Re: A/C Start Up on Generator

Quote:
Originally Posted by teejayevans View Post
My experience is with a Frigidare 5000 BTU AC and Honda 1000 is:
normal amp draw when running is ~5amps (it starts around 4.8 and slowly climbs to 5.2 for some reason).
When set on low, Fan draws about .5 amps, but when compressor kicks in it goes up to 14 amps, the gen has a 4 second delay before disconnecting, with eco-throttle on, sometimes it recovers in 4 seconds and sometimes it doesn't.
One thing I can't explain, when set to high, the draw is the same, I'm using kill-a-watt to measure the amps.
Tom
The current draw on an A/C is not relative to the temp setting. The fan speed can have a small effect, but depending on the circuitry used to control fan speed it may even go up on lower speeds.
capn_billl is offline   Reply With Quote
Old 17-06-2011, 11:24   #32
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,572
Re: A/C Start Up on Generator

The old A/C units required very large starting currents , (3-10times normal current draw), for the compressors. My generator is 10KW for two 12kBTU A/C units, of which I can only start one at a time. The 3300 portable generator is very small for a 15KBTU A/C unit. The new A/C units with rotary or scroll compressors have very small starting currents, (1.5-2 times normal current). I know you don't want to hear this, but either a bigger generator, or a new A/C may be your only option. You can call the generator manufactorer and see what is the max inrush current it can handle, and compare to inrush current of A/C, remember the more the voltage drops the more current it takes to start.
capn_billl is offline   Reply With Quote
Old 17-06-2011, 11:35   #33
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by capn_billl View Post
I know you don't want to hear this, but either a bigger generator, or a new A/C may be your only option. You can call the generator manufactorer and see what is the max inrush current it can handle, and compare to inrush current of A/C, remember the more the voltage drops the more current it takes to start.
What about the indications given by the gen people? see post #25.
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 13:53   #34
Registered User

Join Date: Sep 2007
Location: FL
Boat: Pacific Seacraft 31 - Cielo Azul
Posts: 360
Images: 3
Re: A/C Start Up on Generator

Quote:
Originally Posted by capn_billl View Post
The current draw on an A/C is not relative to the temp setting. The fan speed can have a small effect, but depending on the circuitry used to control fan speed it may even go up on lower speeds.
HI LOW was referring to the cool setting, not the thermostat.
Tom
teejayevans is offline   Reply With Quote
Old 17-06-2011, 14:17   #35
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,966
Re: A/C Start Up on Generator

Quote:
Originally Posted by Alecadi View Post
What about the indications given by the gen people? see post #25.
Nah, those instructions are for tuning the voltage regulator to set the voltage right. Your voltage is right; it only comes down because of the overload.

You can't run that A/C from such a genset. With a Victron inverter/charger ith power assist? may be, but I still wouldn't want that genset to run my A/C.

ciao!
Nick.
s/v Jedi is offline   Reply With Quote
Old 17-06-2011, 14:26   #36
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,059
Re: A/C Start Up on Generator

Just for fun, can you borrow a Honda and try it?
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is online now   Reply With Quote
Old 19-06-2011, 07:14   #37
Registered User
 
dropanchorfor3's Avatar

Join Date: Jun 2011
Location: South Florida
Boat: Still looking
Posts: 91
Re: A/C Start Up on Generator

Quote:
Originally Posted by Alecadi View Post
We isntalled the soft start but doesn't work either
and yes we have a voltage drop of more than 30v...
Chances are if you have a voltage drop of 30 volts you may have a bad contact relay which supplies voltage to the compressor the T- stat board, fan etc. A hard start is measured in microfarads and so is a start and run capacitors. If either one is not supplying enough voltage tp a certain componet your a/c will not run. Run caps have a start, herm, and c for compressor terminals. Run caps are usually around a 35+5 cap. I'm not sure what yours will be most likely smaller in size and in number 15+5 cap etc. They supply voltage to the compressor, fan. Make sure you have the right voltage coming in to your a/c 120v and 24v coming out. Check the voltage on transformer for high and low voltage.
dropanchorfor3 is offline   Reply With Quote
Old 19-06-2011, 07:53   #38
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: A/C Start Up on Generator

From all evidence, including the reply from the manufacturer here is the problem.

1. When an A/C unit first starts it draws a lot of extra power.

2. The generator does not have enough power for the startup.

3. The adjustments will not make any difference.

Bottom line, the generator is too small to work in the current system. You might be able to add a capacitor that will reduce the start up power but it might not be enough.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 19-06-2011, 08:02   #39
Registered User
 
dropanchorfor3's Avatar

Join Date: Jun 2011
Location: South Florida
Boat: Still looking
Posts: 91
Re: A/C Start Up on Generator

It will draw extra power, I for got that you were using a generator upon start up. The other accessories will not help then, sorry I thought I could help. So you need a higher kW generator?
dropanchorfor3 is offline   Reply With Quote
Old 21-06-2011, 14:28   #40
Registered User
 
Beausoleil's Avatar

Join Date: Jul 2007
Location: Solomons, MD USA
Boat: Formosa 51 Aft Cockpit Ketch - "Beausoleil"
Posts: 611
Images: 3
Re: A/C Start Up on Generator

I haven't seen any talk about the true capacity of this generator. According to Boliy, this Pro3600 variable speed generator is only capable of 3000W continuous, 3300W max.

They claim it can start up an RV 15k BTU A/C unit, but don't specify a make or model. It may be able to start up a modern unit, but an older unit like Alecadi has is a big if...
__________________
Cap'n Jon (KB1HTW)
S/V Beausoleil -1979 Formosa 51 Ketch
"If it's gonna happen, it's gonna happen out there." - Captain Ron
Beausoleil is offline   Reply With Quote
Old 22-06-2011, 06:43   #41
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,572
Re: A/C Start Up on Generator

Quote:
Originally Posted by teejayevans View Post
HI LOW was referring to the cool setting, not the thermostat.
Tom
My statement stands, a compressor only has one speed, and power draw. Any settings on AC unit only effect fan speed, or cycle time, neither change current draw.
capn_billl is offline   Reply With Quote
Old 22-06-2011, 06:47   #42
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,572
Re: A/C Start Up on Generator

Quote:
Originally Posted by Beausoleil View Post
I haven't seen any talk about the true capacity of this generator. According to Boliy, this Pro3600 variable speed generator is only capable of 3000W continuous, 3300W max.

They claim it can start up an RV 15k BTU A/C unit, but don't specify a make or model. It may be able to start up a modern unit, but an older unit like Alecadi has is a big if...
That says it. no one wants to tell this guy to go out and spend a lot of money for new stuff, but the general rule is Big AC = Big Gen; Small AC = Small Gen. Anything else is asking for trouble. Newer AC units use a LOT less power than old ones, especially on startup.
capn_billl is offline   Reply With Quote
Old 22-06-2011, 07:14   #43
Registered User
 
S/V Illusion's Avatar

Join Date: Oct 2007
Location: Lakewood Ranch, FLORIDA
Boat: Alden 50, Sarasota, Florida
Posts: 3,471
Re: A/C Start Up on Generator

I didn't bother reading through 3 pages of comments so if this is redundant, please ignore.

A simple hard start cap might solve your problem as it has countless other folks:

RV Air Conditioner Hard Start Capacitor | ModMyRV
S/V Illusion is offline   Reply With Quote
Old 22-06-2011, 07:17   #44
Registered User
 
dropanchorfor3's Avatar

Join Date: Jun 2011
Location: South Florida
Boat: Still looking
Posts: 91
Re: A/C Start Up on Generator

Quote:
Originally Posted by capn_billl View Post
My statement stands, a compressor only has one speed, and power draw. Any settings on AC unit only effect fan speed, or cycle time, neither change current draw.
Exactly right, the amp draw on a compressor will drop a little after it starts and runs. I know on commercial water towers there is a new style of compressor using magnitaion. Magnets are used inside the compressor as apposed to a coil. Making the compressor the most efficient on the market.
I will find out if they are making marine a/c's and or portable a/c units using the same technology, if so problem should be solved as far as voltage- amp draw.
dropanchorfor3 is offline   Reply With Quote
Old 22-06-2011, 07:19   #45
Registered User
 
dropanchorfor3's Avatar

Join Date: Jun 2011
Location: South Florida
Boat: Still looking
Posts: 91
Re: A/C Start Up on Generator

Quote:
Originally Posted by S/V Illusion View Post
I didn't bother reading through 3 pages of comments so if this is redundant, please ignore.

A simple hard start cap might solve your problem as it has countless other folks:

RV Air Conditioner Hard Start Capacitor | ModMyRV
If he has a droppage in volts a hard start will not help. Unfortunately...
dropanchorfor3 is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator vs Inverter Generator (Genset) Jon4399 Electrical: Batteries, Generators & Solar 30 11-01-2011 09:13
Fault with First Start of Generator ? kerry231168 Electrical: Batteries, Generators & Solar 5 04-12-2010 08:38
Portable Generator vs Solar Panels or Wind Generator Sweet As Electrical: Batteries, Generators & Solar 120 16-09-2010 18:27
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06

Advertise Here


All times are GMT -7. The time now is 13:38.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.