Re: Distance from inlet to main breaker

Quote:
Originally Posted by ramblinrod View Post
Actually, your modification is not safe.

As found, the ELCI protected all downstream AC circuits from the inverter/charger or shore power produced AC current from possible ground fault.

By moving the ELCI between the shore power inlet and inverter charger, any AC produced by the inverter is not ELCI protected.

I recommend you return the ELCI location to between the inverter charger and AC distribution panel.
generally the inverter is only in half of the AC system. split between inverter and non inverter loads. so then only half the boat would be elci...

do you have an ELCI and an isolation transformer on your gen output? of course not. it's not needed for ship produced power. there is nowhere for the power to leak too. it has to go back to the source which is your boat.
smac999 is offline   Reply With Quote
Old 11-02-2017, 04:26   #17
Registered User

Join Date: Dec 2014
Location: the Med
Boat: Nauta 54' by Scott Kaufman/S&S - 1989
Posts: 1,180
Images: 3
Re: Distance from inlet to main breaker

Easy go
I have a portable electric panel, with breaker, placed between AC inlet and shore power.

It allows me for 3 european sockets, 32A, 16A, schuco (7A)
TheThunderbird is offline   Reply With Quote
Old 11-02-2017, 05:01   #18
Registered User

Join Date: Dec 2012
Boat: Jeanneau SO45.2
Posts: 384
Re: Distance from inlet to main breaker

Quote:
Originally Posted by ramblinrod View Post
Actually, your modification is not safe.



As found, the ELCI protected all downstream AC circuits from the inverter/charger or shore power produced AC current from possible ground fault.



By moving the ELCI between the shore power inlet and inverter charger, any AC produced by the inverter is not ELCI protected.



I recommend you return the ELCI location to between the inverter charger and AC distribution panel.


As smac wrote, inverter power does not present the same risk of ground leakage that shore power does. Also, all our AC outlets are GFCIs which are more sensitive than an ELCI. The only non-outlet AC load we have is... the water heater, which we never run on the inverter.

My ELCI is staying next to the shore inlet.

I may in fact add a second ELCI because I'd like an AC inlet at the bow in the anchor well, because I'm getting tired of always using two 50' 30A shore power cable to reach the shore outlet when we dock bow-in. "Doing this right" will need an ELCI at the inlet, then a run of #30 all the way aft to a transfer switch/breaker before the charger.

It would be a lot simpler (and cheaper) to blow off the 10' rule, but I am not cutting that corner.

Payback... never, but I think of this every time I uncoil or stow the second cord.
Redline452 is offline   Reply With Quote
Old 11-02-2017, 05:54   #19
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Distance from inlet to main breaker

This is probably more of a terminology issue but the main breaker serves two main purposes (setting aside any GFI/ ELCI operation).

(1) protection of the main circuit against overloads. In this consideration the breaker can be anywhere upstream of the load (typically main panel). It will function just a well at the shore power connector or at the main panel.

(2) protection against short circuit/ ground faults. Now we want the breaker as close as possible to the shore power inlet. If the cable between the SP inlet and the main panel develops a short circuit then it will only be protected downstream of the breaker. As a practical matter if you are plugged into a properly functioning shore power system the pedestal breaker will also clear the fault condition.

Don't think I would let the length of the cable between the shore power inlet and the MB keep me up at night as much as the condition of the cable.

The GFI/ AFCI functions are also not compromised by locating the main breaker at the panel end.
Frankly is offline   Reply With Quote
Old 11-02-2017, 06:53   #20
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Distance from inlet to main breaker

Quote:
Originally Posted by Redline452 View Post
As smac wrote, inverter power does not present the same risk of ground leakage that shore power does. Also, all our AC outlets are GFCIs which are more sensitive than an ELCI. The only non-outlet AC load we have is... the water heater, which we never run on the inverter.

My ELCI is staying next to the shore inlet.

I may in fact add a second ELCI because I'd like an AC inlet at the bow in the anchor well, because I'm getting tired of always using two 50' 30A shore power cable to reach the shore outlet when we dock bow-in. "Doing this right" will need an ELCI at the inlet, then a run of #30 all the way aft to a transfer switch/breaker before the charger.

It would be a lot simpler (and cheaper) to blow off the 10' rule, but I am not cutting that corner.

Payback... never, but I think of this every time I uncoil or stow the second cord.
Incorrect. A properly installed marine inverter / charger is connected to the vessel AC grounding system. The only difference is that when connected to shore power, the grounding system is tied to earth at the distribution panel. When shore power is disconnected the grounding reference is to the source grounding (inverter, generator, etc.) If the ELCI is installed correctly, it
Will trip a ground fault from inverter or generator (as well as shore power
When connected) Above does not pertain to a non Marine floating inverter.
ramblinrod is offline   Reply With Quote
Old 11-02-2017, 09:17   #21
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Distance from inlet to main breaker

ABYC E 11.11.1

An ELCI shall be installed with or in addition to the main shore power disconnect circuit breaker(s) or at the additional overcurrent protection as required by E 11. 10.2 8.3 whichever is closer to the shore power connection.
mitiempo is offline   Reply With Quote
Old 11-02-2017, 14:57   #22
Registered User
 
Rowglide's Avatar

Join Date: Jan 2017
Location: Kingston, Ontario
Boat: Hans Christian 43
Posts: 382
Re: Distance from inlet to main breaker

Quote:
Originally Posted by mitiempo View Post
ABYC E 11.11.1

An ELCI shall be installed with or in addition to the main shore power disconnect circuit breaker(s) or at the additional overcurrent protection as required by E 11. 10.2 8.3 whichever is closer to the shore power connection.
So to be clear... Shore power inlet - ground isolator - less than 10' wire - circuit breaker - more wire - ELCI/circuit breaker at panel.
Rowglide is offline   Reply With Quote
Old 11-02-2017, 17:25   #23
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Distance from inlet to main breaker

Quote:
Originally Posted by Rowglide View Post
So to be clear... Shore power inlet - ground isolator - less than 10' wire - circuit breaker - more wire - ELCI/circuit breaker at panel.
Correct! And if there is another AC source (such as an inverter or generator) the switching mechanism (that may be an inverter internal transfer switch) has to be before the ELCI, or the downstream circuits are not protected by the ELCI.
ramblinrod is offline   Reply With Quote
Old 12-02-2017, 01:09   #24
Registered User

Join Date: Dec 2014
Location: the Med
Boat: Nauta 54' by Scott Kaufman/S&S - 1989
Posts: 1,180
Images: 3
Re: Distance from inlet to main breaker

Let me resort to your professional advice, please.

I took the ground line off, cause of repeated breakings when on shore power (rarely so, l depend on genny) even without any drawing of current.

Also l noticed that l had continuity in most (8 out of 12) of 220V sockets onboard, between the blue wire (Line) and ground (yellow/green), and l cut it off either.

I increased an existing copper plate in transom, but l don't know YET whether it works for AC/DC or both.....

Now, shore power is thru 2 main breakers, one before -magnetothermic-, another after -differential- the Marinco inlet.

After the deviator (SP/genny) on panel, l have another main switch 40A going back to Panel (where l am ordering new breakers from oem Heinemann for 220AC) and to 4 other DIN BREAKERS behind.

KITCHEN bypasses that main switch, as it has its own 30A DIN breaker.
The electric panel is grounded (yellow/green) but its 220VAC breakers have 2 poles only :-) . Does it make sense??

Note:
Boilers are safely away, operated from panel switch.
Grill oven was professionally inspected 2years ago....sure, we could personally inspect insulation again...
My cooking hob is an Induction plate, so it is physically insulated, like a Transformer Insulator, as the Genny is (its output is a 2-wire cord).

Any other eventual appliance should have a plastic cover...

I think and hope it is OK

Any major faults!? Or comments? Unfortunately, legacy is a major factor after 30years of different owners and multiple changes from many persons... the rear panel is hardly manageable...with 10# of wires hanging around, making even visual access difficult...
TheThunderbird is offline   Reply With Quote
Old 12-02-2017, 04:40   #25
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Distance from inlet to main breaker

Quote:
Originally Posted by ramblinrod View Post
Incorrect. A properly installed marine inverter / charger is connected to the vessel AC grounding system. The only difference is that when connected to shore power, the grounding system is tied to earth at the distribution panel. When shore power is disconnected the grounding reference is to the source grounding (inverter, generator, etc.) If the ELCI is installed correctly, it
Will trip a ground fault from inverter or generator (as well as shore power
When connected) Above does not pertain to a non Marine floating inverter.
Clairifcation - The only difference is that when connected to shore power, the grounding system is tied to earth at the shoreside distribution panel.
ramblinrod is offline   Reply With Quote
Old 12-02-2017, 04:56   #26
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Distance from inlet to main breaker

Quote:
Originally Posted by Frankly View Post
This is probably more of a terminology issue but the main breaker serves two main purposes (setting aside any GFI/ ELCI operation).
Yes, it is difficult when different terminology is used. For responses, I will do my best to use ABYC definitions.

(1) protection of the main circuit against overloads. In this consideration the breaker can be anywhere upstream of the load (typically main panel). It will function just a well at the shore power connector or at the main panel.

(2) protection against short circuit/ ground faults. Now we want the breaker as close as possible to the shore power inlet. If the cable between the SP inlet and the main panel develops a short circuit then it will only be protected downstream of the breaker. As a practical matter if you are plugged into a properly functioning shore power system the pedestal breaker will also clear the fault condition.

By ABYC standards, the "Main Breaker" protects from "over-current" (higher current than trip rating) in the downstream "ungrounded" or "grounded" AC conductor. It is configured such that "Reverse Polarity" will be indicated before the breaker is switched on, to ensure the grounded conductor (neutral in residential wiring) is the "white" conductor in the colour-coded wiring aboard.

This is so that all switches and breakers actually disconnect the ungrounded conductor (hot in residential wiring), so that downstream of the switch of breaker there can be no current.

So a fuse or breaker, rated at 15 A, will trip if ANY condition cause greater than 15 A to pass between line and neutral (and line to ground because somewhere, the two are connected).

"Ground fault protection" is only provided by either a GFCI (5 mA) or an ELCI 30 mA). This monitors the current travelling in the ungrounded (black) and grounded and (white) conductor. If there is a difference greater than the trip value, the device disconnects the protected downstream circuit. (It is assumed that the difference is because current is travelling between the ungrounded conductor (black), through a person, to the grounding (green) conductor ("ground" or "earth" in residential wiring).

The purpose is to prevent 80 mA or higher, from travelling through a person, which could potentially stop their heart (electrocute then).

So folks, if you don't know this stuff (per what ever marine electrical standard applies in your region), don't #$%%^ with it, because you could accidentally kill people on or around your boat.
ramblinrod is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage Drop From Battery To Main Breaker Panel marina.alex Electrical: Batteries, Generators & Solar 17 11-11-2021 15:16
AC Main Circuit Breaker EggHrbrGuy Electrical: Batteries, Generators & Solar 11 28-06-2015 06:12
Why does my main AC breaker keep tripping? Toubab Electrical: Batteries, Generators & Solar 19 10-10-2013 13:31
Sailing from Fire Island Inlet to Shinnecock Inlet Dswerdloff Navigation 5 10-11-2011 06:25
30A 110V Main Breaker Not Working boto Electrical: Batteries, Generators & Solar 10 19-08-2008 15:25

Advertise Here


All times are GMT -7. The time now is 07:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.