Old 27-02-2021, 18:54   #16
Registered User
 
jt11791's Avatar

Join Date: Aug 2017
Location: Cruising the world
Boat: Hylas 54
Posts: 414
Re: Alternator output wire size question

Both of my alternators' outputs go through fuses (breakers) on the way to the 1-2-both switch. Protects from alternator shorts and good if I need to remove an alternator.
jt11791 is offline   Reply With Quote
Old 28-02-2021, 18:48   #17
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Alternator output wire size question

Quote:
Originally Posted by Buster007 View Post

the house bank positive will be fused. i understand no need to fuse the starter battery per ABYC
Actually that is not correct.

ABYC does not require a dedicated start battery to be fused. By dedicated they mean a battery that can not be used for anything except engine starting. Battery to simple on/off switch and to starter.

With a 1/2/both/off switch either battery can be used for any load so both batteries do need fusing.

It is not hard to do. I fuse start circuits regularly, most often with a fuse of about 250 amps. Typically wired with 2/0.
mitiempo is offline   Reply With Quote
Old 28-02-2021, 18:57   #18
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Alternator output wire size question

Quote:
Originally Posted by Celestialsailor View Post
I have never seen a fuse on an alternator. If a short developed "in" an alternator the diodes would blow. Yes, It's quite common to fuse at the common on the battery switch.
An alternator is a current limited device. As long as the wire is sized properly a fuse is not needed at the alternator.

The battery is the source that can cause the problem. That is why fusing should always be at the battery end of a cable, not at the load end.

smac999 is correct, only fuse if the wire is led from the alt to a battery directly.
mitiempo is offline   Reply With Quote
Old 28-02-2021, 20:21   #19
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,469
Images: 5
Re: Alternator output wire size question

Quote:
Originally Posted by mitiempo View Post
An alternator is a current limited device. As long as the wire is sized properly a fuse is not needed at the alternator.

The battery is the source that can cause the problem. That is why fusing should always be at the battery end of a cable, not at the load end.

smac999 is correct, only fuse if the wire is led from the alt to a battery directly.

I think we were on the same page. I usually fuse the common on the 1/2/ALL/OFF selector switch and yes, in most cases 2/0 is most sufficient for a cable run (depending on distance run of course). Still, fusing the alternator is not a practice that I have seen. More importantly IMHO is proper routing and chafe protection of the large battery cables. Over time with a multitude of wire changes and add-ons, the cables can get covered by a birds nest of wire and if there is a chafe problem, hard to see before it is too late.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Reply

Tags
alternator, size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lofrans tigress wire size? Voltage drop/wire size calc question.. Eastward ho 24 Construction, Maintenance & Refit 30 09-06-2020 09:50
Bumping the rigging up one size (wire) do I compensate for streched old wire? Eastward ho 24 Construction, Maintenance & Refit 17 02-07-2019 13:56
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47

Advertise Here