mast step and bonding wire for lightning protection

I am in the process of tying up all chainplates (minus the insulated backstay) with a 8AWG tinned copper wire. I have a keel stepped mast, my ballast is fully enclosed(no keelbolts) so i have a dynaplate.
Idea is to run this wire to a dynaplate and connect each bronze through hull to it. Base of the mast sits on a thin insulated teflon or plastic sheet between aluminum mast and the stainless mast step. Mast step is bolted to the cross stringer.

Since mast sits on an insulated plastic (very thin sheet) it is DC insulated so no stray currents. In terms of lightning, I imagine i have enough capacitance to present a low impedance path for lightning should the surge current travel through aluminum mast in addition to shrouds. I would expect most of the surge will travel through shrouds but Stainless is not as good of conductor as aluminum so Id like to add provision for surge that might travel through the mast. My question is do i put a jumper wire from base of aluminum mast to the step where the rest of the 8AWG bonding wire is connected, or do i add caps or MOVs or a DC blocking device what will act as a lightning or RF short, between mast base and mast step.
phorvati is offline   Reply With Quote
Old 18-10-2019, 00:49   #2
Registered User

Join Date: Jun 2016
Posts: 165
Re: mast step and bonding wire for lightning protection

8awg wire won’t help a whole lot for a lightning strike.... copper bar about 1/2 inch square might be a good start.... even the dynaplate only really does much for a radio ground. Things like mov’s will just cease to exist in a blinding flash.....

Where you are concerned about higher risk of a strike, a heavy chain or cable wrapped around the mast and chainplates dropped into the water both sides is likely to do more to help.....

In my experience lightning tends to not behave as you would expect.... seems like it has a mind of its own, sometimes not going down the (apparently) more conducive path - I’ve seen it blow through a rubber aircraft tyre instead of going along the purpose designed earthing lead..... heard stories of it going clean through fibreglass hull sides instead of through “lightning protection systems”
mickt243 is offline   Reply With Quote
Old 18-10-2019, 07:26   #3
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,205
Images: 6
Re: mast step and bonding wire for lightning protection

That does not sound very encouraging. From what i read, 8 AWG is a minimum bonding wire size. I have to assume its better than nothing. Ohm's law persists even in lightning strike, we just fail to understand how it applies beyond DC operation.
phorvati is offline   Reply With Quote
Old 18-10-2019, 10:52   #4
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,265
Re: mast step and bonding wire for lightning protection

Lightning starts as a mega high voltage DC charge but as it strikes it becomes a damped high frequency AC wave. You can hear the effect in a radio. It's not just a snap, but a crashing sound. The quickly diminishing AC voltage acts differently than a straight DC arc due to the capacitive effects of the materials it encounters.


To back up my statement, I found this:


https://www.nemasurge.org/wp-content.../grounding.pdf
__________________
'You only live once, but if you do it right, once is enough.

Mae West
senormechanico is offline   Reply With Quote
Old 18-10-2019, 11:40   #5
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 997
Re: mast step and bonding wire for lightning protection

If I correctly understand what you are asking, I would tie two of the Dynaplate bolts together with some 1 x 1/4" copper bar stock, do the same on the second pair of Dynaplate bolts (if your DP is not big enough to have 4 mounting bolts, it is probably not large enough). Then drill and tap the sides of the mast a few inches from the the base of the mast and run # 1/0 or so to each copper bar stock connector. Repeat for the other set of bolt. Then tie all rigging bonding wires to the copper bars or DP bolts.

That aluminium mast is going to conduct the majority of the current from a direct hit, but bonding the rigging helps prevent flash over problems by attempting to keep everything at the same voltage level.


Dynaplate don't have a great reputation for handling lightning strikes. One issue might be people just connecting one bolt and that single connection is just not up to the task. Thus my suggestion of tying all the bolts together.

Frankly
Frankly is offline   Reply With Quote
Old 18-10-2019, 12:51   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 51,347
Images: 241
Re: mast step and bonding wire for lightning protection

Lightning protection codes were updated a few years ago.
The primary lightning downconductor should be a minimum of #4AWG, and the secondary bonding conductors #6AWG.



__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 18-10-2019, 17:15   #7
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,391
Re: mast step and bonding wire for lightning protection

Quote:
Originally Posted by phorvati View Post
...........
Since mast sits on an insulated plastic (very thin sheet) it is DC insulated so no stray currents. In terms of lightning, I imagine i have enough capacitance to present a low impedance path for lightning should the surge current travel through aluminum mast in addition to shrouds. .......
I very much doubt there would be anywhere near enough capacitance to be useful.

I also very much doubt the very thin sheet of plastic under the mast would have anything remotely near the dielectric strength needed to prevent the arc breaking it down.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Reply

Tags
lightning, mast, rot

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Step one buy boat...step two??? Step three sailing Lotus Eater Liveaboard's Forum 34 29-10-2019 21:07
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 01:30
Wire size for Cathodic and/or Lightning protection geoffr Construction, Maintenance & Refit 12 14-08-2016 10:36
Bonding Mast For Lightning Strike silverp40 Construction, Maintenance & Refit 1 22-11-2013 03:00
Carbon Fibre Mast Lightning Protection stillbuilding General Sailing Forum 4 15-05-2011 11:57

Advertise Here


All times are GMT -7. The time now is 06:06.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.