Old 11-05-2018, 06:38   #1
Registered User
 
jr_spyder's Avatar

Join Date: Aug 2011
Location: Boston area
Boat: Little Harbor 46 (1988)
Posts: 326
50hz dock power and my charger/inverter

Hi, for the first time I am sailing in an area where I can only get “European” power, meaning 120vac at 50hz. I know of the issues generally and that I should be concerned.

I’ve just gone through my entire manual for my inverter/charger and can’t find any spec on allowable input Hz. It is an older Trace U2512.

My only vac systems on board are the Trace, a microwave, and compressors for air conditioning. Minimally I want to be sure I can power up the Trace and charge batteries and keep 12vdc systems happy (mainly refrigeration). If I can safely run the other systems that would be a bonus.

Sorry I haven’t done a deep search on the forums on this as I am underway with sketchy data service.

Any quick help appreciated.

Thanks, JR
jr_spyder is offline   Reply With Quote
Old 11-05-2018, 07:35   #2
Registered User

Join Date: Oct 2015
Posts: 2,007
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by jr_spyder View Post
Hi, for the first time I am sailing in an area where I can only get “European” power, meaning 120vac at 50hz. I know of the issues generally and that I should be concerned.

I’ve just gone through my entire manual for my inverter/charger and can’t find any spec on allowable input Hz. It is an older Trace U2512.

My only vac systems on board are the Trace, a microwave, and compressors for air conditioning. Minimally I want to be sure I can power up the Trace and charge batteries and keep 12vdc systems happy (mainly refrigeration). If I can safely run the other systems that would be a bonus.

Sorry I haven’t done a deep search on the forums on this as I am underway with sketchy data service.

Any quick help appreciated.

Thanks, JR
For what it is worth 120V/50Hz is not a European power standard. Europe is 220V/50Hz (or sometimes 240V/50Hz or 230V/50Hz) 120V/50Hz is an oddball that is seen in a few Caribbean countries.

The trace should be fine between 40 and 70 Hz. You might want to turn off the "inverter" function so if dock power drops out, you don't get sudden switches of frequency. I am sure the Trace is not smart enough to match phse and frequency of output power.

Air conditioners are a "maybe"... some do fine and just run a bit a slower with 50 Hz power, with others the controllers are unhappy. We have one Cruisair and a MarinAire and both do fine on either frequency. The microwave, probably needs to be kept off if power is 50Hz.
billknny is offline   Reply With Quote
Old 11-05-2018, 07:35   #3
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
50hz dock power and my charger/inverter

When I lived in Germany, all our US 60hz stuff worked, TV’s VCR’s Microwave, everything. It all had to be run through a transformer of course to get 110VAC.
All of it was placarded 60hz.
Electric motors run slightly hotter and slower I believe and manual clocks won’t keep time, but I think you will have to try to and see.
Our microwave sounded different and I think cooked slower.
a64pilot is offline   Reply With Quote
Old 11-05-2018, 08:00   #4
Registered User
 
miyagimoon's Avatar

Join Date: Feb 2009
Location: Any Where there is Blue Water
Boat: Oyster 435 - Miyagi Moon
Posts: 94
Send a message via Skype™ to miyagimoon
Re: 50hz dock power and my charger/inverter

The European standard is 220v 50Hz.
You can of course use a transformer to reduce the voltage to 110v but the frequency will still be 50Hz. This could mean that some equipment designed for 60Hz will not operate correctly.
Motors will certainly run slower as in general Induction motor speed (rpm) is determined by Frequency x 60 (seconds per minute) x 2 (positive and negative pulses in the cycle)/ no of Poles.

Hence at 60Hz a 2 pole motor = 60 x 60 x 2 / 2 = 3600 rpm

at 50Hz = 50 x 60 x 2 / 2 = 3000 rpm.
miyagimoon is offline   Reply With Quote
Old 11-05-2018, 10:09   #5
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: 50hz dock power and my charger/inverter

personally I wouldn't try. I would disconnect the AC to the inverter. (it should have breaker input)

buy a battery charger that is 50/60 hz 120/240. charge batteries with that.

turn inverter on. power outlets with 120v/60hz.
smac999 is online now   Reply With Quote
Old 11-05-2018, 10:17   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by billknny View Post
.

The trace should be fine between 40 and 70 Hz. You might want to turn off the "inverter" function so if dock power drops out, you don't get sudden switches of frequency. I am sure the Trace is not smart enough to match phse and frequency of output power.

.
inverter chargers are always trying to phase snyc the input with the inverter. that's it's job. when you first turn an inverter / charger on, it takes 30 secs before it allows the power to be used. because it's checking it, and syncing to it.

a good (60hz) inverter charger would simply fail the 50hz input, and not allow it to pass or be used, and stay off.

this is why you can't buy multi voltage / mutli hz inverter chargers.
smac999 is online now   Reply With Quote
Old 11-05-2018, 10:27   #7
Registered User

Join Date: Nov 2014
Location: Falmouth, UK
Posts: 252
Re: 50hz dock power and my charger/inverter

The European standard is actually 230vac, although you're unlikely to ever come across this - see the article I've pasted below as that was easier than me explaining it

I think the one thing you should note is that some areas of Western Europe use 240v. This being the case, a 2:1 step-down transformer would give you 120v, not 110v, which could potentially be a greater issue than the 60/50hz one.

Currently, ALL Western European supplies are classified 230VAC. In reality there is no 230VAC supply unless you create one locally. 230VAC was a “standard” created during European "harmonisation" to give a single voltage standard across Western Europe, including UK and Irish Republic.

Although the ideal would have been to have a single voltage there were too many political, financial and technical obstacles to reduce UK voltage to European levels or to increase European voltage to UK levels, so a new standard was created to cover both. This was achieved by changing the tolerances of previously existing supply standards. UK voltage to 240VAC + 6% and - 10% and European to 220VAC +10% and -6% (thereby creating a manageable overlap) and we would call these two combined 230VAC, despite the fact that nobody was intentionally generating at 230VAC!

Depending on the voltage sensitivity of the product and the variance from nominal of the actual supplied voltage, it may not be advisable to use a 220VAC specific device in the UK or a 240VAC specific device in Mainland Europe etc. For instance a 240VAC supply can rise to as high as 254.4VAC and still be within tolerance, but the maximum rated voltage for a 220VAC product is only 242VAC. A 220VAC supply can drop as low as 206.8 within tolerance but the minimum rated voltage for correct operation of a 240VAC product is 216VAC It may work perfectly well either way but it could be, technically, outside the specification of the equipment with obvious implications. A 230VAC product must be compatible with all voltages across this range
wiekeith is offline   Reply With Quote
Old 11-05-2018, 11:23   #8
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by smac999 View Post
inverter chargers are always trying to phase snyc the input with the inverter. that's it's job. when you first turn an inverter / charger on, it takes 30 secs before it allows the power to be used. because it's checking it, and syncing to it.

My Magnum MS 2812 is so fast it is actually a UPS, you can kill shorepower and it will pick up the load so fast the TV won’t even flicker.
a64pilot is offline   Reply With Quote
Old 11-05-2018, 19:46   #9
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by a64pilot View Post
My Magnum MS 2812 is so fast it is actually a UPS, you can kill shorepower and it will pick up the load so fast the TV won’t even flicker.
exactly because it's already synced with the input and "waiting" to go.

I can't see how the 60hz 120 output could properly be syncing with a 50hz input. normally it would just "fail" it and not allow it to pass through. and stay in inverter mode
smac999 is online now   Reply With Quote
Old 11-05-2018, 19:48   #10
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by wiekeith View Post
The European standard is actually 230vac, although you're unlikely to ever come across this - see the article I've pasted below as that was easier than me explaining it

I think the one thing you should note is that some areas of Western Europe use 240v. This being the case, a 2:1 step-down transformer would give you 120v, not 110v, which could potentially be a greater issue than the 60/50hz one.

north america is 120 / 240 v

at the end of dock is maybe down to 110.

normally see about 117-118
smac999 is online now   Reply With Quote
Old 11-05-2018, 19:58   #11
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by smac999 View Post
inverter chargers are always trying to phase snyc the input with the inverter. that's it's job. when you first turn an inverter / charger on, it takes 30 secs before it allows the power to be used. because it's checking it, and syncing to it.

a good (60hz) inverter charger would simply fail the 50hz input, and not allow it to pass or be used, and stay off.

this is why you can't buy multi voltage / mutli hz inverter chargers.
Um, to the contrary, Victron Multi Plus is indeed a multi hz inverter...
__________________
Scott Berg
WAŘLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 20-05-2018, 14:27   #12
Registered User

Join Date: Nov 2014
Location: Germany
Boat: Beneteau Sense 43
Posts: 176
Re: 50hz dock power and my charger/inverter

Quote:
Originally Posted by wiekeith View Post
The European standard is actually 230vac, although you're unlikely to ever come across this - see the article I've pasted below as that was easier than me explaining it



...



Currently, ALL Western European supplies are classified 230VAC. In reality there is no 230VAC supply unless you create one locally. 230VAC was a “standard” created during European "harmonisation" to give a single voltage standard across Western Europe, including UK and Irish Republic.



220 V is long gone, mains voltage in Europe has been 230V +-23V @50Hz since the late 80s.

Attached image shows a voltage reading taken from a German outlet today.
Click image for larger version

Name:	IMG_7307.jpg
Views:	91
Size:	75.1 KB
ID:	170204
mbartosch is offline   Reply With Quote
Reply

Tags
charger, dock, inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inverter vs. Inverter/charger and which brand jbinbi Electrical: Batteries, Generators & Solar 34 07-03-2017 15:35
Connecting 50hz Italian boat to 60hz US power Inthefridge Electrical: Batteries, Generators & Solar 20 09-12-2016 10:59
Magnum 230v 50HZ inverter 3 wire tuberider Electrical: Batteries, Generators & Solar 4 03-04-2016 20:31
European power 50hz 60hz solution tulsag Electrical: Batteries, Generators & Solar 0 28-10-2014 07:11
Separate Charger and Inverter or Charger-Inverter ? SvenG Electrical: Batteries, Generators & Solar 14 15-10-2010 17:14

Advertise Here


All times are GMT -7. The time now is 22:00.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.