Re: DC Wiring Question - Fuse Placement

Quote:
Originally Posted by ramblinrod View Post
Commercially available marine bus bars have a max current rating.

Reference: Blue Sea

https://www.bluesea.com/products/category/18/BusBars

A properly designed and wired marine electrical distribution system will always have a feed current rated greater than the highest branch current.

ABYC E11 AC & DC Electrical Systems on Vessels, Section 11.8 identifies how to calculate the load represented by a panel board (DC distribution panel) to size the feeder wire and 11.9 for overcurrent protection.

Basically, the distribution panel and feeder wire must be capable of handling the sum of the continuous loads (irrespective of branch circuit wiring size) plus 10% of the sum of the intermittent loads (or the highest intermittent load, whichever is greater).

Only if all loads were miniscule, could the feeder wire the same size as the branch wires be valid.

Therefore, it is possible for the feeder wire to be correctly sized the same as the branch circuits, but in practice, extremely rare, and in most cases, would likely be a wiring error.

An exception that comes to mind is a 4 or 6 circuit fuse block to low power instruments from an "instrument" breaker. However, in that case, the fuse block fuses all have to be rated lower than the "instrument" breaker feeding the fuse block.

Anything else is a wiring error.

Two overcurrent protection devices of the same rating in a single series circuit, (or a load fuse larger than a branch fuse) is a wiring error.

Individual overcurrent protection devices, rated to the component they are attached, being less than the branch circuit over-protection, is valid, and should be done to prevent other parallel circuits of the branch from being disabled in the event of a single device fault.
With LEDs everywhere and increasing use of multiplex distribution it's not as uncommon as that given the 16 awg recommended min awg size.
camel2012 is offline   Reply With Quote
Reply

Tags
men, wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Starter wiring with in line fuse? Dubble D Electrical: Batteries, Generators & Solar 47 21-07-2016 22:18
Installing a 50W solar panel - fuse and wire gauge question Cthoops Electrical: Batteries, Generators & Solar 22 29-03-2016 08:27
Fuse size question janice142 Electrical: Batteries, Generators & Solar 9 18-11-2013 22:55
Fuse/breaker question for solar set-up GeoPowers Electrical: Batteries, Generators & Solar 9 20-04-2012 04:03
Fuse and circuit breaker question gulfstar1 Electrical: Batteries, Generators & Solar 15 30-03-2011 04:35

Advertise Here


All times are GMT -7. The time now is 23:30.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.