Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
I see what you are referring to about cutting energy in half. Let me asked this which may clarify this for you. Do you save the same amount of amp hours going from R2- R12 as you would save going from R12 to R22?

Sticking with our 80AH R10 example that I gave in my first response to seeing your graph for simplicity:
R10 80AH
R20 40AH = Saves 40AH
R40 20AH = Saves 20AH

You save half as much daily power with each successive doubling of the R-value. That's why there is a diminishing return of the power savings...cutting in half of a smaller number each time you double the R-value keeps giving you a smaller number. It's why most people settle on a R20 or R30 Box but rarely do they go up above the R40 range, it just isn't worth it from a Cost/Energy savings standpoint.
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 31-08-2016, 08:51   #32
Registered User

Join Date: Nov 2014
Location: Michigan
Posts: 116
Re: Freezer Insulation of R-40 per inch or better

ENERGY BOOMER: Why Doubling Attic Insulation Does Not Cut Your Energy Use in Half

This might explain it a little better. I do agree that you are cutting the energy need each time in half but each additional half is a small piece of the whole. If I have a pizza with 8 slices and we cut that in half we get 4 slices. If I cut the 4 slices in half again we get 2 slices not an additional 4 slices. Each reduction in half is a smaller percentage of the whole.

If I have 100 amp hours on a R2 fridge and insulate it to R10 I will save 80 amp hours. If I go to R20 I will save a total of 89.5 amp hours. If I then go to R40 I will save a total of 94 amp hours. So yes I am cutting it in half each time I double insulation but the percentage of the total is less and less of a gain.
Waterrat10 is offline   Reply With Quote
Old 31-08-2016, 09:00   #33
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
So yes I am cutting it [Energy use] in half each time I double insulation but the percentage of the total is less and less of a gain.
Cruisers don't care about the % of the total being less with each doubling, they care about total daily power usage. Real world vs Chat Room.

But I'm glad you came around to exactly what I have been saying from the start...whew...that was like pulling teeth...
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 31-08-2016, 09:00   #34
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
ENERGY BOOMER: Why Doubling Attic Insulation Does Not Cut Your Energy Use in Half

This might explain it a little better. I do agree that you are cutting the energy need each time in half but each additional half is a small piece of the whole. If I have a pizza with 8 slices and we cut that in half we get 4 slices. If I cut the 4 slices in half again we get 2 slices not an additional 4 slices. Each reduction in half is a smaller percentage of the whole.

If I have 100 amp hours on a R2 fridge and insulate it to R10 I will save 80 amp hours. If I go to R20 I will save a total of 89.5 amp hours. If I then go to R40 I will save a total of 94 amp hours. So yes I am cutting it in half each time I double insulation but the percentage of the total is less and less of a gain.
No need to over-complicate it. SV stated it clearly.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 31-08-2016, 09:00   #35
Registered User

Join Date: Nov 2014
Location: Michigan
Posts: 116
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by SV THIRD DAY View Post
Sticking with our 80AH R10 example that I gave in my first response to seeing your graph for simplicity:
R10 80AH
R20 40AH = Saves 40AH
R40 20AH = Saves 20AH

You save half as much daily power with each successive doubling of the R-value. That's why there is a diminishing return of the power savings...cutting in half of a smaller number each time you double the R-value keeps giving you a smaller number. It's why most people settle on a R20 or R30 Box but rarely do they go up above the R40 range, it just isn't worth it from a Cost/Energy savings standpoint.
I did not see this post when I posted my last post. It sounds like we are in agreement. Diminishing returns on effort. What I have been saying all along. It is exponential decay. Therefore you gain less and less the more you insulate. Going from R20 to R40 is less then a 5% reduction in energy where going from R2 to R20 is a 90% reduction in energy use. I believe we are debating around the same point.
Waterrat10 is offline   Reply With Quote
Old 31-08-2016, 09:03   #36
Registered User

Join Date: Aug 2016
Posts: 42
Re: Freezer Insulation of R-40 per inch or better

Looks like the Cost per R value (SV THIRD DAY) is a good Guide! Thanks!

I built a Prototype refrigeration system and am now looking at Aerogel or VIPs to get the thickness down, while keeping the system efficient.
Pic attached: Partially built, a box in a box with an extra "Bread Box" on top to keep the sun off everything.

The current prototype is of R-5x1"panels "wall insulation", not Polyiso.
Thickness is 4" to 8". The thinner being in "front" where people need to reach over and past the insulation for access. This and the lid/hatch are of best ROI for Aerogel.

The BD35 is SP water cooled Isotherm 2351. Yes, boat movement helps efficiency noticeably)
Total solar power is 250W. (LEDs lighting)
Battery is 12v x 225AH (plus a starter 12v batt)

The whole yacht's usage recharges on a typical day by 2pm latest, allowing for desalination work thereafter (Spectra 200C 7amps makes 8gallons per hr)

The prototype runs about 14Ahr overnight (tough to isolate like a Lab, with the sun rising) Ambient is about 75F day, 62F nights.
It has FOUR sections:
1) Freezer where the evaporator is. 15-25F Thermostat is above the evaporator, in contact)
2) Below that is 1/2Cft freezer storage. Blue-Ice filled-in; 20-30F
3) After 1" of R-5, there is the refrigeration area. 38-55F (usually lined with beer cans)
4) Above all this, 4" of R-5 away is a "Bread Box" to keep the window's heat off the fridge. always below 65F.


a 4-ch temp monitor (by Perfect Prime, AMAZON) shows the temps as stated above.
I've Cruized this setup for several weeks throughout the Channel Islands, CA this summer full time and it works well. Yes the fridge area is a bit warm when 55F. One goal was to fast freeze fish in the evaporator, then store that below in the 'freezer storage'; which works well. The Bread Box was almost a joke when built since the boat shape just kinda dictated it. But this too has been great, since handmade bread keeps longer, 4 days+ and is good for soft butter too (yum)

The final version will be built inside-out; tech first, wood finish last.
The HighTEch isulation ($$) will be at LEAST for the front, top, and hatch.
I'll fibreglass the whole thing, no drain, inside for a water-tight tub.
The hatch I'll cast in-place with FRP, 404 filler, and an 1/8" freezer seal with hardware latch.

Finish Carpentry is my weak spot, and awful expensive....thats another Thread, LoL!
Thanks for your expert advice SV Third Day and All!!
CaptnBry is offline   Reply With Quote
Old 31-08-2016, 09:05   #37
Registered User

Join Date: Aug 2016
Posts: 42
Re: Freezer Insulation of R-40 per inch or better

pic of Prototype
Attached Thumbnails
Click image for larger version

Name:	IMG_20160622_115549024_HDR.jpg
Views:	200
Size:	402.7 KB
ID:	130356  
CaptnBry is offline   Reply With Quote
Old 31-08-2016, 09:10   #38
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
Going from R20 to R40 is less then a 5% reduction in energy.
Amigo, check your math because cutting the power usage from 40AH to 20AH by doubling the R-Value is a 50% reduction in energy usage, not a 5%.
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 31-08-2016, 09:12   #39
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by CaptnBry View Post
...
The hatch I'll cast in-place with FRP, 404 filler, and an 1/8" freezer seal with hardware latch.

Finish Carpentry is my weak spot...
Unless you want "Engineering" to be a close second (weak spot) rethink your hatch plan and 1/8" gasket.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 31-08-2016, 09:13   #40
Registered User

Join Date: Nov 2014
Location: Michigan
Posts: 116
Re: Freezer Insulation of R-40 per inch or better

If anyones statements are misleading sir it would be yours. It is not linear. It is classic exponential decay. The more I add the less I get for each addition. So real world wise going from R20 to R40 will only make a minuscule difference in your amp hour if you open your fridge a couple of times a day to drink said beer. Your 5% savings will really only be .5% savings if you are lucky. If I shell meet you someday we can open our fridges and share some beers and argue circles some more. Cheers
Waterrat10 is offline   Reply With Quote
Old 31-08-2016, 09:22   #41
Registered User

Join Date: Nov 2014
Location: Michigan
Posts: 116
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by SV THIRD DAY View Post
Amigo, check your math because cutting the power usage from 40AH to 20AH by doubling the R-Value is a 50% reduction in energy usage, not a 5%.
Sir you forgot about the R2-R10 and R10 - R20 part of the equation which is by far the biggest gain. There are plenty of old boats in real world that have R2-5 with air leaks, poor missing insulation etc etc. You are cherry picking.
Waterrat10 is offline   Reply With Quote
Old 31-08-2016, 09:33   #42
Registered User

Join Date: Nov 2014
Location: Michigan
Posts: 116
Re: Freezer Insulation of R-40 per inch or better

Overall energy use.
Going from R-2 to R-10 save me about 80 amp hours
R-2 = 100 amp hours needed
R-20 = 10 amp hours needed
R-40 = 5 amp hours needed

That is a very small gain. If I open this fridge 5 times a day that 5 amp hours mean squat.
Waterrat10 is offline   Reply With Quote
Old 31-08-2016, 09:35   #43
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
So real world wise going from R20 to R40 will only make a minuscule difference in your amp hour if you open your fridge a couple of times a day to drink said beer.
Ha ha ha...first he agrees with me...then he falls back off the cliff and forgets everything we managed to teach him in this thread. So lets do one final review before flunking him from the class:

Going from a R20 to a R40 Box cuts your power usage in half (something you previously admitted but have now forgotten)
So if you were using 60AH you would be down at the 30AH range.
Our friend Waterrat10 can call a 50% reduction in power usage "minuscule" but to real cruisers out in the real world that's a big deal.


Quote:
Originally Posted by Waterrat10 View Post
Sir you forgot about the R2-R10 and R10 - R20 part of the equation which is by far the biggest gain. There are plenty of old boats in real world that have R2-5 with air leaks, poor missing insulation etc etc. You are cherry picking.
Who's forgetting about anything?
Going from R2-R10 and then from R10 to R20 does not have ANY bearing on the simple math and fact that going from a R20 to a R40 will cut your power usage by 50% and not 5%. Going from R10 to R20 also cuts it in half...again...simple Math. Each time you double the R-Value of a Box you cut the energy usage in half. And each time you are cutting a number in half, the real number gets smaller, it's simple math Sir.

Quote:
Originally Posted by Waterrat10 View Post
Overall energy use.
Going from R-2 to R-10 save me about 80 amp hours
R-2 = 100 amp hours needed
R-20 = 10 amp hours needed
R-40 = 5 amp hours needed
.
In your OWN EXAMPLE you show that the power usage in going from R20 to R40 is a 50% power savings (10AH down to 5AH is 50% but above you said it was 5%)...for the love of Pete, try and work with me here will ya...

Listen, it's not my problem that you can't get it and I know I can be a smart ass at times, but I've went above and beyond here in trying to help you and it's just time to give up. So class is closed for today, at least for you because I'm sending you to the principal's office and I have to work on my teak deck replacement project. Epoxy Day!
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 31-08-2016, 09:47   #44
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by SV THIRD DAY View Post
...it's not my problem that you can't get it, I've went above and beyond here in trying to help you..
Indeed you have. And he doesn't.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 31-08-2016, 09:54   #45
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Freezer Insulation of R-40 per inch or better

Quote:
Originally Posted by Waterrat10 View Post
Overall energy use.
Going from R-2 to R-10 save me about 80 amp hours
R-2 = 100 amp hours needed
R-20 = 10 amp hours needed
R-40 = 5 amp hours needed

That is a very small gain. If I open this fridge 5 times a day that 5 amp hours mean squat.
5 ah means more than you give it credit it means that I can run a couple extra fans at night to keep cool or run a forced Air heater to keep warm as the case may be.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Reply

Tags
freezer, insulation


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Insulation Between Fridge and Freezer mikereed100 Plumbing Systems and Fixtures 6 30-08-2010 15:53
Multipanel for Freezer Insulation ozmike Construction, Maintenance & Refit 4 20-07-2010 06:18
Freezer Insulation ? gbanker Plumbing Systems and Fixtures 8 20-05-2010 19:42
Improving Insulation on Existing Fridge / Freezer sailorgal Plumbing Systems and Fixtures 1 17-04-2010 06:21
What Are You Paying per Foot per Month? David M General Sailing Forum 56 09-04-2010 09:10

Advertise Here


All times are GMT -7. The time now is 21:13.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.