Cummins 9.5MDKBM 120 vac problem

I have this Cummins generator that generates both 120 and 240 vac. I might have overloaded the 120 vac output, but the main breaker on the generator did not trip. I can’t find any specific beaker for the 120 vac.

It still generates 240 vac just fine. Any idea if Cummins has a specific breaker for the 120 vac leg somewhere in the unit?

From the schematic, it appears that L0 is the tap that generates the 120 vac.

Praying for a simple solution….
Attached Thumbnails
Click image for larger version

Name:	IMG_0248.jpeg
Views:	42
Size:	24.3 KB
ID:	277647  
Maddox is offline   Reply With Quote
Old 04-07-2023, 03:27   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 51,629
Images: 241
Re: Cummins 9.5MDKBM 120 vac problem

Cummins/Onan “MDKB_” Marine Generator

Operator Manual ➥ https://www.cummins.fr/wp-content/up...-7-English.pdf

Service Manual ➥ https://www.seapowermarine.com/seapo...ice-Manual.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 04-07-2023, 07:11   #3
Registered User

Join Date: Sep 2014
Posts: 13
Re: Cummins 9.5MDKBM 120 vac problem

Thanks - I found the installation guide and it doesn’t discuss any breakers on the 120 vac, but at least it explains where the connections are. I will keep investigating
Maddox is offline   Reply With Quote
Old 04-07-2023, 09:31   #4
Registered User

Join Date: Apr 2022
Posts: 101
Re: Cummins 9.5MDKBM 120 vac problem

In the simplest terms your generator, like most generators in this size range do not themselves generate 240V. Instead they generate 2 different lines at 120 V (labeled L1 & L2) which are out of phase by 180º. It's commonly called split phase power. Google it. The 2 circuit breakers shown on your attachment are for these 2 lines of 120 V and are sized @ likely 40 amps to protect the wires that run to your breaker panel. The funny looking arrow thingy indicates that these 2 breakers have their levers physically connected together, which is required on all split phase lines so that if you overload one line both trip and no power is available anywhere until you reset the breaker.

These 2 lines of 120 V are brought to your breaker panel by about 8 gauge wires (likely red and black) where about half of the 120 V breakers are connected via a copper bus bar to the red wire and the other half, to the black wire.
Any appliance that requires 240 V AC (your water heater, clothes dryer, etc.) will have both the red and black connected, which then results in a 240 V supply.

The L0 line is the neutral conductor which is only require for the 120 V consumers.

If indeed you have a 240V supply to some appliance, by definition you must have 2, 120 V lines that are out of phase to produce this 240 V. This would mean both lines must be working correctly. If so, what is the problem?
Putt-Putt is offline   Reply With Quote
Old 04-07-2023, 11:23   #5
Registered User

Join Date: May 2016
Posts: 108
Re: Cummins 9.5MDKBM 120 vac problem

Have you checked the breaker on the left side of the sound box about 12” back and about 2” from top edge.
Senojev is offline   Reply With Quote
Old 05-07-2023, 06:48   #6
Registered User

Join Date: Sep 2014
Posts: 13
Re: Cummins 9.5MDKBM 120 vac problem

Thanks for the help. I finally found the external breaker box that had tripped for the 120 v line. It was under an bunk close to the generator.
Maddox is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Convert from 240 VAC to 120 VAC dpeel Electrical: Batteries, Generators & Solar 53 28-08-2018 18:31
120 vac or 12V Refridgeration lifeofreilly57 Construction, Maintenance & Refit 20 11-02-2018 08:19
Have 240 vac shore power, but only 120 vac used jr_spyder Electrical: Batteries, Generators & Solar 24 26-10-2016 04:49
For Sale: Refrigeration Components 120 VAC Achernome Classifieds Archive 0 30-05-2012 06:23
120 VAC GFCI Outlet velero Electrical: Batteries, Generators & Solar 1 11-01-2010 13:39

Advertise Here


All times are GMT -7. The time now is 04:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.