Can I tap into a 12v battery bank from multiple points at the same time?

Hey Cruisers!

Quick basic question: can I tap into a 3 battery 12v bank at more than just one +/- point?

Another way of wording it is if I have 3 12v battery's connected in parallel, can I for example hook up my main DC panel to one battery's poles, my small AC inverter to another battery, and my solar charger/battery charger to the third battery?

If so, will this change power output? Wear on batteries? Current or capacity change? Does this change anything at all or am I just tapping into the circuit from more than one point?

Thanks!
Hank
TenaciousH is offline   Reply With Quote
Old 17-08-2015, 11:04   #2
Registered User
 
S/V Illusion's Avatar

Join Date: Oct 2007
Location: Lakewood Ranch, FLORIDA
Boat: Alden 50, Sarasota, Florida
Posts: 3,472
Re: Can I tap into a 12v battery bank from multiple points at the same time?

The best way is to connect the three to the POS of the first and the NEG to the last battery in the bank thereby ensuring a balanced draw and recharge across all three.
S/V Illusion is offline   Reply With Quote
Old 17-08-2015, 11:09   #3
Registered User

Join Date: Apr 2015
Posts: 549
Re: Can I tap into a 12v battery bank from multiple points at the same time?

As long as the batteries are side by side and connected to each other with minimum length high current wires, it won't make any difference. Electrically they are the same.
jwcolby54 is offline   Reply With Quote
Old 17-08-2015, 11:38   #4
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by jwcolby54 View Post
As long as the batteries are side by side and connected to each other with minimum length high current wires, it won't make any difference. Electrically they are the same.
Exactly. Assuming that all cables are well connected and ignoring the very small and for all practical purposes, insignificant resistance and voltage drop between the batteries, if they are in parallel then connecting to one battery positive is exactly the same as connecting to any other battery positive.

I have connected the six 6 Volt batteries in my boat the way suggested by S/V Illusion IE pos at one end of the string, neg at the other. However I have read arguments from some marine electronics guys that do know what they're doing that in the average boat this also makes little difference. Since it costs nothing and doesn't create awkward wiring for me I'll just keep doing it this way, just in case.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 17-08-2015, 11:48   #5
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by TenaciousH View Post
Hey Cruisers!

Quick basic question: can I tap into a 3 battery 12v bank at more than just one +/- point?

Another way of wording it is if I have 3 12v battery's connected in parallel, can I for example hook up my main DC panel to one battery's poles, my small AC inverter to another battery, and my solar charger/battery charger to the third battery?

If so, will this change power output? Wear on batteries? Current or capacity change? Does this change anything at all or am I just tapping into the circuit from more than one point?

Thanks!
Hank
That is not a good idea. It will make it difficult/expensive to install proper battery fuses and make it impossible to install a shunt for a battery monitor or ammeter. Make sure the paralleling wire is very fat and connect positive in one end (with a proper MRBF fuse) and negative in the other end of the bank.

Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
svlamorocha is offline   Reply With Quote
Old 17-08-2015, 12:25   #6
Registered User

Join Date: Dec 2011
Location: Buzzards Bay MA
Boat: Beneteau 423
Posts: 868
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Here is a link to a diagram showing the proper way to parallel batteries as others have described.

Battery School | Batteriesnorthwest.com | Connect Your Batteries for Optimum Efficiency

There is another link that details why this is important, even for what seems like very short and fat cables, but I'm having trouble coming up with it.
hlev00 is offline   Reply With Quote
Old 17-08-2015, 13:22   #7
Registered User

Join Date: Aug 2015
Location: Pa.
Posts: 5
Re: Can I tap into a 12v battery bank from multiple points at the same time?

svlamorocha.
New guy just guy just joined the other day.
Please allow me to ask why you would fuse the postive side of a D.C. circuit as this is after the load. Electricity comes out of the negative side of the battery. Would it not be better to fuse on the negative side before the load there by protecting it from a over current event?
Nature Boy is offline   Reply With Quote
Old 17-08-2015, 13:27   #8
Long Range Cruiser
 
MarkJ's Avatar

Join Date: Dec 2007
Location: Australian living on "Sea Life" currently in England.
Boat: Beneteau 393 "Sea Life"
Posts: 12,822
Images: 25
Re: Can I tap into a 12v battery bank from multiple points at the same time?

I use diffent poles so that the gain and draw are evened out and stuff goes in and out of the bank differently.

for example I have a freezer directly connected to the bank. It uses different poles than the main board. Same with the solar and wind, different poles.


Mark
__________________
Notes on a Circumnavigation.
OurLifeAtSea.com

Somalia Pirates and our Convoy
MarkJ is offline   Reply With Quote
Old 17-08-2015, 13:28   #9
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by hlev00 View Post
Here is a link to a diagram showing the proper way to parallel batteries as others have described.

Battery School | Batteriesnorthwest.com | Connect Your Batteries for Optimum Efficiency

There is another link that details why this is important, even for what seems like very short and fat cables, but I'm having trouble coming up with it.
Here is a different opinion on battery wiring and the benefit or not of connecting the pos and neg wires to one battery vs opposite batteries in the bank. The whole thread is here.

http://www.cruisersforum.com/forums/...el-148682.html

It is a common misconception despite being perpetuated and mis-quoted frequently.

Its not that voltage differences do or do not exist during starting, but the fact that they are small in comparison to the internal differences in battery impedance. You are going to all that trouble to save 1/10 volt during starting an
engine when in fact the inherent battery parameters are an order of magnitude larger. If they had not been in parallel and you tested each battery for voltage supplied during starting loads, their voltage would differ much more than the minor drops due to wiring layout.

Within a second after starting is completed, the batteries will all be at the same voltage due to battery to battery current so any imbalance only lasted a few seconds. Each battery contributed energy for the starting function but once completed they all are AT THE SAME VOLTAGE so each had contributed its share of the energy that it could release between the initial voltage prior to starting and the rest voltage after starting.

Eventually you took xyz amp-hours out of the battery bank to start the
engine. The net effect of wiring differences boil down to heating loss which again is insignificant. For maximum efficiency the wiring layout should minimize wiring resistance.

__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 17-08-2015, 14:45   #10
Registered User

Join Date: Aug 2010
Location: sydney, australia
Boat: 38 roberts ketch
Posts: 1,309
Images: 3
Re: Can I tap into a 12v battery bank from multiple points at the same time?

I'm in the habit of isolating my starter batt. for startups - I've often wondered if i'm just wasting my time fiddling with switches - in particular, i often forget to switch the house batteries back on so they get some charge. Are there any potential problems from overloading the starter if all batteries are connected? I know that as the old starter started dying, i gradually had to use more batteries to get a turnover.
charliehows is offline   Reply With Quote
Old 17-08-2015, 14:53   #11
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Can I tap into a 12v battery bank from multiple points at the same time?

OK, someone's gotta say it...
Three posts and you fuse the neg because the juice comes out there???
I guess I had better completely rewire my boat !

__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is online now   Reply With Quote
Old 17-08-2015, 15:42   #12
Registered User
 
Albro359's Avatar

Join Date: Jun 2009
Location: Elyse is in New Zealand
Boat: Amel Super Maramu 2000
Posts: 589
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by Nature Boy View Post
svlamorocha.
New guy just guy just joined the other day.
Please allow me to ask why you would fuse the postive side of a D.C. circuit as this is after the load. Electricity comes out of the negative side of the battery. Would it not be better to fuse on the negative side before the load there by protecting it from a over current event?
While it is true that electrons or electronic energy flows from negative to positive, by historical convention, the positive wire is used to feed individual appliances and the negative wires are all connected together, hence the fuses are in the positive cable.....in effect it doesn't make any difference.
Any current flow is caused by the potential difference and the resistance of the appliance, the direction of flow is immaterial to the fuse...
__________________
See you out there ....... Alan S.V. Elyse
now https://svelyse.weebly.com
older https://voyagesofDIVA.weebly.com
Albro359 is offline   Reply With Quote
Old 17-08-2015, 16:08   #13
Registered User
 
MBWhite's Avatar

Join Date: Apr 2012
Location: Illinois
Boat: Rinker 24
Posts: 398
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by senormechanico View Post
OK, someone's gotta say it...
Three posts and you fuse the neg because the juice comes out there???
I guess I had better completely rewire my boat !

IIRC it's because the boat is in the Southern Hemisphere.
MBWhite is offline   Reply With Quote
Old 17-08-2015, 16:17   #14
Registered User

Join Date: Aug 2015
Location: Pa.
Posts: 5
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Ok just saying operational readyness of the circuit does not care where the fuse is, but the expensive electronics you are trying to protect might. I know A.C. and D.C. are not exactly the same but it is a simular argument the fuse an A.C. circuit on the neutral leg not an acceptable arragement.
Nature Boy is offline   Reply With Quote
Old 17-08-2015, 18:04   #15
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Can I tap into a 12v battery bank from multiple points at the same time?

Quote:
Originally Posted by charliehows View Post
I'm in the habit of isolating my starter batt. for startups - I've often wondered if i'm just wasting my time fiddling with switches - in particular, i often forget to switch the house batteries back on so they get some charge. Are there any potential problems from overloading the starter if all batteries are connected? I know that as the old starter started dying, i gradually had to use more batteries to get a turnover.
Putting batteries in the circuit, as long as you keep the system at 12 volts will not hurt the starter in any way. In fact it could be beneficial as more battery capacity connected to the starter you will get less voltage drop.

Instead of trying to remember to switch batteries on and off for starting, charging and to isolate the start batteries so you don't accidentally run them down you need to get a battery charge controller like the Yandina Combiner or Balmar Duocharge.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
multiple sources into one battery charger? bobmac10 Electrical: Batteries, Generators & Solar 3 09-03-2014 17:40
Can I use 12v and 24v panels with same controller? montenido Electrical: Batteries, Generators & Solar 7 25-06-2013 06:18
Multiple Batteries, Multiple Banks, Single Charger dakno Electrical: Batteries, Generators & Solar 3 06-06-2010 10:45
Multiple Charging Sources to the Same Battery Bank schoonerdog Electrical: Batteries, Generators & Solar 55 14-09-2009 14:47

Advertise Here


All times are GMT -7. The time now is 15:18.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.