I have a problem: the A/C would not start on the generator
A/C is old Cruis'air (probably 15k BTU, I'm not sure) the generator is 3300 nominal and 3600 peak, 120v 30A.
I was told that I need to put a relay and capacitor for the surge at start up and that will solve the problem
Also that a delay in the water pump start will help.
Can anybody help me with more details and explain a little more what I have to do in order to have the A/C starting correctly under generator?
Thank you
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
06-06-2011, 08:58
|
#2
|
Registered User

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 3,924
|
Re: A/C Start Up on Generator
I had the same problem. What you need is called a "Hard Start Capacitor". They are made by Supco. Here is a link: http://www.supco.com/images/pdfs/200...ion%202-51.pdf
They are very easy to install. If you look at the label on your AC compressor you will see a number called Locked Rotor Amps or LRA. This is very close to the number of amps you will need to start the compressor. It can be eight or ten times the amps required to run it. The hard start capacitor stores up energy and then gives out a burst to kick the compressor into motion. I think newer ACs are coming with these already installed. My little 5000 BTU AC needs over 3000 watts to start. With the hard start capacitor installed I can start and run it on a little 1000 watt Honda.
__________________
Retired from Hopkins-Carter Marine Supplies
|
|
|
06-06-2011, 09:00
|
#3
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
Quote:
Originally Posted by HopCar
I had the same problem. What you need is called a "Hard Start Capacitor". They are made by Supco. Here is a link: http://www.supco.com/images/pdfs/200...ion%202-51.pdf
They are very easy to install. If you look at the label on your AC compressor you will see a number called Locked Rotor Amps or LRA. This is very close to the number of amps you will need to start the compressor. It can be eight or ten times the amps required to run it. The hard start capacitor stores up energy and then gives out a burst to kick the compressor into motion. I think newer ACs are coming with these already installed. My little 5000 BTU AC needs over 3000 watts to start. With the hard start capacitor installed I can start and run it on a little 1000 watt Honda.
|
THANKS A LOT!!
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
06-06-2011, 09:03
|
#4
|
Registered User

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 3,924
|
Re: A/C Start Up on Generator
You're very welcome. Let me know how it works out. You can probably buy the hard start kit locally from a refridgeration supply house. They aren't expensive.
__________________
Retired from Hopkins-Carter Marine Supplies
|
|
|
06-06-2011, 15:25
|
#5
|
Registered User
Join Date: Mar 2010
Location: Ventura, CA
Boat: 48 Californian
Posts: 195
|
Re: A/C Start Up on Generator
Is this a new install or has it worked in the past?
|
|
|
06-06-2011, 20:38
|
#6
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
Gen is new. A/C was there already.
Will install a Supca Hard start SSP 6 as soon as possible
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
06-06-2011, 21:22
|
#7
|
Moderator Emeritus

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
|
Re: A/C Start Up on Generator
There are also capacitor start motors in case the first solution does not work.
__________________
David
Life begins where land ends.
|
|
|
13-06-2011, 12:06
|
#8
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
We tried SSP6 doesn't work...
A/C specialist recommend installing the Crusair "soft start" kit. Not cheap.. but the Admiral will be happy if we managed to have the A/C working.
Somebody suggested that the gen being new, the engine has to be broken down a few 10 hrs before having really an opinion... ??? I'm puzzled by the comment
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
14-06-2011, 05:27
|
#9
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
The soft start kit will be installed next Friday.. let's hope the problem will be solved.
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
14-06-2011, 05:38
|
#10
|
Registered User
Join Date: May 2008
Posts: 3,162
|
Re: A/C Start Up on Generator
If the soft start doesn't work, another solution is something like a Victron Inverter/Charger. These can use the inverter to provide extra power from the batteries while passing through the the power from the genset. Since it's only for a second, the batteries have more than enough capacity.
This only makes sense if you need a new inverter/charger. Of course, this is even more money to solve a problem that doesn't seem like it should have been a problem in the first place. But this is a boat......
Carl
|
|
|
14-06-2011, 05:46
|
#11
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
Quote:
Originally Posted by CarlF
If the soft start doesn't work, another solution is something like a Victron Inverter/Charger. These can use the inverter to provide extra power from the batteries while passing through the the power from the genset. Since it's only for a second, the batteries have more than enough capacity.
This only makes sense if you need a new inverter/charger. Of course, this is even more money to solve a problem that doesn't seem like it should have been a problem in the first place. But this is a boat......
Carl
|
Thanks
Where can I get more details on this?
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
14-06-2011, 08:27
|
#12
|
Do… or do not

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 13,765
|
Re: A/C Start Up on Generator
Quote:
Originally Posted by Alecadi
Thanks
Where can I get more details on this?
|
It's called "Power Assist":
Quote:
Power connections to provide all the power you need are not always available. That’s why Victron Energy developed Power Assist. This feature monitors power consumption and supplies additional power to prevent overloading. The Quattro can temporarily turn a 16A connection into 38A and a 5kVA generator into 10kVA. No other brand offers better functionality in this arena than the inventor: Victron Energy.
|
ciao!
Nick.
|
|
|
14-06-2011, 08:54
|
#13
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
Quote:
Originally Posted by s/v Jedi
It's called "Power Assist":
ciao!
Nick.
|
Thanks Nick
Alec
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
14-06-2011, 09:08
|
#14
|
Registered User
Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,474
|
Re: A/C Start Up on Generator
If this is a new installation, follow the above. If this is an old, clean and reconnect ALL wires from the generator to the Ac unit. Mine was having trouble starting, and I found a 40volt drop from generator to AC during startup. New connectors fixed this.
|
|
|
16-06-2011, 09:32
|
#15
|
Registered User

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
|
Re: A/C Start Up on Generator
We isntalled the soft start but doesn't work either
and yes we have a voltage drop of more than 30v...
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
|
|
|
 |
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Rate This Thread |
Linear Mode
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
Advertise Here
Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
Vendor Spotlight |
|
|
|
|
|