Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 05-11-2013, 08:20   #1
Registered User
 
jimrosbe's Avatar

Join Date: May 2009
Location: Indian Point, Nova Scotia
Boat: Gouwerok Motorsailer 12m
Posts: 8
charger failure - excess incoming voltage

Problem: When connected to shore, excess incoming voltage causes charger failure

I have a steel Dutch-built motorsailer built in 1990, that I bought in 2011. From May to September, when connected to shore power, we never noticed any problems. Last month I connected my boat to shore power in Norway, and my Mastervolt 24/40-3 charger (installed new six months ago) registers “FAILURE 266U” and the voltmeter on the boat’s main electrical panel is at the very top of its scale (>250v).

We measured voltage of 238v at boat end of shore cable...and taking off the cover of the charger, measure incoming voltage to the charger at 251v.

When connected to shore power, I can hear a humming sound buried somewhere in the cabinetry...and according to the boat’s wiring diagram there is an isolation transformer.

When running the boat’s Onan 6.5kw generator, the charger works fine.

Any suggestions? Is it possible that the isolation transformer is stepping up the voltage?
jimrosbe is offline   Reply With Quote
Old 05-11-2013, 08:26   #2
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,711
Re: charger failure - excess incoming voltage

There are isolation transformers with taps which can increase the voltage 10% or so--they are used where there are problems with marina voltage supplies sagging.
donradcliffe is offline   Reply With Quote
Old 05-11-2013, 15:19   #3
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,525
Re: charger failure - excess incoming voltage

+1 for Don's comment although all electrical devices operate on the general spec of acceptable voltage being +/- 10%. If the IT is fitted, and if it has taps, my guess is that the tap setting is for > 10%.

You need to dig into the cabinetry and find the nameplate data for the "hummer" before we can be much more helpful.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 05-11-2013, 22:43   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,642
Re: charger failure - excess incoming voltage

some have a switch so you can boost voltage with the flip of the switch. as needed or not needed at different marinas. may be that easy to fix. may require some rewiring.
smac999 is offline   Reply With Quote
Old 06-11-2013, 06:51   #5
Registered User
 
jimrosbe's Avatar

Join Date: May 2009
Location: Indian Point, Nova Scotia
Boat: Gouwerok Motorsailer 12m
Posts: 8
Re: charger failure - excess incoming voltage

Thanks for your comments. Unfortunately I will have to wait until returning to Norway in April to uncover the isolation transformer, but if (as I expect) it is a Victron, here is what they emailed me:

"There Is no voltage control in the transformer. its so that the transformer voltage is always (10-15 volts)higher than the input voltage. If you will put a heavy load on it the voltage will drop.
With small loads the voltage will not drop much and if your input voltage is higher than normal , then you could measure higher voltages on the output, this cannot be adjusted."

I will contact Mastervolt to see if there is an adjustment on the charger to safely accept higher voltage.
jimrosbe is offline   Reply With Quote
Old 06-11-2013, 21:34   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,642
Re: charger failure - excess incoming voltage

if possible move the boat further down the dock away from land. the voltage will be less at the ends of the dock.

if you have a meter. go measure the plugs further down the dock and see what happens first.

increasing the load of your own boat will likely not effect much. as you move down the dock, you have the loads of all the boats added.
smac999 is offline   Reply With Quote
Reply

Tags
charger

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 00:09.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.