Connecting Generator Neutral to Ground Conductor

Does anybody ever wonder why a world wide, world class generator mfg like Honda has purposefully decided to not connect the neutral and ground together. Even on their newly issued EU 2200 they have continued the same practice. They make these generators and turn them loose on the public with little control on where and how. For all we know there may be one on the International Space Sation for backup power.

There are valid reasons why the "powers that be" decided on making a grounded electrical systems the norm for everyday electrical distribution, but they may not be applicable in all cases. There are lots of ungrounded and resistance grounded electrical systems in operation all over.


If you feel more comfortable operating a Honda generator with the neutral and ground tied together, then a plug is easily fabricated to make that connection. IMHO it ain't no big deal.


Frankly
Frankly is offline   Reply With Quote
Old 23-12-2019, 07:32   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Connecting Generator Neutral to Ground Conductor

I am not an electrical Engineer.
However unless I’m mistaken one or two that are have posted that not having them connected is actually safer, something having to do with how most power tools you buy now are not grounded, if you look most don’t have that third ground leg anymore.

However of course ABYC requires them to be connected and I believe only once and at the source, so to be within regulations we should connect the ground and neutral together, but only at the source, which in my opinion a plug would be.

Same for inverters, they are an AC power source to, and I believe Marine inverters have a relay so that when they are inverting then can connect the neutral and ground together in the inverter, but when they are not, they are not connected.

You have to have a relay so that you don’t have the neutral and ground bonded when on generator or shore power, as that is unsafe.

So one would assume that if you bonded the neutral and ground together, you should unplug the bonded plug when using an inverter to prevent two sources of a neutral / ground bond?
a64pilot is offline   Reply With Quote
Old 23-12-2019, 09:14   #3
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

Keep in mind my comments were on small portable inverter/generators not larger built in generators. The latter should have the neutral and ground connected and the best (and legal) place is at the unit, but them electrons don't know no ABYC or NEC.


The marine inverters/ chargers (built in transfer switches) that I have installed on my boats all have relays that lift the ground to neutral connection when in the charge mode and establish the connection in the inverter mode. Probably got more to do with lawyers than anything electrical.

Multiple ground to neutral connections are more of a book keeping issue. Usually not a safety issue, again them electrons will take the path or paths as necessary. Can be an issue with the ELCI shore power systems that are soon coming to a marina near you.

When using my EU 2000 to power the house (I have a dedicated 20 breaker standby panel), the transfer switch does not switch the neutral so my neutral to ground connection in the main service panel is still electrically in play. But it would work just fine if it was not there.

Been a while since I mucked around in the ABYC, but is there anything in there that really speaks to portable generators.


Frankly
Frankly is offline   Reply With Quote
Old 23-12-2019, 09:30   #4
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: Connecting Generator Neutral to Ground Conductor

The Honda design is 100% okay as it is...

I know people tend to point at ABYC but while those rules do create a safe system, that doesn’t mean it is the only way to a safe system... better and safer systems may exist.

When you are out at anchor and use the Honda, you can not be electrocuted when you grab ground with one hand and either the hot or the neutral from the Honda.

Remember that you need to complete a circuit and when a power source is galvanic isolated from ground, the ground can never complete a circuit
s/v Jedi is offline   Reply With Quote
Old 24-12-2019, 06:23   #5
Registered User

Community Sponsor

Join Date: Nov 2019
Location: South Carolina
Boat: Philip Rhodes Custom 71'
Posts: 192
Re: Connecting Generator Neutral to Ground Conductor

Quote:
Originally Posted by s/v Jedi View Post
The Honda design is 100% okay as it is...

<SNIP>

Remember that you need to complete a circuit and when a power source is galvanic isolated from ground, the ground can never complete a circuit
That is not correct, ABYC specifications require that the galvanic isolator be capable of carrying 130% of rated current continuously. Rather than just type testing in a lab, EVERY isolator that Yandina makes is put through the ABYC electrical tests until the temperature stabilizes, including the new 2.5 volt isolator.
__________________
Ann-Marie Foster
YANDINA is offline   Reply With Quote
Old 24-12-2019, 06:51   #6
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

Think we have a little terminology issue here.

The term "galvanically isolated " describes a condition of electrical isolation (think insulated).

A "galvanic isolator" is the device to reduce corrosion from electrical current. Originally installed in the AC ground to 12VDC negative/ engine connection, but now installed in series with the shore power AC ground connection.


Frankly
Frankly is offline   Reply With Quote
Old 24-12-2019, 07:01   #7
Registered User

Community Sponsor

Join Date: Nov 2019
Location: South Carolina
Boat: Philip Rhodes Custom 71'
Posts: 192
Re: Connecting Generator Neutral to Ground Conductor

Sorry, I can't agree. "Electrical isolation" is the equivalent of insulated = no connection between them.
When you modify the level of isolation with the word "galvanic" it now refers to an insulator limited to "galvanic" voltages.
If you want to "think insulated" you should say insulated.
__________________
Ann-Marie Foster
YANDINA is offline   Reply With Quote
Old 24-12-2019, 07:49   #8
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

I reckon we will have to agree to disagree although most current references tend to apply to ground circuit isolation but not exclusively.


Frankly
Frankly is offline   Reply With Quote
Old 24-12-2019, 07:59   #9
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: Connecting Generator Neutral to Ground Conductor

Quote:
Originally Posted by YANDINA View Post
Sorry, I can't agree. "Electrical isolation" is the equivalent of insulated = no connection between them.
When you modify the level of isolation with the word "galvanic" it now refers to an insulator limited to "galvanic" voltages.
If you want to "think insulated" you should say insulated.
Okay, “insulated” then. I used the term that engineers tend to use for this, not related to your product “galvanic isolator”. I agree that it may even be wrong and “electrically isolated” is better.

That said, it still means that the Honda is perfectly fine as it is. When it is used at anchor instead of shore power, by using the shore power inlet, crew can not be electrocuted by touching any grounded or bonded surface with one hand and either hot or neutral with the other hand.

Also, boats have no ground unless connected to shore power. Even when they use an underwater ground plate, it is at a different potential than land based ground or even an anchor in the seabed. I once measured 1.7V difference between anchor chain and ground plate.
s/v Jedi is offline   Reply With Quote
Old 24-12-2019, 08:26   #10
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,439
Images: 241
Re: Connecting Generator Neutral to Ground Conductor

Isolation simply refers to keeping two things apart. It is not a “thing”, but a concept.
It is desirable to isolate human beings from high voltages. This doesn't say how you do it, just that you must keep them apart.
On the other hand, insulation refers to some physical “thing”, that is used to keep two things apart.
So, insulation is a type of physical thing, that provides isolation.
Insulation can be plastic around a wire, or a sheet of paper/cardboard, between two windings of a transformer.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 24-12-2019, 09:07   #11
Registered User
 
jhulmer's Avatar

Join Date: Aug 2014
Location: Biloxi, MS
Boat: 1978 Cabo Rico Tiburon 36 "Isabella"
Posts: 598
Re: Connecting Generator Neutral to Ground Conductor

okay! for the dumbass country boy mechanical engineer. Should I do anything more to connect my Honda besides plugging it into the shore power receptacle that has the grounded twist-lock plug (cord cap)?

There is a ground lug on the outside of the Honda that nags at my sense of security. "should you be connected to something" I ask?
__________________
refit blog
jhulmer is offline   Reply With Quote
Old 24-12-2019, 09:16   #12
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

In the most general definition/ usage you are correct about "isolation". In the normal electrical usage "electrical isolation" is used as in isolation transformer, opto coupler isolation, isolation by insulation, and physical isolation where air is the insulating medium.


Insulation is also used for that stuff in walls to reduce heat transfer.


Electronics and electricity are advancing faster than the language can keep up, so we do the best we can.


Frankly
Frankly is offline   Reply With Quote
Old 24-12-2019, 09:32   #13
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

Forget about the external ground lug. Plug in your shore power cable, if you want to connect the neutral and ground make a dummy plug for the extra space in the receptacle. Will work and be equally safe either way.


If your really want to improve on electrical safety make a short pigtail with a plug on one end and a gfci receptacle on the other end (installed in a box). Then plug the shore power cable into the gfi receptacle and the plug into the generator. About as safe as you are going to get without getting into some complicated and expensive stuff.


Frankly
Frankly is offline   Reply With Quote
Old 24-12-2019, 09:49   #14
Registered User
 
jhulmer's Avatar

Join Date: Aug 2014
Location: Biloxi, MS
Boat: 1978 Cabo Rico Tiburon 36 "Isabella"
Posts: 598
Re: Connecting Generator Neutral to Ground Conductor

Quote:
Originally Posted by Frankly View Post
Forget about the external ground lug. Plug in your shore power cable, if you want to connect the neutral and ground make a dummy plug for the extra space in the receptacle. Will work and be equally safe either way.


If your really want to improve on electrical safety make a short pigtail with a plug on one end and a gfci receptacle on the other end (installed in a box). Then plug the shore power cable into the gfi receptacle and the plug into the generator. About as safe as you are going to get without getting into some complicated and expensive stuff.


Frankly
I understand the dummy plug would have the neutral prong and the middle ground prong connected with a jumper? What would this accomplish on a closed system of the generator besides protection inside the generator case?

My 120v AC system is not grounded to my DC ground (except through the Galvanic isolator) nor is it grounded to the Sea as this is, as I understand, the ABYC standard. So with the GFI in the Generator circuit, I would have total protection from accidental electrocution of myself, close friends, family, pets, etc?
__________________
refit blog
jhulmer is offline   Reply With Quote
Old 24-12-2019, 11:36   #15
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Connecting Generator Neutral to Ground Conductor

Don't think there is any requirement to directly connect the AC ground to the seawater. There is a requirement to connect the AC ground to the engine block/ 12 Volt negative and as such will typically electrically connect the AC ground to seawater (via prop shaft/ propeller). Connecting these two grounds together electrically safer but can cause corrosion issues. This is where galvanic isolators come into the picture. Earlier times the GI was installed in this connection between the AC ground and 12 Volt ground (typically called zinc savers), more recently the GI is installed in series with the shore power AC ground on the boat (typically called galvanic isolators).


GFCI (receptacle or breaker) technology will protect you and family from shock produced by contact between the hot leg (typically black color ) and ground (the more typical electrical failure scenario ). Contact the hot leg and the neutral conductor (white or grey color) simultaneously you will receive a significant shock. Body resistance and prayer is all you got going for you then.


Generator neutral to ground connection is typically made at only one location and the special plug will fill this obligation if you feel so inclined.


Frankly
Frankly is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Negative Ground vs Positive Ground History Question. Wotname Electrical: Batteries, Generators & Solar 23 26-04-2021 04:22
Question to battery experts, connecting ground of AGM and LiFePo4 LilleVenn Electrical: Batteries, Generators & Solar 13 15-12-2019 10:54
9 V difference between ground and ground Arrandir Electrical: Batteries, Generators & Solar 12 19-07-2018 22:51
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
Coax in Place of Single-Conductor Wire ? yzlian Marine Electronics 10 16-03-2011 12:00

Advertise Here


All times are GMT -7. The time now is 14:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.