. so only 30ma has to flow into the water.
smac999 is offline   Reply With Quote
Old 23-01-2018, 06:00   #21
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 361
Re: ground for AC

Thinking of all the electric related deaths in fresh water marinas being in the news, should we trust any marina's ground path?
Zil is offline   Reply With Quote
Old 29-01-2018, 14:36   #22
Registered User

Join Date: Oct 2013
Location: Italy
Boat: Beneteau Oceanis
Posts: 113
Re: ground for AC

smac999

"&/OR your RDC"

RCD = ELCI
sailabroad is offline   Reply With Quote
Old 30-01-2018, 17:42   #23
Senior Cruiser
 
BlackHeron's Avatar

Join Date: Jan 2016
Boat: Bathtub
Posts: 889
Images: 19
Re: ground for AC

Quote:
Originally Posted by sailabroad View Post
smac999

"&/OR your RDC"

RCD = ELCI
ELCI is a type of RCD. They are not equivalent and shouln't be used interchagibly.

You can't say RCD =ELCI any more than you can say RCD = GFCI -or GFCI= ELCI for that matter.

A lemon is a kind of citrus fruit, and so is a grapefruit. But you can't say that citrus = lemon.
BlackHeron is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Negative Ground vs Positive Ground History Question. Wotname Electrical: Batteries, Generators & Solar 23 26-04-2021 04:22
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
A Simple RF Ground Test GordMay Marine Electronics 15 21-06-2009 07:08
ssb ground davemaskell Marine Electronics 17 02-12-2005 18:47
External Ground Plate Kai Nui Electrical: Batteries, Generators & Solar 2 09-10-2005 02:14

Advertise Here


All times are GMT -7. The time now is 01:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.