Re: Arcing in 30 amp shore power cord? (Picture)

Quote:
Originally Posted by Jammer View Post
There have been various product proposals for a shore power connection with a temperature sensor that will disconnect the boat in the event of overheating, before there is a risk of fire. I'm only aware of one that made it to market and it was withdrawn due to problems with build quality.
That's not really a solution, just early detection of failure.

The problem is the usual connector - it seems to be a poor match for the weight and rigidity of most shorepower cables, its twist-lock is inadequate, and the contact area is minimal for the rated max current, especially as the connectors age and wear.

For many boats who don't have heavy AC loads, they may never experience a problem; they usually aren't drawing enough current to start the contact heating. And you can prolong the life of the contacts by using a contact cleaner/protectant (as per Frankly), and by never connecting/disconnecting "hot" - the boat and pedestel breakers should be off first - so you don't cause arcing at the connectors.

The Smart Plug is a step in the right direction, but then you still have the same old plug at the pedestel end.
__________________
When we give up on truth, we concede power to those with the wealth and charisma to create spectacle in its place.
- Timothy Snyder
Lake-Effect is offline   Reply With Quote
Old 02-08-2022, 07:15   #17
Registered User

Join Date: Mar 2022
Location: Ontario Canada
Boat: Jeanneau SO 389
Posts: 1,969
Re: Arcing in 30 amp shore power cord? (Picture)

I’m happy you unplugged it. You need to replace your boats plug in and check the hull ground wire. I think the green stuff got your ground.
Rumrace is offline   Reply With Quote
Old 02-08-2022, 08:20   #18
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,187
Images: 6
Re: Arcing in 30 amp shore power cord? (Picture)

This is a classic example of an arc fault. This is series arc, so low current, not enough for Circuit breaker to trip and also no mismatch for GFCI, ELCI to trip. this is part of the reason UL mandated Arc Fault Circuit Interrupters AFCIs in homes, granted this is at a dock. I wonder if UL marine AFCI is coming as a mandate soon because ELCI cannot catch this.

If terminal is oxidized enough contacts develop semi-conductive path for small arc to develop. It becomes carbonized over time and the path is ripe for creating even more arcing which if left un-attended leads to heat buildup and ultimately fires. The more arcing the more carbon buildup and conditions escalate. Conditions need to be just right. Happens in home wiring (over decades)if improper torque is used for securing wires to wall fixtures or circuit breaker panels. In salty environment its a lot easier for those conditions to develop.

UL test AFCIs by creating this type of carbonized arcing samples in the test lab, to verify AFCI "work". It's very difficult to make them, so a lot of samples get thrown away, a bit of a witch craft.
phorvati is offline   Reply With Quote
Old 02-08-2022, 08:29   #19
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,518
Re: Arcing in 30 amp shore power cord? (Picture)

Not uncommon. I used to replace my cord every year living aboard as we ran a small space heater in winter. The end would look similar to that and if you inspected the internal copper wiring it as black.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 12-08-2022, 07:18   #20
Registered User

Join Date: Jun 2012
Location: Lighthouse Point Fl
Boat: Hake 32RK
Posts: 177
Re: Arcing in 30 amp shore power cord? (Picture)

both the cord "female" end connector and the boat "male" connector should be replaced when this kind of heat induced failure is seen. It may well be that the problem is starting in the male connector due to a damaged or previously overheated contact.
Mauruuru is offline   Reply With Quote
Old 12-08-2022, 07:48   #21
Registered User
 
thesaltytar's Avatar

Join Date: Feb 2022
Location: Savannah, GA
Boat: 1956 Bud McIntosh 36' schooner
Posts: 279
Re: Arcing in 30 amp shore power cord? (Picture)

Quote:
Originally Posted by Frankly View Post


Get a tube, mine must be 30 years old and has been smeared on a lot of electrical connections over the years.

That's actually a very good idea. Not to remedy the existing issue (as you noted at the top of your comment) but helping the conductivity over time will likely lengthen the lifespan of the plugs.

I used to do something similar with the little ends of halogen light bulbs because the vibration of the engine would shorten their lifespan. Improving their contact lengthened their lifespan.

Also... I do have a smart plug and stand by it, bit it's just a better design doing the same job and susceptible to the same failures over perhaps longer time.
thesaltytar is offline   Reply With Quote
Old 12-08-2022, 08:28   #22
Registered User

Join Date: May 2020
Posts: 19
Re: Arcing in 30 amp shore power cord? (Picture)

This is certainly a fire hazard. One of the reasons this occurs I haven’t seen mentioned yet, is that some folks do not cut the AC panel breaker off, and the Pedestal breaker off prior to attaching or detaching the SP cord. This leads to pitting on both the cord, and the inlet connection. Over time, that can lead to the same issue.

Good to see you are pulling the inlet connection. I would also suggest cutting back the AC wire if there is any charting at all. Sometimes, a new AC wire to at least the breaker will be necessary. Can become a bigger job, the further the deterioration is.
Nate24 is offline   Reply With Quote
Old 12-08-2022, 08:31   #23
Registered User

Join Date: Nov 2018
Location: NJ
Boat: Mariner 38 Pilot House
Posts: 186
Re: Arcing in 30 amp shore power cord? (Picture)

I concur with the others that suggested you replace the inlet on the boat and unfortunately the new cord also needs to be replaced.

Now the best solution is to ditch the L5-30 style connector on the boat side of the cord. Many use the Smartplug but I use a 30amp watertight pin and sleeve that moves the point of failure to the shore side of the service.
Attached Thumbnails
Click image for larger version

Name:	18AE3858-3139-437B-BBF1-E73A8E5E5DF8.jpg
Views:	60
Size:	419.1 KB
ID:	262721  
mcon12000 is offline   Reply With Quote
Old 12-08-2022, 09:53   #24
Registered User

Join Date: Jul 2017
Location: UK
Boat: Summer Twins 25
Posts: 749
Re: Arcing in 30 amp shore power cord? (Picture)

Replace the plug.
Chances are the plug is worn / damaged from the arcing - cleaning an arc is not good enough.
No Electrician worth his salt would try and clean that up.
Shaneesprit is offline   Reply With Quote
Old 12-08-2022, 11:22   #25
Registered User

Join Date: Nov 2014
Location: Sodus Bay, US (south) side of Lake Ontario
Boat: Pacific Seacraft Crealock 34
Posts: 86
Images: 2
Re: Arcing in 30 amp shore power cord? (Picture)

I’ll also vote strongly for the SmartPlug. My solution to occasionally needing the conventional inlet was to leave it in place and wire the SmartPlug inlet next to the original in parallel. I can thus use either one as needed.

BUT, BUT, BUT a conventional 3-prong inlet has male prongs in there, and those prongs will be “hot” when the parallel wired SmartPlug is use. My solution to that was to cut a cylinder of high density foam to fit the inside diameter of the old inlet, and slice 3 slots in that foam cylinder using a handheld jig saw blade to accept the prongs. That cylinder just lives in the old inlet since I rarely need it. There’s a pull cold loop of light cord to remove that insulating cylinder when needed.

I’m sure a surveyor would have a conniption fit over what I did. “That’s Unsafe! Violates standards!”

But it works.
BoatBumm is offline   Reply With Quote
Old 12-08-2022, 13:58   #26
Registered User
 
captainwd40's Avatar

Join Date: Jun 2016
Posts: 71
Re: Arcing in 30 amp shore power cord? (Picture)

That is the neutral pin being armed.

You either have a floating ground or forgot to install the jumper on your inverter.

An electrician can easily diagnose and fix your problem.

Cheers!
captainwd40 is offline   Reply With Quote
Old 12-08-2022, 16:04   #27
Registered User
 
GrowleyMonster's Avatar

Join Date: Dec 2012
Location: New Orleans
Boat: Bruce Roberts 44 Ofshore
Posts: 2,863
Re: Arcing in 30 amp shore power cord? (Picture)

Quote:
Originally Posted by CSY Man View Post
Hello from Florida:
Plugged in my 30 amp cord to run the 10,000 BTU A/C: Strong smell of burnt something.
Disconnected the cord and noticed black soot marks on the female end.
Cleaned the male contacts (They were already clean, no corrosion, but black from the arcing)

Different day, different marina AND different cord, same result: Arching and burned smell.
What is going on?
(No breakers popped on the boat or on the dock pedestals, the A/C was working normally.)

A short in the vessel's 110 volt system? (If so, breakers should have popped)
I would say that your male connection is bad, not making good contact. High resistance and current equals heat. Sometimes lots of heat. Replace the receptacle.
__________________
GrowleyMonster
1979 Bruce Roberts Offshore 44, BRUTE FORCE
GrowleyMonster is offline   Reply With Quote
Old 12-08-2022, 17:27   #28
Now on the Dark Side: Stink Potter.
 
CSY Man's Avatar

Join Date: Aug 2003
Location: Palm Coast, Florida
Boat: Sea Hunt 234 Ultra
Posts: 3,971
Images: 124
Re: Arcing in 30 amp shore power cord? (Picture)

Yes, replacing the inlet for sure, just curious what triggered it..
(Pulled out the old one, no corrosion, probably just old age)

Got an exact replacement from the same maker, $90.00
Attached Thumbnails
Click image for larger version

Name:	0E62E7B7-F991-4CC8-B5AE-920217D25AFC.jpg
Views:	44
Size:	420.3 KB
ID:	262748  
__________________
Life is sexually transmitted
CSY Man is offline   Reply With Quote
Old 12-08-2022, 17:36   #29
Now on the Dark Side: Stink Potter.
 
CSY Man's Avatar

Join Date: Aug 2003
Location: Palm Coast, Florida
Boat: Sea Hunt 234 Ultra
Posts: 3,971
Images: 124
Re: Arcing in 30 amp shore power cord? (Picture)

One guy got upset about the above question/thread and sent me a nasty message, probably full of himself and rum 'n coke.

For those who are concerned about fires and being in the same marina as me:
Shore power are hardly ever being used, nor do I visit marinas more than once or twice per year.
Got a nice solar panel and an 80 amp alternator.

Just curious what happened to my shore power cable and why the arcing..

Thanks for the informative advice and information, much appreciated
__________________
Life is sexually transmitted
CSY Man is offline   Reply With Quote
Old 12-08-2022, 18:25   #30
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Arcing in 30 amp shore power cord? (Picture)

Quote:
Originally Posted by CSY Man View Post
One guy got upset about the above question/thread and sent me a nasty message, probably full of himself and rum 'n coke.



For those who are concerned about fires and being in the same marina as me:

Shore power are hardly ever being used, nor do I visit marinas more than once or twice per year.

Got a nice solar panel and an 80 amp alternator.



Just curious what happened to my shore power cable and why the arcing..



Thanks for the informative advice and information, much appreciated


Whoever sent that message to you must be unaware that most boats with 30a shore connections and any load greater than 18-20 amps have melted connections.
Sailmonkey is offline   Reply With Quote
Reply

Tags
arc, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Airmar "Transom&q uot ; style triducer does not give wate Franziska Marine Electronics 3 04-10-2021 12:45
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
Yammer, won't start without arcing RebeccaM Engines and Propulsion Systems 8 17-06-2017 08:05
For Sale: Shore Power Cord 30 Amps 50ft w/Cord Pro XL velero Classifieds Archive 0 07-07-2014 10:56
Shore Power Cord vs. RV Cord Blc7 Electrical: Batteries, Generators & Solar 5 04-11-2013 11:05

Advertise Here


All times are GMT -7. The time now is 18:48.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.