We have a Phasor Marine LP2-6kw diesel generator that has blown 3 AVR voltage regulators over the past year. The output is regulated by a potted regulator, and does not use a capacitor (although a capacitor is part of the internal regulator circuit of course, but it isn't a high-voltage capacitor type regulator). A picture of the regulator is attached.

A new regulator will work just fine for 1-4 months and then start to go - resulting in a high voltage from the generator at random times until it stops regulating completely a few days later and the voltage stays at the high unregulated level.

The brushes are good, the commutator is clean and shiny and the windings look fine to me. I have ducted in forced cool air to the front of the generator head and have another ducted fan sucking hot air from the back of it. The head stays cool, so heat is not the problem.

The Kubota engine runs fine.

Does anyone have any ideas on why it is blowing regulators so often? The original regulator lasted 7 years, the second 10 months and the third 2 months.

Mark
Attached Thumbnails
Click image for larger version

Name:	AVR.jpg
Views:	234
Size:	21.4 KB
ID:	13445  
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 23-02-2010, 08:50   #2
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
One possibility is a heat problem. These potted AVR's don't like excessive heat. Mine (on a NextGen 3.5KW) blew after a year or so and a very hot summer.

Genset temps often go way up after you shut down. One thing you might do: try to cool the generator a bit before shutting down, by taking all loads off it. Let it run a few minutes like that. Also, do you have an exhaust blower on the genset? Is there a way to keep the blower going after the genset shuts off? Do you have an enclosure? These can really raise the heat level.

Good luck.

Bill
btrayfors is offline   Reply With Quote
Old 23-02-2010, 11:40   #3
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
My original thought was heat, so I installed two blowers - one bringing cool outside air into the front of the generator head and the other removing air to the outside from the rear of the head (this is the normal flow of cooling air through the head). This still resulted in a loss of the AVR. I always let the generator run a few minutes after removing loads. There is no enclosure, although the generator is in a dedicated ventilated locker (that is much larger than the generator itself. After shutting down and waiting a bit, the locker temperature is almost ambient.

I don't think the temps are a problem, and the first AVR lasted 7 years without the additional cooling blowers.

Any other thoughts? I've exhausted all of mine.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 23-02-2010, 12:29   #4
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Mark,

Seems you've done everything a reasonable man could. Now, I think I'd call Phasor and bug them until this gets resolved. They MUST have run across this before.

It's probably a good thing to start with the sales staff rather than tech support...more responsive. Then, move on to the real techies and find out what's going on.

Their contact in FL:

2090 SW 71 Terr. H-4
Davie,
Florida 33317
Sales: 954-684-4801


Bill
btrayfors is offline   Reply With Quote
Old 24-02-2010, 20:30   #5
Registered User

Join Date: Oct 2009
Location: Paraty - Brazil
Boat: OC43 - Nave Rara
Posts: 10
Might it be the AVR is assisted by some sort of mechanical governor ? To maintain rpms within a range where AVR is capable to actuate. I've seem some mechanical governors that lost spring resistance, thus fluctuating voltage and frequency, regardless AVRs. Have you noticed any rpm fluctuation ? Good luck.
negrini is offline   Reply With Quote
Old 24-02-2010, 23:10   #6
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,862
My Northern lights is brushless except for that one brush... check if you have one too!

Also, let an electronics geek check it out to see what broke. From the picture it should be easy to find it and to repair it!!

Edit: I mean when you know what broke, you have a clue what can be wrong.

cheers,
Nick.
s/v Jedi is online now   Reply With Quote
Old 25-02-2010, 08:07   #7
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Negrini: Yes, the engine speed is held constant by a solenoid controlled by a governor. I have not noticed any speed fluctuations, but can check it out further.

Nick: The generator head uses brushes. The brushes and commutator are good. I agree that it should be easy to fix the AVR, but what isn't apparent in the picture is that the whole thing is potted in epoxy except the trim pot and the top of the capacitor. This makes it quite a bit more difficult to fix.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 25-02-2010, 10:26   #8
Registered User
 
Zephyr's Aura's Avatar

Join Date: Jun 2008
Location: North Carolina, USA
Boat: Dufour Arpege 30
Posts: 93
Do you have a battery charger, solar panel, and or wind generator? I ran into a similar problem where my charging system would fry the voltage regulator. I had to make sure that the start battery was only charged by the engine. That cured the problem for me.

Tim
__________________
* _/)_
~~~~~~~
If you really want to do something you’ll find a way. If you’re not so sure you’ll find excuses.
Zephyr's Aura is offline   Reply With Quote
Old 25-02-2010, 11:18   #9
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Quote:
Originally Posted by Zephyr's Aura View Post
Do you have a battery charger, solar panel, and or wind generator? I ran into a similar problem where my charging system would fry the voltage regulator. I had to make sure that the start battery was only charged by the engine. That cured the problem for me.

Tim
Tim,

Could you explain further? That makes no sense to me at all, since unless the generator is actually running and connected to the AC circuit (via a proper transfer switch), there should be NO voltage on the AVR at all. Are you talking about an AVR to regulate 120VAC??

Thanks,

Bill
btrayfors is offline   Reply With Quote
Old 25-02-2010, 11:26   #10
Registered User
 
tallyhorob's Avatar

Join Date: Jan 2010
Location: Belleville, MI
Boat: Catalina 27 - Handyman NO# 1229771
Posts: 209
Send a message via MSN to tallyhorob
just to confim the heat idea get a laser temp probe from Home depot they are like 20- 30 dollars now. Test temp hitting the AVR direct and beside the temp probe comes in really handy for other stuff too.
tallyhorob is offline   Reply With Quote
Old 25-02-2010, 11:42   #11
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,862
With all those fans and the first 7 years without trouble I don't think it's heat. I think it's time to get a geek with a scope and check out the wave forms coming from the windings and on every wire connected to the AVR.

AVR repair: ah, I couldn't see it was potted on the photo.

cheers,
Nick.
s/v Jedi is online now   Reply With Quote
Old 25-02-2010, 13:38   #12
Registered User

Join Date: Feb 2009
Posts: 1,315
do you idle your generator.
chala is offline   Reply With Quote
Old 25-02-2010, 14:02   #13
Registered User
 
Zephyr's Aura's Avatar

Join Date: Jun 2008
Location: North Carolina, USA
Boat: Dufour Arpege 30
Posts: 93
My mistake...

Quote:
Originally Posted by btrayfors View Post
Tim,

Could you explain further? That makes no sense to me at all, since unless the generator is actually running and connected to the AC circuit (via a proper transfer switch), there should be NO voltage on the AVR at all. Are you talking about an AVR to regulate 120VAC??

Thanks,

Bill
Sorry Bill I guess I had a case of cranialrectumitis for a minute. I thought you were talking about the 12 volt alternator. That's what I get for scanning the text instead of reading it fully.
__________________
* _/)_
~~~~~~~
If you really want to do something you’ll find a way. If you’re not so sure you’ll find excuses.
Zephyr's Aura is offline   Reply With Quote
Old 25-02-2010, 14:42   #14
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Quote:
Originally Posted by Zephyr's Aura View Post
Sorry Bill I guess I had a case of cranialrectumitis for a minute. I thought you were talking about the 12 volt alternator. That's what I get for scanning the text instead of reading it fully.
Hey, no problem. Just wanted to be sure I wasn't missing something :-)

Re: the cranialrectumitis, it's a pretty common affliction amongst sailors. Sometimes I only have a few functioning neurons myself, and some of those connected by spirochetes!

Cheers,

Bill
btrayfors is offline   Reply With Quote
Old 25-02-2010, 15:40   #15
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Quote:
Originally Posted by btrayfors View Post
Sometimes I only have a few functioning neurons myself, and some of those connected by spirochetes!
Lyme disease can be a bitch..

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Reply

Tags
generator

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Battery-Charging Regulator Problem ? MasterVolt Problem ? RJV Electrical: Batteries, Generators & Solar 18 06-11-2011 22:53
Honda Generator / Xantrax Charger Problem TOM Electrical: Batteries, Generators & Solar 8 21-02-2010 05:48
Generator or A/C problem? avazquez Electrical: Batteries, Generators & Solar 5 05-01-2010 17:48
Problem with Westerbeke 3.8KW Generator Mike Sibley Electrical: Batteries, Generators & Solar 6 14-01-2009 04:37
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06

Advertise Here


All times are GMT -7. The time now is 13:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.