Hello everybody,
We have a new batterie bank with 16 x 6volt t-106 batteries. We use solar to charge them. What is the normal maximum charge that we should program the controller? We use them as a 12 volt system using 24 volt solar panels but charging to 12 volts. Actually at the moment we charge them up to 14.7 but in 8 months have lost almost 1 cup of water in each cell, am I over charging? Thanks in advance, JP and Tania in need of helpé
raphaella is offline   Reply With Quote
Old 09-10-2013, 17:34   #2
Registered User
 
raphaella's Avatar

Join Date: Jun 2011
Location: Montreal, Canada
Boat: Lagoon 410, 41 ft
Posts: 52
Re: 6volt batterie banks

sorry t-105 batteries 6volt
raphaella is offline   Reply With Quote
Old 09-10-2013, 17:56   #3
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: 6volt batterie banks

Wow....16 T-105's. That's 1,800 amp hours total capacity @ 12VDC. Is this an installation in a house??

Re: charging, what you need is a good solar charge controller with adjustable charging profiles for different battery chemistries. I personally like the Morningstar MPPT controllers.

T-105's like to be charged at 14.8 or even 15.0VDC in the absorption cycle, at normal room temperatures. After receiving a full charge, T-105's like to be kept at about 13.2-13.4VDC float level, with periodic bumping up to absorption voltage for short periods of time.

I'd say that your water loss may not be excessive, but you can cut it down a lot by using either HydroCaps or WaterMiser caps. I use WaterMiser caps on all 10 of my T-105s. They make it easier to check water levels and to top them up.

Also, the new automatic watering system offered by Trojan is truly wonderful. It makes the job of keeping water levels properly maintained very easy and fast.

Bill
btrayfors is offline   Reply With Quote
Old 09-10-2013, 17:57   #4
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: 6volt batterie banks

Good question but really needs more information to answer correctly.

It will depend to some degree on how much you are drawing out of the batteries and how much solar capacity you have. If you had 1000 Watts of solar panels and draw very little from the batteries each day then 14.7V constantly could be too much.

But if you are using a lot of battery every day and only have a 150 Watts of solar then 14.7V should not be a problem.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 09-10-2013, 18:01   #5
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: 6volt batterie banks

Holy crap that is a big bank! Do you use over 1,000 AHrs each day? We are electricity hogs and we only have 6 T-105's.

Trojan recommends charging these batteries at 14.8V to absorption and holding there until float amperage input is reached.

However, this needs to be temperature compensated. Here in the tropics, the battery hold can easily be 90-100*, so the compensated charging voltage is often 14.4-14.5V instead.

At these temps and charging voltages, we need to add water to ours every 3 months or so, and the amount is much less than you are using - maybe 1/4 cup per cell (I use an outboard fuel line squeeze bulb to deliver water and it usually takes 1-2 partial squeezes of the bulb per cell).

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 09-10-2013, 18:04   #6
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: 6volt batterie banks

Along those lines, if you are never drawing the batteries down much, and your solar charger has a fixed absorption time instead of variable, then you will be boiling them for several hours each day.

If this is the case, then your best solution is to get rid of half of your batteries. Or buy a solar controller that has a better algorithm. Or set yours to much shorter absorption times, if possible.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 19-10-2013, 07:31   #7
Registered User
 
raphaella's Avatar

Join Date: Jun 2011
Location: Montreal, Canada
Boat: Lagoon 410, 41 ft
Posts: 52
Re: 6V Battery Banks

Thanks a lot guys for all the info. And we do use much current, 2 fridges, 1 freezer and a new 12volt aircon unit being installed at this very moment. Never knew that making toasts used 92 amps on DC and with 6 daughters and 4 grandchildren, we need lots of toasts in the morning. Even thinking of getting a coffee maker. We do have a programmable solar MPPT controller and have adjusted to the proper settings with all your info and actually got in touch with Trojen where they were very helpful and gave all the technical data to my questions.
raphaella is offline   Reply With Quote
Old 19-10-2013, 07:32   #8
Registered User
 
raphaella's Avatar

Join Date: Jun 2011
Location: Montreal, Canada
Boat: Lagoon 410, 41 ft
Posts: 52
Re: 6V Battery Banks

Now for another question. Wind generator!! What kind is the most silent one and that actually charges well?
raphaella is offline   Reply With Quote
Old 17-05-2014, 04:52   #9
Registered User
 
raphaella's Avatar

Join Date: Jun 2011
Location: Montreal, Canada
Boat: Lagoon 410, 41 ft
Posts: 52
Re: 6V Battery Banks

Finally we installed a new silent wind and wow noise level lower than we expected! Yahoooo! Amps just under but that is the life. Only one thing after one month we realised that there was a little vibration that started. We simply washed the blades properly for dust particles started to stick to the ends of the blades, causing this vibration. Once washed vibration gone. Also do not forget to check the screws after a couple of weeks for they do loosen as mine did!!!
raphaella is offline   Reply With Quote
Old 17-05-2014, 05:29   #10
Registered User
 
Mike OReilly's Avatar

Join Date: Sep 2011
Location: Good question
Boat: Rafiki 37
Posts: 14,206
Re: 6V Battery Banks

Quote:
Originally Posted by raphaella View Post
Finally we installed a new silent wind and wow noise level lower than we expected! Yahoooo! Amps just under but that is the life. Only one thing after one month we realised that there was a little vibration that started. We simply washed the blades properly for dust particles started to stick to the ends of the blades, causing this vibration. Once washed vibration gone. Also do not forget to check the screws after a couple of weeks for they do loosen as mine did!!!
Hi raphaella, I just noticed this thread. I installed a SilentWind generator last season, and have been very pleased with it so far. Very quiet, and seems to produce power pretty close to spec.

Thanks for the tips. I'll be sure to clean our blades before re-installing this season.
__________________
Why go fast, when you can go slow.
BLOG: www.helplink.com/CLAFC
Mike OReilly is offline   Reply With Quote
Old 17-05-2014, 05:53   #11
mrm
Registered User

Join Date: Feb 2011
Location: Poland, EU
Boat: crew on Bavaria 38 Cruiser
Posts: 654
Re: 6V Battery Banks

Quote:
Originally Posted by raphaella View Post
Finally we installed a new silent wind
[...] causing this vibration. Once washed vibration gone.

Also do not forget to check the screws after a couple of weeks for they do loosen as mine did!!!
Did you use a mild threadlocking compound on install? This is highly recommended on installing any parts which may vibrate.
mrm is offline   Reply With Quote
Old 17-05-2014, 07:13   #12
Registered User

Join Date: May 2014
Location: Al
Boat: 1981 51' Formosa
Posts: 187
Re: 6V Battery Banks

edit: missed the last couple post before responding.

Take a look at Rutland wind generators, there are bigger ones out there but these are whisper quiet and start making power in relatively low wind. I don't don't have one but a friend has had one going for 4 years or so with no issues.
Formosa Scott is offline   Reply With Quote
Old 17-05-2014, 07:17   #13
Registered User
 
zboss's Avatar

Join Date: Sep 2011
Location: On a boat
Boat: 1987 Cabo Rico 38 #117 (sold) & 2008 Manta 42 #124
Posts: 4,174
Re: 6V Battery Banks

Quote:
Originally Posted by mrm View Post
Did you use a mild threadlocking compound on install? This is highly recommended on installing any parts which may vibrate.
Silentwind does not include or mention the use of a threadlocker on their blades, so we didn't use it either.
zboss is offline   Reply With Quote
Old 17-05-2014, 13:15   #14
mrm
Registered User

Join Date: Feb 2011
Location: Poland, EU
Boat: crew on Bavaria 38 Cruiser
Posts: 654
Re: 6V Battery Banks

Quote:
Originally Posted by zboss View Post
Silentwind does not include or mention the use of a threadlocker on their blades, so we didn't use it either.
Nevertheless, next time you find some loose screws, try to apply some. It may (and likely will) make all the difference. I recommend a weak threadlock compound so screws can be undone with hand tools. Medium compound requires a substantial force to break, and strong one usually requires heat too.
mrm is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Charging Multiple Battery Banks nmit5903 Electrical: Batteries, Generators & Solar 67 10-09-2013 22:32
2 Ohm Resister tuberider Electrical: Batteries, Generators & Solar 60 26-06-2013 01:10
Battery Switch Wiring Rustic Charm Electrical: Batteries, Generators & Solar 61 19-11-2012 09:43
Battery Cabling for Parallel Bank Rustic Charm Electrical: Batteries, Generators & Solar 103 14-06-2012 16:33
AGMs and Dumb Regulator . . . stevensuf Electrical: Batteries, Generators & Solar 57 17-11-2011 19:01

Advertise Here


All times are GMT -7. The time now is 02:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.